• mains electrical supply connectors crimping

    From Richard Smith@21:1/5 to All on Wed Sep 20 10:32:47 2023
    Hello all
    I'd appreciate fine detail on crimp connectors for "mains" electrics
    in a home.

    Example - a "straight-through" connector looks something like this

    \___________/
    ___________
    / \

    to connect wires which go like this
    __ ___
    __|====== ======|___

    I got offcuts of Earthing cable and crimped them together and tried
    pulling them apart.

    I found that if you get the crimp tool "snug" up against flare of the
    outer end of the crimp-fitting the result is so strong you cannot
    feasibly pull the crimped cables apart.

    This is the crimp tool I am referring to

    https://www.toolstation.com/search?q=crimp+tool
    and/or
    https://www.toolstation.com/search?q=42429
    Product code: 42429
    Heavy Duty Semi Ratchet Crimping Tool

    Whereas if you clamp the crimp tool anywhere at the 1/4-length you can
    pull the assembly apart.
    Glad I saw that.

    Obviously other use of crimps is to terminate one wire with a lug to
    go onto a screwed/bolted connection.

    Anything else you can helpfully comment?

    This is about the UK.
    Voltage 230V (r.m.s.) 50Hz AC.
    Regulation of electrical systems in and around buildings in the UK is
    known as "18th Edition". Which is also British Standard BS7671.
    It is very much more like an American "Code" (eg "ASME9", "AWS D1.1")
    rather than in ISO. Has developed in an evolutionary way over
    something like 140 years ("first edition" was in the 1880's).

    Regards,
    Rich Smith

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jim Wilkins@21:1/5 to All on Wed Sep 20 07:42:28 2023
    "Richard Smith" wrote in message news:ly4jjptcjk.fsf@void.com...

    Hello all
    I'd appreciate fine detail on crimp connectors for "mains" electrics
    in a home.

    ----------------------------

    When I was doing industrial wiring the proper crimping tools were provided,
    and they worked well. At home I won't spend $200 apiece on them so I bought used ones from flea markets and less satisfactory general purpose tools like this: https://www.amazon.com/IWISS-Terminal-Crimping-6-50mm%C2%B2-Electrician/dp/B017S9EINA/ref=cm_cr_arp_d_product_top?ie=UTF8

    The calibration test for my good used AMP crimper is to measure the closed
    jaw gap with drill bit shanks. It was worn and I had to shim it.

    In my experience the inexpensive commercial tools for up to 25-30A crimp connectors are usually satisfactory, I have to experiment to get adequate results from low cost tools on connectors in the 50A and above range. The
    pull test is standard and easy to do with a fishing scale, I also measure
    the resistance with a microOhm meter and look for numbers comparable to the wire resistance, my first PP120 screw connector mod measured 0.68 milliOhms.

    https://s3vi.ndc.nasa.gov/ssri-kb/static/resources/nasa-std-8739.4a.pdf
    The pull test values are on page 54. Detailed operating instructions come
    with the crimping tool.

    Thermal imagers have come down in price and are very useful for finding hot spots in live circuits caused by bad connections. Yesterday I found a 30A
    fuse that was overheating at 13A and replaced it with a better name brand
    one that runs cool.

    If you solder a crimped connector, apply it at the exposed end of the wire
    and don't use enough to wick all the way through, the wires need to be able
    to flex individually where they come out. You shouldn't need to if you have
    the proper tool. I make do with what I have and then measure the result.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Richard Smith@21:1/5 to Jim Wilkins on Wed Sep 20 17:26:41 2023
    "Jim Wilkins" <muratlanne@gmail.com> writes:

    Wow! Even this "cheap" tool looks formidable.

    ... and less satisfactory
    general purpose tools like this: https://www.amazon.com/IWISS-Terminal-Crimping-6-50mm%C2%B2-Electrician/dp/B017S9EINA/ref=cm_cr_arp_d_product_top?ie=UTF8
    ...

