• Determining boiler size from serial number

    From Tim+@21:1/5 to All on Mon Feb 12 18:37:48 2024
    We’re looking into getting an ASHP but I’m unsure of the capacity of our current Vaillant ecoMAX pro boiler as all our installation and other
    manuals are for 18 and 28kW boilers which I believe are the same
    externally.

    There are no easily accessible ID plates but I do have the serial number that’s been copied into the installation guide.

    Before I go bothering Vaillant on the phone does anyone know how to ID our boiler? FWIW, ours is a 5 bedroom house from the early 70s so I’m guessing it’s *probably* the 28kW but I could be wrong.

    Tim
    --
    Please don't feed the trolls

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to All on Mon Feb 12 18:52:31 2024
    On 12/02/2024 18:37, Tim+ wrote:
    We’re looking into getting an ASHP
    Punches advice to people lookimg to get an ASHP.
    Dont.
    You'll be lucky to get 10KW out of one.,

    --
    "I am inclined to tell the truth and dislike people who lie consistently.
    This makes me unfit for the company of people of a Left persuasion, and
    all women"

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to timdownieuk@yahoo.co.youkay on Mon Feb 12 21:43:57 2024
    Tim+ <timdownieuk@yahoo.co.youkay> wrote:

    We’re looking into getting an ASHP but I’m unsure of the capacity of our current Vaillant ecoMAX pro boiler as all our installation and other
    manuals are for 18 and 28kW boilers which I believe are the same
    externally.

    There are no easily accessible ID plates but I do have the serial number that’s been copied into the installation guide.

    Before I go bothering Vaillant on the phone does anyone know how to ID our boiler? FWIW, ours is a 5 bedroom house from the early 70s so I’m guessing it’s *probably* the 28kW but I could be wrong.

    Your boiler is almost certainly oversized so the size is irrelevant really.
    In the depth of winter does it run continuously or does it cycle on and
    off (assuming you have the heating on for a long time, not running it for an hour here or there)? If it cycles, then it's oversized.

    Do a heat loss calculation and that'll tell you what size you actually need.

    Assuming you want the ASHP to do hot water too, work out what size cylinder
    you have / want and then you can calculate the time to heat it with a given size of heat pump.

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year round,
    for less we spent being barely warm on oil)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Spike@21:1/5 to Theo on Tue Feb 13 09:01:21 2024
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    […]

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year round, for less we spent being barely warm on oil)

    Is that comparing like for like, such as ‘oil boiler +
    some insulation’ with ‘ASHP with the same insulation’,
    or with ‘ASHP + lots of new insulation’?

    --
    Spike

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Spike on Tue Feb 13 09:51:34 2024
    On 13/02/2024 09:01, Spike wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    […]

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year round, >> for less we spent being barely warm on oil)

    Is that comparing like for like, such as ‘oil boiler +
    some insulation’ with ‘ASHP with the same insulation’,
    or with ‘ASHP + lots of new insulation’?

    Same thought occurred to me.

    I commissioned my Pi based heating controller and zone thermometers in December, and by fine tuning it to my actual needs I think I have cut
    about £1000 off the winter heating bill, And feel warmer.

    For less than £150 worth of custom designed bits and a week or three of software.

    ASHP works if the house is built for it. It almost never works on larger
    or older properties. Or where winters are exceptionally cold. And, if
    you are saving money with it at current prices, there was something
    wrong with whatever it replaced.

    --
    "I guess a rattlesnake ain't risponsible fer bein' a rattlesnake, but ah
    puts mah heel on um jess the same if'n I catches him around mah chillun".

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to John J on Tue Feb 13 10:24:26 2024
    John J <johnjessop46@gmail.com> wrote:
    There is a vaillant air source heat pump Facebook group which you would do well to spend some time reading. To achieve similar comfort conditions at reasonable running cost you WILL have to alter your lifestyle. You WILL
    have to run your radiators at much lower (40 degree) temperatures than
    with your boiler thus normally requiring swapping out for larger sizes
    which may also require pipe changes. You will find a massive problem with ongoing maintenance of the external unit refrigerant containing section
    and discover there are huge numbers of throw it in and run cowboys who somehow have become "registered" with mcs but when push comes to shove
    don't expect help from them. If you do pursue swapping to a heat pump
    check out the installation company on trustpilot and believe the bad
    reviews more than the good ones.

    You'd do well to get an installer who is Heat Geek certified. They know
    their stuff and you're likely to get an install that is properly designed.
    The MCS certification is about 'quality' but more of a box ticking exercise rather than teaching people about the fundamentals of good system design.

    The Skill Builder Youtube channel is run by a guy who is a heat pump
    skeptic, and there's an interesting series of videos between him and the guy who runs Heat Geek. The current series has them look at a botched install
    by a fly by night company, and how Heat Geek came in and worked out what was wrong with the old install (several basic errors). They're now in the
    process of fixing it.

    Playlist (start at the bottom): https://www.youtube.com/playlist?list=PLvRh7uimDQfdltavC53l7917QDwPwUBUO

    Heat Geek also has a lot of handy videos:
    https://www.youtube.com/@HeatGeek

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Spike on Tue Feb 13 10:17:00 2024
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    […]

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year
    round, for less we spent being barely warm on oil)

    Is that comparing like for like, such as ‘oil boiler +
    some insulation’ with ‘ASHP with the same insulation’,
    or with ‘ASHP + lots of new insulation’?

    Identical amounts of insulation, which is crap tbh - 80/100mm of fibreglass loft insulation, but the loft is only a crawlspace so putting more in would make it impossible to crawl. Redoing that lot with PIR is on the todo list
    but it's such a PITA to access.

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tim+@21:1/5 to Theo on Tue Feb 13 10:59:07 2024
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Tim+ <timdownieuk@yahoo.co.youkay> wrote:

    We’re looking into getting an ASHP but I’m unsure of the capacity of our >> current Vaillant ecoMAX pro boiler as all our installation and other
    manuals are for 18 and 28kW boilers which I believe are the same
    externally.

    There are no easily accessible ID plates but I do have the serial number
    that’s been copied into the installation guide.

    Before I go bothering Vaillant on the phone does anyone know how to ID our >> boiler? FWIW, ours is a 5 bedroom house from the early 70s so I’m guessing
    it’s *probably* the 28kW but I could be wrong.

    Your boiler is almost certainly oversized so the size is irrelevant really.

    I’ve come around to that idea too. Decided that gas consumption over the year is probably a more useful measure.


    In the depth of winter does it run continuously or does it cycle on and
    off (assuming you have the heating on for a long time, not running it for an hour here or there)? If it cycles, then it's oversized.

    Do a heat loss calculation and that'll tell you what size you actually need.

    Assuming you want the ASHP to do hot water too, work out what size cylinder you have / want and then you can calculate the time to heat it with a given size of heat pump.


    Less fussed about water heating. It’s only costing 35p a day on cheap rate power at present. Designing the system around the hot water requirements rather than the house heating needs seems an odd way to do things if one’s interested in optimum efficiency.

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year round, for less we spent being barely warm on oil)


    That can’t possibly be true. TNP has spoken otherwise. ;-)

    Tim


    --
    Please don't feed the trolls

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Spike@21:1/5 to Theo on Tue Feb 13 13:58:47 2024
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    […]

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year
    round, for less we spent being barely warm on oil)

    Is that comparing like for like, such as ‘oil boiler +
    some insulation’ with ‘ASHP with the same insulation’,
    or with ‘ASHP + lots of new insulation’?

    Identical amounts of insulation, which is crap tbh - 80/100mm of fibreglass loft insulation, but the loft is only a crawlspace so putting more in would make it impossible to crawl. Redoing that lot with PIR is on the todo list but it's such a PITA to access.

    Thanks for that.

    With such a difference in costs and effectiveness between oil and ASHP, I’m tempted to ask what was wrong with the oil-fired set-up!

    As regards the loft insulation, could you get a man in to spray-insulate
    it? I’ll get my coat…


    --
    Spike

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Spike on Tue Feb 13 14:42:23 2024
    Spike <aero.spike@mail.com> wrote:
    Thanks for that.

    With such a difference in costs and effectiveness between oil and ASHP, I’m tempted to ask what was wrong with the oil-fired set-up!

    The oil boiler (20yo) was a rusty pile of ***** and died. I didn't know you could weld oil boilers like you weld old cars, but this one had been welded until there was nothing left but rust to weld. The radiators were ancient
    too.