    Pull-out test:
    I'm talking about - one end of the cable in a vice, put a vice-grip / locking-pliers on the cable and welt the locking-pliers with a copper
    mallet until the cable is a mess but the crimp hasn't let-go.
    Much more force than this polite requirement.

    ...
    https://s3vi.ndc.nasa.gov/ssri-kb/static/resources/nasa-std-8739.4a.pdf
    The pull test values are on page 54. Detailed operating instructions
    come with the crimping tool.
    ...

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From James Waldby@21:1/5 to Richard Smith on Wed Sep 20 18:12:28 2023
    Richard Smith <null@void.com> wrote:

    I'd appreciate fine detail on crimp connectors for "mains" electrics
    in a home.> Example - a "straight-through" connector looks something
    like this

    \___________/
    ___________
    / \

    to connect wires which go like this
    __ ___
    __|====== ======|___

    I got offcuts of Earthing cable and crimped them together and tried
    pulling them apart.

    I found that if you get the crimp tool "snug" up against flare of the
    outer end of the crimp-fitting the result is so strong you cannot
    feasibly pull the crimped cables apart.
    [... crimper links]
    Whereas if you clamp the crimp tool anywhere at the 1/4-length you can
    pull the assembly apart.
    [...]
    This is about the UK.
    Voltage 230V (r.m.s.) 50Hz AC.
    Regulation of electrical systems in and around buildings in the UK is
    known as "18th Edition". Which is also British Standard BS7671.
    It is very much more like an American "Code" (eg "ASME9", "AWS D1.1")
    rather than in ISO. Has developed in an evolutionary way over
    something like 140 years ("first edition" was in the 1880's).

    As I understand it, US code for line voltage wiring requires
    continuous runs without connectors when a wire run is concealed; any
    connection must be accessible. If that's not a UK requirement, US
    experience with crimped butt splices for mains power wire hidden away
    in house walls might be irrelevant, unsanctioned, or nonexistent.
    That aside, I imagine many of us have used butt splices for automotive
    etc low voltage wiring, or for motor wiring, and your comments on the
    splice strength depending on the crimp point are useful and welcome.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Leon Fisk@21:1/5 to Richard Smith on Wed Sep 20 13:55:23 2023
    On Wed, 20 Sep 2023 17:26:41 +0100
    Richard Smith <null@void.com> wrote:

    I'm talking about - one end of the cable in a vice, put a vice-grip / >locking-pliers on the cable and welt the locking-pliers with a copper
    mallet until the cable is a mess but the crimp hasn't let-go.
    Much more force than this polite requirement.
    <snip>

    For most applications that kind of pull-out isn't necessary and maybe
    not even desirable...

    Years ago we lost a large spruce tree during a storm. When it came down
    it pulled the Power Companies crimp connections apart where they
    connected to the house wires at the weather head/mast. So all I had to
    do was cut-off what was left of the crimp and use Split-Bolts to
    reattach them. Viola! I had power in the house again. Had those crimps
    held it would have pulled the mast down and/or tore part of my roof out.

    IMO you only get a perfect crimp connection with crimps, crimper and
    specific wire all made to be used together. If any of those three vary
    it will be either too tight or loose.

    Most of the failed crimps I came across while working were put on with
    the wrong crimp tool. Plastic tool used on bare crimp or worse the bare
    crimp tool used on plastic covered crimps.

    Then there were the ones that stripped the wire too long or didn't
    bother to strip it and crimped on the wire insulation...

    --
    Leon Fisk
    Grand Rapids MI

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Richard Smith@21:1/5 to All on Wed Sep 20 21:01:03 2023
    Thanks for comment.
    This is Earthing (Grounding) cable under floorboards - best if it
    stays together and then some...

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jim Wilkins@21:1/5 to All on Wed Sep 20 17:45:30 2023
    "Richard Smith" wrote in message news:lyfs38ajzy.fsf@void.com...

    Pull-out test:
    I'm talking about - one end of the cable in a vice, put a vice-grip / locking-pliers on the cable and welt the locking-pliers with a copper
    mallet until the cable is a mess but the crimp hasn't let-go.
    Much more force than this polite requirement.

    ----------------------------

    That test to destruction will prove your equipment and methods but isn't for checking each connection before installing it. The 'polite' pull test checks for crimps that didn't pressure-weld together. The wire should have a nearby strain relief clamp that protects the connection from being pulled apart
    during further installation or remodeling.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jim Wilkins@21:1/5 to Richard Smith on Wed Sep 20 18:20:06 2023
    "James Waldby" wrote in message news:uefcmb$32aeq$1@dont-email.me...

    Richard Smith <null@void.com> wrote:

    I'd appreciate fine detail on crimp connectors for "mains" electrics
    in a home.> Example - a "straight-through" connector looks something
    like this

    \___________/
    ___________
    / \

    to connect wires which go like this
    __ ___
    __|====== ======|___

    I got offcuts of Earthing cable and crimped them together and tried
    pulling them apart.

    I found that if you get the crimp tool "snug" up against flare of the
    outer end of the crimp-fitting the result is so strong you cannot
    feasibly pull the crimped cables apart.
    [... crimper links]
    Whereas if you clamp the crimp tool anywhere at the 1/4-length you can
    pull the assembly apart.
    [...]
    This is about the UK.
    Voltage 230V (r.m.s.) 50Hz AC.
    Regulation of electrical systems in and around buildings in the UK is
    known as "18th Edition". Which is also British Standard BS7671.
    It is very much more like an American "Code" (eg "ASME9", "AWS D1.1")
    rather than in ISO. Has developed in an evolutionary way over
    something like 140 years ("first edition" was in the 1880's).

    As I understand it, US code for line voltage wiring requires
    continuous runs without connectors when a wire run is concealed; any
    connection must be accessible.

    -------------------------

    In the amateur radio requirements for lightning grounds this is the
    acceptable copper splice:
    https://waterwelders.com/what-is-cad-welding/

    Although this strongly recommends against gas welding it suggests that it is still allowed to join copper grounds: https://www.britsafe.org/publications/safety-management-magazine/safety-management-magazine/2019/down-to-earth/

    You may be heading toward a situation where only illegal immigrants can
    perform dangerous tasks, like yours.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Richard Smith@21:1/5 to Jim Wilkins on Thu Sep 21 08:10:40 2023
    "Jim Wilkins" <muratlanne@gmail.com> writes:

    ...


    In the amateur radio requirements for lightning grounds this is the acceptable copper splice:
    https://waterwelders.com/what-is-cad-welding/

    Although this strongly recommends against gas welding it suggests that
    it is still allowed to join copper grounds: https://www.britsafe.org/publications/safety-management-magazine/safety-management-magazine/2019/down-to-earth/

    You may be heading toward a situation where only illegal immigrants
    can perform dangerous tasks, like yours.

    Another very interesting whole new view of how things can be done.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Richard Smith@21:1/5 to Jim Wilkins on Thu Sep 21 08:09:20 2023
    "Jim Wilkins" <muratlanne@gmail.com> writes:

    "Richard Smith" wrote in message news:lyfs38ajzy.fsf@void.com...

    Pull-out test:
    I'm talking about - one end of the cable in a vice, put a vice-grip / locking-pliers on the cable and welt the locking-pliers with a copper
    mallet until the cable is a mess but the crimp hasn't let-go.
    Much more force than this polite requirement.

    ----------------------------

    That test to destruction will prove your equipment and methods but
    isn't for checking each connection before installing it. The 'polite'
    pull test checks for crimps that didn't pressure-weld together. The
    wire should have a nearby strain relief clamp that protects the
    connection from being pulled apart during further installation or
    remodeling.

    Yes.
    But testing your process and finding out its characteristics,
    hopefully finding a robust operating mode which gives results
    somewhere up near ideal and/or certainly way beyond any reasonable
    acceptable threshold is the number-one in any manufacturing situation,
    surely?