    Also it needed a giant tank in the garden which was a big waste of space.

    The ASHP costs less to run and is more comfortable than oil, so no point reinstalling oil.

    As regards the loft insulation, could you get a man in to spray-insulate
    it? I’ll get my coat…

    :-) Spray foam is ok if done right, as they do in the US. Trouble is in
    the UK we don't do it enough to trust they're doing it right.

    It's not helped by the loft insulation being where all the pipes and wires
    go, so access is needed to them occasionally. At least with PIR you can
    pull it up if you need access.

    One thought is to line the ceilings on the most awkward side with PIR-backed plasterboard, which would cover some dubious Artex and give an extra layer without taking height from the loft. And maybe on the other side put some
    PIR between the rafters.

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Spike on Tue Feb 13 15:37:25 2024
    On 13/02/2024 13:58, Spike wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    […]

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year
    round, for less we spent being barely warm on oil)

    Is that comparing like for like, such as ‘oil boiler +
    some insulation’ with ‘ASHP with the same insulation’,
    or with ‘ASHP + lots of new insulation’?

    Identical amounts of insulation, which is crap tbh - 80/100mm of fibreglass >> loft insulation, but the loft is only a crawlspace so putting more in would >> make it impossible to crawl. Redoing that lot with PIR is on the todo list >> but it's such a PITA to access.

    Thanks for that.

    With such a difference in costs and effectiveness between oil and ASHP, I’m tempted to ask what was wrong with the oil-fired set-up!

    precisely. Oil at the moment is about 65p a litre which equates to
    around 6.5p/kWh.
    Even at 4:1 uplift on an ASHP which is a miracle in winter, that's 26p a
    unit equivalent electricity.

    I am suspicious. It sounds like the old 'double glazing saved me
    thousands' which turned out to actually mean 'having windows that didn't
    have draughts saved me thousands'



    As regards the loft insulation, could you get a man in to spray-insulate
    it? I’ll get my coat…



    --
    When plunder becomes a way of life for a group of men in a society, over
    the course of time they create for themselves a legal system that
    authorizes it and a moral code that glorifies it.

    Frédéric Bastiat

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From alan_m@21:1/5 to Theo on Tue Feb 13 17:13:21 2024
    On 13/02/2024 10:24, Theo wrote:

    You'd do well to get an installer who is Heat Geek certified. They know their stuff and you're likely to get an install that is properly designed.

    The Skill Builder Youtube channel is run by a guy who is a heat pump
    skeptic, and there's an interesting series of videos between him and the guy who runs Heat Geek. The current series has them look at a botched install
    by a fly by night company,

    From what I've seen on both channels with reference to ASHP:-

    It helps to fully research the subject of ASHP yourself before you get a company involved to be able to see through much of the BS.

    Putting in a ASHP is not simple as a simple boiler swap. Much of an
    existing system may also have to be replaced or at least fully evaluated
    before selecting a ASHP.

    Watch out for ASHP that are designed for higher temperatures that are
    maybe considered for 60C DHW. They will not be as efficient, COP wise,
    as those working at, say, 40C. The salesman will give you the costs
    associated with running the 40C system but probably not mention what
    happens to efficiency when the output temperature rise.

    Both channels admit that when it comes to systems running at low
    temperatures the standard of training (and skill level) in the industry
    is dire.


    --
    mailto : news {at} admac {dot} myzen {dot} co {dot} uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tim+@21:1/5 to Spike on Tue Feb 13 18:19:38 2024
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    […]

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year
    round, for less we spent being barely warm on oil)

    Is that comparing like for like, such as ‘oil boiler +
    some insulation’ with ‘ASHP with the same insulation’,
    or with ‘ASHP + lots of new insulation’?

    Identical amounts of insulation, which is crap tbh - 80/100mm of fibreglass >> loft insulation, but the loft is only a crawlspace so putting more in would >> make it impossible to crawl. Redoing that lot with PIR is on the todo list >> but it's such a PITA to access.

    Thanks for that.

    With such a difference in costs and effectiveness between oil and ASHP, I’m tempted to ask what was wrong with the oil-fired set-up!

    Hard to generate your own oil. Electricity from solar panels is a lot
    easier.