    Coming from my unusual background and finding my own way, I have been
    amazed who people make things difficult and expensive for themselves
    and everyone looking at just creeping over the line with requirements.
    No dynamic thought about how the processes run and no thought of
    variables interaction.
    Where it would be a lot lot lot cheaper to look-at and consider the process(es), do rough-and-ready tests looking for amongst good guesses
    what gives good results - hopefully find one or more so close up
    to ideal and so broad in its stability range that the production run
    becomes low-cost.

    People get mesmerised by the minimum acceptance criterion/criteria, to
    the exclusion of all other.
    Sign of a "service economy / managerial / post-industrial world" ?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jim Wilkins@21:1/5 to Jim Wilkins on Thu Sep 21 08:47:32 2023
    "Richard Smith" wrote in message news:ly4jjo80kf.fsf@void.com...

    "Jim Wilkins" <muratlanne@gmail.com> writes:

    "Richard Smith" wrote in message news:lyfs38ajzy.fsf@void.com...

    Pull-out test:
    I'm talking about - one end of the cable in a vice, put a vice-grip / locking-pliers on the cable and welt the locking-pliers with a copper
    mallet until the cable is a mess but the crimp hasn't let-go.
    Much more force than this polite requirement.

    ----------------------------

    That test to destruction will prove your equipment and methods but
    isn't for checking each connection before installing it. The 'polite'
    pull test checks for crimps that didn't pressure-weld together. The
    wire should have a nearby strain relief clamp that protects the
    connection from being pulled apart during further installation or
    remodeling.

    Yes.
    But testing your process and finding out its characteristics,
    hopefully finding a robust operating mode which gives results
    somewhere up near ideal and/or certainly way beyond any reasonable
    acceptable threshold is the number-one in any manufacturing situation,
    surely?

    Coming from my unusual background and finding my own way, I have been
    amazed who people make things difficult and expensive for themselves
    and everyone looking at just creeping over the line with requirements.
    No dynamic thought about how the processes run and no thought of
    variables interaction.
    Where it would be a lot lot lot cheaper to look-at and consider the process(es), do rough-and-ready tests looking for amongst good guesses
    what gives good results - hopefully find one or more so close up
    to ideal and so broad in its stability range that the production run
    becomes low-cost.

    People get mesmerised by the minimum acceptance criterion/criteria, to
    the exclusion of all other.
    Sign of a "service economy / managerial / post-industrial world" ?

    ----------------------------

    I do what you suggest, and have the equipment to measure the results. It
    isn't common and may be expensive so I don't usually mention the procedures
    or necessary test gear here.

    Contact and crimp resistance: https://www.testequipmenthq.com/datasheets/KEITHLEY-580-Datasheet.pdf
    The voltage drop with 1.00A flowing through the connection is also a good measure, then 1mV = 1milliOhm.

    Insulation resistance:
    https://www.ebay.com/itm/274833931917
    It's also useful to test old electrical appliances. I've had to disassemble
    and clean a few to make them safe again.

    Overheating: https://www.vevor.com/thermal-imaging-camera-c_11961/vevor-infrared-thermal-imager-thermal-camera-ir-resolution-240x180-2-8-lcd-screen-p_010117537355?adp=gmc&utm_source=google&utm_medium=cpc&utm_id=20324005678&utm_term=
    I bought it to check the house insulation and found many other uses. It
    found hot and cold areas I had missed with an IR thermometer, and inner
    areas of a roasted chicken that weren't yet done.