    Tim

    --
    Please don't feed the trolls

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to All on Tue Feb 13 19:57:42 2024
    On 13/02/2024 18:19, Tim+ wrote:
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    […]

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year >>>>> round, for less we spent being barely warm on oil)

    Is that comparing like for like, such as ‘oil boiler +
    some insulation’ with ‘ASHP with the same insulation’,
    or with ‘ASHP + lots of new insulation’?

    Identical amounts of insulation, which is crap tbh - 80/100mm of fibreglass >>> loft insulation, but the loft is only a crawlspace so putting more in would >>> make it impossible to crawl. Redoing that lot with PIR is on the todo list >>> but it's such a PITA to access.

    Thanks for that.

    With such a difference in costs and effectiveness between oil and ASHP, I’m
    tempted to ask what was wrong with the oil-fired set-up!

    Hard to generate your own oil. Electricity from solar panels is a lot easier.

    Harder to generate your won solar panels.

    Christ, the green tendency are thicker than two short planks.

    Tim


    --
    I would rather have questions that cannot be answered...
    ...than to have answers that cannot be questioned

    Richard Feynman

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to All on Tue Feb 13 20:17:58 2024
    On 13/02/2024 10:59, Tim+ wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Tim+ <timdownieuk@yahoo.co.youkay> wrote:

    We’re looking into getting an ASHP but I’m unsure of the capacity of our
    current Vaillant ecoMAX pro boiler as all our installation and other
    manuals are for 18 and 28kW boilers which I believe are the same
    externally.

    There are no easily accessible ID plates but I do have the serial number >>> that’s been copied into the installation guide.

    Before I go bothering Vaillant on the phone does anyone know how to ID our >>> boiler? FWIW, ours is a 5 bedroom house from the early 70s so I’m guessing
    it’s *probably* the 28kW but I could be wrong.

    Your boiler is almost certainly oversized so the size is irrelevant really.

    I’ve come around to that idea too. Decided that gas consumption over the year is probably a more useful measure.

    Isn't there a blog of comparing gas consumption with ASHP needs? I'm
    sure someone posted a link here a while ago.

    In the depth of winter does it run continuously or does it cycle on and
    off (assuming you have the heating on for a long time, not running it for an >> hour here or there)? If it cycles, then it's oversized.

    Do a heat loss calculation and that'll tell you what size you actually need. >>
    Assuming you want the ASHP to do hot water too, work out what size cylinder >> you have / want and then you can calculate the time to heat it with a given >> size of heat pump.


    Less fussed about water heating. It’s only costing 35p a day on cheap rate power at present. Designing the system around the hot water requirements rather than the house heating needs seems an odd way to do things if one’s interested in optimum efficiency.

    And in the summer given the short term firing times and typical cycling
    of a boiler heating hot water might have significant losses.

    Theo

    (whose ASHP works just fine, for the record. Nice and warm all year round, >> for less we spent being barely warm on oil)


    That can’t possibly be true. TNP has spoken otherwise. ;-)

    I would agree with TNP, and the only way it becomes cheap enough to run
    is with further insulation.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Lee@21:1/5 to All on Tue Feb 13 22:45:42 2024
    On 13/02/2024 10:59, Tim+ wrote:

    Precious few of them in Scotland and the nearest “heat geek verified” one hasn’t ever got back to us to quote. Our local heat geek certified fitter quoted over £25,000. Don’t think he wanted the job.

    Where are you? I can recommend two excellent fitters.
    Heat Geek 'verified' only means they have passed the HG courses, and
    registered for the website listing. At least one person in the Company
    has done the course and passed, but, after that HG dont have any say in
    what they do, or how they work. I'm on that list on their website.

    HG Elite is the 'better' installers, who, again, have passed the HG
    courses, but they also pay HG a monthly fee to be part of the 'elite'.
    Again, only one person in the company may have done the course, there is
    a little bit more assurance, as they can lose their status if there are
    upheld complaints. They are not a Trade Assn., they are promoting good
    work by heating fitters, and trying to get a better standard of install,
    but, they cannot inspect every install done by their 'accredited' Companies.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Andrew@21:1/5 to All on Wed Feb 14 13:08:33 2024
    On 13/02/2024 10:59, Tim+ wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    John J <johnjessop46@gmail.com> wrote:
    There is a vaillant air source heat pump Facebook group which you would do >>> well to spend some time reading. To achieve similar comfort conditions at >>> reasonable running cost you WILL have to alter your lifestyle. You WILL >>> have to run your radiators at much lower (40 degree) temperatures than
    with your boiler thus normally requiring swapping out for larger sizes
    which may also require pipe changes. You will find a massive problem with >>> ongoing maintenance of the external unit refrigerant containing section
    and discover there are huge numbers of throw it in and run cowboys who
    somehow have become "registered" with mcs but when push comes to shove
    don't expect help from them. If you do pursue swapping to a heat pump
    check out the installation company on trustpilot and believe the bad
    reviews more than the good ones.