    Pull force: https://www.vevor.com/crane-scale-c_10459/hanging-scale-crane-scale-1000-kg-2000-lb-digital-industrial-heavy-duty-auto-off-p_010231654597
    It's to proof test my home made hoisting equipment and check loads that
    might overstress it, mainly heavy logs and boulders. It also tests fiber and wire rope splice strength. This type failed: https://www.homedepot.com/p/Everbilt-3-16-in-Zinc-Plated-Flush-Type-Wire-Rope-Clamp-2-Pack-42984/205883072

    Applying the pull: https://www.homedepot.com/p/Vestil-2-000-lbs-Capacity-10-ft-Lift-Professional-Lever-Hoist-PLH-20-10/303099071
    It's much handier than a chainfall for horizontal pulls, though I think
    those are better and safer for vertical hoisting because you can lift higher and stand further away. My Harbor Freight 1300# electric hoist doesn't allow fine position control and starts with a considerable jolt that flexes the supporting beam.

    Those may not be the model I own or price I paid, often second-hand and
    overdue for calibration. I've been experimenting with the consequences of avoiding fossil fuel by using solar electricity and found several problems
    in available equipment with my test gear.

    Personally I want to be satisfied with my workmanship but commercially there was no reward for doing better than required if it took longer and cost
    more, which was typically the case once you learned to work efficiently. The requirements were supposed to be matched to the specs of available products, and generally were for US manufacturers. I don't see that with imports and
    test before using.

    https://www.vocabulary.com/dictionary/schlock

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jim Wilkins@21:1/5 to All on Thu Sep 21 09:50:19 2023
    "Richard Smith" wrote in message news:ly4jjo80kf.fsf@void.com...

    People get mesmerised by the minimum acceptance criterion/criteria, to
    the exclusion of all other.
    Sign of a "service economy / managerial / post-industrial world" ?

    ------------------------

    I've come to believe that acceptance criteria can be valid if written by
    people with both theoretical and practical knowledge, but they may prefer to avoid working in a bureaucracy, leaving neurotic paper-pushing staffers with literary degrees to formulate them from incomplete written sources. Mitre
    was an attempt to isolate scientists and engineers working on government projects from its bureaucracy. Yesterday a very hands-on and disgusted municipal employee and I were discussing how the bureaucracy is a welfare refuge for managers whose emotional dysfunction keeps them from working commercially.

    Like you my combination of knowledge and practical skills provokes envy and resentment from those who consider themselves inherently superior because it feels good, like the aristos of the Ancien Regime and today's leftists.

    Much of the Internet ad copy for high tech products and new developments appears to come from writers who don't comprehend the subject beyond quoting what they think they were told, and may lack the practical ability to change
    a light bulb or tie their shoelaces. Look at the insulting comments on the writer's incompetence that follow Yahoo high tech articles. I have
    experience here, I've struggled to teach actors how to build scenery and intelligent Mensans how to paddle a canoe. Hardly any could learn to tie a bowline. The actors felt such work was beneath them when really it was
    beyond them.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Leon Fisk@21:1/5 to Jim Wilkins on Thu Sep 21 10:55:06 2023
    On Thu, 21 Sep 2023 09:50:19 -0400
    "Jim Wilkins" <muratlanne@gmail.com> wrote:

    <snip>
    I have
    experience here, I've struggled to teach actors how to build scenery and >intelligent Mensans how to paddle a canoe. Hardly any could learn to tie a >bowline. The actors felt such work was beneath them when really it was >beyond them.

    Well said👍

    --
    Leon Fisk
    Grand Rapids MI

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Leon Fisk@21:1/5 to Jim Wilkins on Thu Sep 21 10:51:58 2023
    On Thu, 21 Sep 2023 08:47:32 -0400
    "Jim Wilkins" <muratlanne@gmail.com> wrote:

    <snip>
    wire rope splice strength. This type failed: >https://www.homedepot.com/p/Everbilt-3-16-in-Zinc-Plated-Flush-Type-Wire-Rope-Clamp-2-Pack-42984/205883072

    I had not seen those before. Makes for a nice end without all the sharp
    areas like U-Bolts do. Too bad it doesn't hold up well...