    You'd do well to get an installer who is Heat Geek certified. They know
    their stuff and you're likely to get an install that is properly designed. >> The MCS certification is about 'quality' but more of a box ticking exercise >> rather than teaching people about the fundamentals of good system design.

    Precious few of them in Scotland and the nearest “heat geek verified” one hasn’t ever got back to us to quote. Our local heat geek certified fitter quoted over £25,000. Don’t think he wanted the job.

    Tim


    An early 70's house (detached?) will have almost no effective
    insulation at all, except perhaps a thin layer of loft
    insulation. It may have had replacement DG during its
    lifetime, and some more loft insulation, but it will be the
    heatloss through the walls and (?solid) ground floor that is
    the issue.

    A combination of cavity wall insulation (to stop air movement
    inside the cavity) as well as external wall insulation is probably
    the thing to spend your money on. The original house will have
    a cavity that is only 50mm or 65mm, so filling that will only
    offer marginal improvement (unless there is significant air
    movement through the cavity). In Scotland there is the issue
    of driving rain, so cavity insulation on its own might have
    unexpected downsides. Adding external wall insulation as well
    will add a new external rain skin because of the extra
    render.

    That leaves the (?solid) ground floor which might be fixable
    but that involves digging out the screed and replacing with
    PIR between battens screwed into the slab and a new timber
    floor. If the screed has sufficient depth then you might be
    able to consider underfloor heating but this is highly
    disruptive and costly, unless you can diy it. External wall
    insulation would only need outside pipework to be relocated.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Andrew on Wed Feb 14 22:22:29 2024
    Andrew <Andrew97d@btinternet.com> wrote:
    An early 70's house (detached?) will have almost no effective
    insulation at all, except perhaps a thin layer of loft
    insulation. It may have had replacement DG during its
    lifetime, and some more loft insulation, but it will be the
    heatloss through the walls and (?solid) ground floor that is
    the issue.

    It is highly likely that a 70s house will have had cavity wall insulation installed by now, in the 90s if not before.

    A combination of cavity wall insulation (to stop air movement
    inside the cavity) as well as external wall insulation is probably
    the thing to spend your money on. The original house will have
    a cavity that is only 50mm or 65mm, so filling that will only
    offer marginal improvement (unless there is significant air
    movement through the cavity). In Scotland there is the issue
    of driving rain, so cavity insulation on its own might have
    unexpected downsides. Adding external wall insulation as well
    will add a new external rain skin because of the extra
    render.

    Just doing a cavity fill isn't perfect, but a lot better than nothing - much more than marginal.

    An unfilled cavity wall has a U value of about 1.6, when filled it's about
    0.3. So reduces the heat loss by 80%.

    That and loft insulation are the easiest and cheapest to do, if you haven't already.

    That leaves the (?solid) ground floor which might be fixable
    but that involves digging out the screed and replacing with
    PIR between battens screwed into the slab and a new timber
    floor. If the screed has sufficient depth then you might be
    able to consider underfloor heating but this is highly
    disruptive and costly, unless you can diy it. External wall
    insulation would only need outside pipework to be relocated.

    An uninsulated floor contributes about 10% of your heat loss. For many
    people the costs of redoing a solid floor means this isn't worth chasing.
    A simple way to insulate is carpets with good underlay - it's not in the
    same league as PIR, but if you're installing carpets anyway then it helps.

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Spike@21:1/5 to Theo on Thu Feb 15 10:06:43 2024
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Andrew <Andrew97d@btinternet.com> wrote:
    An early 70's house (detached?) will have almost no effective
    insulation at all, except perhaps a thin layer of loft
    insulation. It may have had replacement DG during its
    lifetime, and some more loft insulation, but it will be the
    heatloss through the walls and (?solid) ground floor that is
    the issue.

    It is highly likely that a 70s house will have had cavity wall insulation installed by now, in the 90s if not before.

    A combination of cavity wall insulation (to stop air movement
    inside the cavity) as well as external wall insulation is probably
    the thing to spend your money on. The original house will have
    a cavity that is only 50mm or 65mm, so filling that will only
    offer marginal improvement (unless there is significant air
    movement through the cavity). In Scotland there is the issue
    of driving rain, so cavity insulation on its own might have
    unexpected downsides. Adding external wall insulation as well
    will add a new external rain skin because of the extra
    render.

    Just doing a cavity fill isn't perfect, but a lot better than nothing - much more than marginal.

    An unfilled cavity wall has a U value of about 1.6, when filled it's about 0.3. So reduces the heat loss by 80%.

    That and loft insulation are the easiest and cheapest to do, if you
    haven't if you haven't already.

    There are a number of firms that specialise in cavity-wall insulation
    removal, which isn’t a cheap exercise, and there’s also the Cavity Insulation Victims Alliance who try to get some form of justice for
    sufferers of mis-sold CWI.

    CWI is not a universally-acceptable procedure.


    --
    Spike

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Spike on Thu Feb 15 11:42:01 2024
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    There are a number of firms that specialise in cavity-wall insulation
    removal, which isn’t a cheap exercise, and there’s also the Cavity
    Insulation Victims Alliance who try to get some form of justice for
    sufferers of mis-sold CWI.

    CWI is not a universally-acceptable procedure.

    Agreed it's not an panacaea, but I'd have thought a 1970s brick+block construction would be relatively uncomplicated? It's not into lime mortar and breatheable paints territory.

    I did see a map somewhere that showed that large parts of the UK were unsuitable for CWI due to the threat posed by heavy driving rain. IIRC the whole of Wales and the South West were one such area.

    I'd have thought that could be addressed by sealing the bricks from the outside, so there's no water penetration by the rain. A lot of properties
    in eg Wales and Scotland are painted or rendered which takes care of the sealing.

    This is Ireland, which is known for being moist: https://www.nsai.ie/images/uploads/certification-agrement/IAB050222.pdf

    "3.5.2.1.2 Severe Exposure
    Severe exposure to wind-driven rain applies in
    districts where the driving rain index is
    5m²/sec/year or greater (see Figure 2).
    In severe exposure areas the type of outer leaf
    masonry finish where the Rockwool Blown Cavity
    Wall Insulation System is suitable is:
    * Impervious cladding and rendered walls with a
    minimum cavity width of 50 mm and up to
    12m in height.
    * Walls must be in a good state of repair with
    no evidence of frost damage and no evidence
    of damage which would cause water ingress.
    Unrendered brickwork is not suitable for full-fill
    cavity wall insulation in the severe exposure
    zones"

    (in other words, sounds like the usual story of cowboy installers and then ambulance-chasing removals firms)

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Spike@21:1/5 to Theo on Thu Feb 15 11:50:17 2024
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    There are a number of firms that specialise in cavity-wall insulation
    removal, which isn’t a cheap exercise, and there’s also the Cavity >>>> Insulation Victims Alliance who try to get some form of justice for
    sufferers of mis-sold CWI.

    CWI is not a universally-acceptable procedure.

    Agreed it's not an panacaea, but I'd have thought a 1970s brick+block
    construction would be relatively uncomplicated? It's not into lime mortar >>> and breatheable paints territory.

    I did see a map somewhere that showed that large parts of the UK were
    unsuitable for CWI due to the threat posed by heavy driving rain. IIRC the >> whole of Wales and the South West were one such area.

    I'd have thought that could be addressed by sealing the bricks from the outside, so there's no water penetration by the rain. A lot of properties
    in eg Wales and Scotland are painted or rendered which takes care of the sealing.