    It reminds me of the electric connector I liked to use for a triplex
    service hook-up:

    https://www.homedepot.com/p/Southwire-Single-Bolt-Parallel-Groove-Clamp-for-2-4-0-Wire-65176240/312648492

    Allows aluminum to copper connections and is easy to tighten up. Sucks
    to tape up but can't have every thing😉

    --
    Leon Fisk
    Grand Rapids MI

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jim Wilkins@21:1/5 to Jim Wilkins on Thu Sep 21 12:34:29 2023
    "Leon Fisk" wrote in message news:uehlae$3igm5$1@dont-email.me...

    On Thu, 21 Sep 2023 08:47:32 -0400
    "Jim Wilkins" <muratlanne@gmail.com> wrote:

    <snip>
    wire rope splice strength. This type failed: >https://www.homedepot.com/p/Everbilt-3-16-in-Zinc-Plated-Flush-Type-Wire-Rope-Clamp-2-Pack-42984/205883072

    I had not seen those before. Makes for a nice end without all the sharp
    areas like U-Bolts do. Too bad it doesn't hold up well...

    ---------------------------

    IIRC it slipped at around 100#. I had tightened it by hand in the woods, it might grip better if tightened with an impact driver, or a cap screw substituted. They could be useful to drag an eye splice over a high branch
    or minimize the fumbling of installing Crosby clamps and thimbles.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Leon Fisk@21:1/5 to Jim Wilkins on Thu Sep 21 13:35:35 2023
    On Thu, 21 Sep 2023 12:34:29 -0400
    "Jim Wilkins" <muratlanne@gmail.com> wrote:

    <snip>
    IIRC it slipped at around 100#. I had tightened it by hand in the woods, it >might grip better if tightened with an impact driver, or a cap screw >substituted. They could be useful to drag an eye splice over a high branch >or minimize the fumbling of installing Crosby clamps and thimbles.

    It's stored in my head now. For some unknown reason I remember stuff
    like that for a long time. Neighbor's name down the street is a
    different story🙄

    Could be useful, keeping in mind that it may not be a "strong"
    connection... Thanks!

    --
    Leon Fisk
    Grand Rapids MI

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Snag@21:1/5 to Jim Wilkins on Thu Sep 21 15:34:39 2023
    On 9/21/2023 8:50 AM, Jim Wilkins wrote:
    "Richard Smith"  wrote in message news:ly4jjo80kf.fsf@void.com...

    People get mesmerised by the minimum acceptance criterion/criteria, to
    the exclusion of all other.
    Sign of a "service economy / managerial / post-industrial world" ?

    ------------------------

    I've come to believe that acceptance criteria can be valid if written by people with both theoretical and practical knowledge, but they may
    prefer to avoid working in a bureaucracy, leaving neurotic paper-pushing staffers with literary degrees to formulate them from incomplete written sources.  Mitre was an attempt to isolate scientists and engineers
    working on government projects from its bureaucracy. Yesterday a very hands-on and disgusted municipal employee and I were discussing how the bureaucracy is a welfare refuge for managers whose emotional dysfunction keeps them from working commercially.

    Like you my combination of knowledge and practical skills provokes envy
    and resentment from those who consider themselves inherently superior
    because it feels good, like the aristos of the Ancien Regime and today's leftists.

    Much of the Internet ad copy for high tech products and new developments appears to come from writers who don't comprehend the subject beyond
    quoting what they think they were told, and may lack the practical
    ability to change a light bulb or tie their shoelaces. Look at the
    insulting comments on the writer's incompetence that follow Yahoo high
    tech articles. I have experience here, I've struggled to teach actors
    how to build scenery and intelligent Mensans how to paddle a canoe.
    Hardly any could learn to tie a bowline. The actors felt such work was beneath them when really it was beyond them.


    I am very lucky to live among people (our little community down here
    in The Holler) who appreciate and utilize my talents rather than being intimidated by them . Of course , every one of them has areas where they
    shine , and I appreciate that too .
    --
    Snag
    Men don't protect women because they're weak .
    We protect them because they're important .

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)