    This is Ireland, which is known for being moist: https://www.nsai.ie/images/uploads/certification-agrement/IAB050222.pdf

    "3.5.2.1.2 Severe Exposure
    Severe exposure to wind-driven rain applies in
    districts where the driving rain index is
    5m²/sec/year or greater (see Figure 2).
    In severe exposure areas the type of outer leaf
    masonry finish where the Rockwool Blown Cavity
    Wall Insulation System is suitable is:
    * Impervious cladding and rendered walls with a
    minimum cavity width of 50 mm and up to
    12m in height.
    * Walls must be in a good state of repair with
    no evidence of frost damage and no evidence
    of damage which would cause water ingress.
    Unrendered brickwork is not suitable for full-fill
    cavity wall insulation in the severe exposure
    zones"

    (in other words, sounds like the usual story of cowboy installers and then ambulance-chasing removals firms)

    Ah…the map I mentioned can be found here:

    <https://www.labc.co.uk/news/full-fill-masonry-cavity-walls-and-exposure-wind-driven-rain>

    --
    Spike

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Spike on Thu Feb 15 11:17:05 2024
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    Just doing a cavity fill isn't perfect, but a lot better than nothing - much
    more than marginal.

    An unfilled cavity wall has a U value of about 1.6, when filled it's about 0.3. So reduces the heat loss by 80%.

    That and loft insulation are the easiest and cheapest to do, if you
    haven't if you haven't already.

    There are a number of firms that specialise in cavity-wall insulation removal, which isn’t a cheap exercise, and there’s also the Cavity Insulation Victims Alliance who try to get some form of justice for
    sufferers of mis-sold CWI.

    CWI is not a universally-acceptable procedure.

    Agreed it's not an panacaea, but I'd have thought a 1970s brick+block construction would be relatively uncomplicated? It's not into lime mortar
    and breatheable paints territory.

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Spike@21:1/5 to Theo on Thu Feb 15 11:21:19 2024
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:

    Just doing a cavity fill isn't perfect, but a lot better than nothing - much
    more than marginal.

    An unfilled cavity wall has a U value of about 1.6, when filled it's about >>> 0.3. So reduces the heat loss by 80%.

    That and loft insulation are the easiest and cheapest to do, if you
    haven't if you haven't already.

    There are a number of firms that specialise in cavity-wall insulation
    removal, which isn’t a cheap exercise, and there’s also the Cavity
    Insulation Victims Alliance who try to get some form of justice for
    sufferers of mis-sold CWI.

    CWI is not a universally-acceptable procedure.

    Agreed it's not an panacaea, but I'd have thought a 1970s brick+block construction would be relatively uncomplicated? It's not into lime mortar and breatheable paints territory.

    I did see a map somewhere that showed that large parts of the UK were unsuitable for CWI due to the threat posed by heavy driving rain. IIRC the whole of Wales and the South West were one such area.

    --
    Spike

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Spike on Thu Feb 15 12:11:57 2024
    Spike <aero.spike@mail.com> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    I'd have thought that could be addressed by sealing the bricks from the outside, so there's no water penetration by the rain. A lot of properties in eg Wales and Scotland are painted or rendered which takes care of the sealing.

    This is Ireland, which is known for being moist: https://www.nsai.ie/images/uploads/certification-agrement/IAB050222.pdf

    "3.5.2.1.2 Severe Exposure
    Severe exposure to wind-driven rain applies in
    districts where the driving rain index is
    5m²/sec/year or greater (see Figure 2).
    In severe exposure areas the type of outer leaf
    masonry finish where the Rockwool Blown Cavity
    Wall Insulation System is suitable is:
    * Impervious cladding and rendered walls with a
    minimum cavity width of 50 mm and up to
    12m in height.
    * Walls must be in a good state of repair with
    no evidence of frost damage and no evidence
    of damage which would cause water ingress.
    Unrendered brickwork is not suitable for full-fill
    cavity wall insulation in the severe exposure
    zones"

    (in other words, sounds like the usual story of cowboy installers and then ambulance-chasing removals firms)

    Ah…the map I mentioned can be found here:

    <https://www.labc.co.uk/news/full-fill-masonry-cavity-walls-and-exposure-wind-driven-rain>

    Yep, that page is talking about new builds rather than retrofits (hence
    cavity sizes are something you can control at design time), but it does make the point that rendering or cladding can allow you to have a full cavity because there's now an impervious layer to stop the bricks getting wet, and
    so the drying function of the cavity isn't needed any more.

    (in other words bricks are a poor rainscreen and better to have a rainscreen which is designed for that job in front of the bricks)

    Theo