    From Tricky Dicky@21:1/5 to All on Wed Jan 3 16:07:46 2024
    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in conjunction with the bathroom light so that the fan comes on when the light
    is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans in the rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as
    planned and using two FCU’s
    One for live and the other for switched live before running the rest of the cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My daughters
    new build has one bathroom, 2 en-suites and a cloakroom/WC all windowless
    and all with ventilators activated by the light switch and I know all the lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for the MF100T
    has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Dicky on Wed Jan 3 16:34:04 2024
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in conjunction with the bathroom light so that the fan comes on when the light is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and switched live and of course the lighting circuit is 6A.

    https://www.tlc-direct.co.uk/Products/CLCMA3020.html

    would do it. Although if it's a 6A MCB I personally wouldn't be devastated
    if there wasn't a separate 3A fuse (but not strictly per mfr instructions
    which might cause troubles elsewhere).

    Or do you need a pull cord isolator?

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Robin@21:1/5 to Tricky Dicky on Wed Jan 3 16:37:00 2024
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in conjunction with the bathroom light so that the fan comes on when the light is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the bathroom but that means all lights beyond that point would now be protected by a 3A fuse and the issue is that there are at least 3 ceiling fans in the rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as planned and using two FCU’s
    One for live and the other for switched live before running the rest of the cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My daughters new build has one bathroom, 2 en-suites and a cloakroom/WC all windowless
    and all with ventilators activated by the light switch and I know all the lighting circuits are 6A.

    So what to do?


    I may be missing something but why not /one/ FCU protecting a branch
    from the light circuit to /only/ the light and fan?



    https://groups.google.com/g/uk.d-i-y/c/lU5icmzsuCM/m/b05BvGWYDwAJ
    --
    Robin
    reply-to address is (intended to be) valid

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From nothanks@aolbin.com@21:1/5 to Tricky Dicky on Wed Jan 3 16:48:17 2024
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in conjunction with the bathroom light so that the fan comes on when the light is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the bathroom but that means all lights beyond that point would now be protected by a 3A fuse and the issue is that there are at least 3 ceiling fans in the rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as planned and using two FCU’s
    One for live and the other for switched live before running the rest of the cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My daughters new build has one bathroom, 2 en-suites and a cloakroom/WC all windowless
    and all with ventilators activated by the light switch and I know all the lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for the MF100T has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    Not an answer, but a suggestion: consider having two pull switches, one
    for the fan and one for the light, rather than having the fan always
    come on with the light. This means you don't have the fan noise at night
    time and you can leave the fan on for a while in the morning after a
    vindaloo supper the night before.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to Robin on Wed Jan 3 16:58:41 2024
    Robin <rbw@outlook.com> wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in
    conjunction with the bathroom light so that the fan comes on when the light >> is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and >> switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be protected >> by a 3A fuse and the issue is that there are at least 3 ceiling fans in the >> rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as
    planned and using two FCU’s
    One for live and the other for switched live before running the rest of the >> cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My daughters >> new build has one bathroom, 2 en-suites and a cloakroom/WC all windowless
    and all with ventilators activated by the light switch and I know all the
    lighting circuits are 6A.

    So what to do?


    I may be missing something but why not /one/ FCU protecting a branch
    from the light circuit to /only/ the light and fan?



    https://groups.google.com/g/uk.d-i-y/c/lU5icmzsuCM/m/b05BvGWYDwAJ

    Thanks Robin that idea came to mind shortly after I posted. So thanks for
    the link to the earlier thread and I think that will be the way to go. I
    have used the 3-plate method but because of the 22deg pitch of our roof I rewired the lighting circuit with a series of Wago boxes in the area where there was a bit of headroom with single cable feeds going to the various
    light fittings. So if I feed the existing feed and the ongoing feed to the
    next light to the input side of the FCU I can then take the output into the existing Wago box for the bathroom light and make all my connections there.

    Thanks again

    Richard

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Lee@21:1/5 to Tricky Dicky on Wed Jan 3 18:41:36 2024
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the bathroom but that means all lights beyond that point would now be protected by a 3A fuse and the issue is that there are at least 3 ceiling fans in the rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.
    Or, buy a Greenwood fan, they dont require a 3 amp fuse.

    --
    Remove the '+' and replace with 'plus' to reply by email

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to All on Wed Jan 3 19:38:56 2024
    On Wed, 3 Jan 2024 18:41:36 +0000, Alan Lee <alan@darkroom.plus.com>
    wrote:

    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be protected >> by a 3A fuse and the issue is that there are at least 3 ceiling fans in the >> rooms beyond that point.

    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.
    Or, buy a Greenwood fan, they dont require a 3 amp fuse.

    What happens next time work is done at the same premises? I thought
    there was a 'last man out' rule making each successive electrician
    responsible for the entire system - or is responsibility restricted to
    the work done by each individual electrician? I have never been sure.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Scott on Wed Jan 3 20:11:36 2024
    Scott <newsgroups@gefion.myzen.co.uk> wrote:
    What happens next time work is done at the same premises? I thought
    there was a 'last man out' rule making each successive electrician responsible for the entire system - or is responsibility restricted to
    the work done by each individual electrician? I have never been sure.

    You have to ensure your own work is to regs, but you don't have to update
    the work done by anyone else in the past. eg it's fine to add an extra
    socket on a circuit with rewireable fuses, even though the latter is not up
    to current regs. If you were adding a new way in the consumer unit you couldn't install that with a rewireable fuse, but you could put it behind an RCBO if that would fit in the old CU - if not you'd need to change the
    board.

    Practically speaking you couldn't do it any other way, since J. Random Electrician has no idea what could be lurking in the parts they can't
    access. Otherwise you'd have to tear the house apart every time you changed
    a light fitting.

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Lee@21:1/5 to Theo on Wed Jan 3 20:38:12 2024
    On 03/01/2024 20:11, Theo wrote:
    You have to ensure your own work is to regs, but you don't have to update
    the work done by anyone else in the past. eg it's fine to add an extra socket on a circuit with rewireable fuses, even though the latter is not up to current regs.

    Unfortunately not. All new work must comply with current standards. So
    an extra socket added onto a rewireable fused circuit would have to be a
    RCD socket, or fed from a RCD spur, and, the cable must be surface
    mounted, or run in mechanically proteted cable/containment,as any cable
    less than 50mm from the surface must be RCD protected.
    Also, the earthing and bonding must be acceptable, no bonding, then the
    job cannot be done (legitimately).

    Back to the 3 amp fused fan, it used to be (in BS7671) that you have to
    follow manufacturers instructions, but that was changed, in either Amd 3
    of the 17th, or 18th, I cant remember which. Now, you need to 'take
    account' of the manufacturers instructions. Putting in a 3 amp fuse on a
    RCD and 6A CB protected circuit is not going to protect anything, so it
    can be ignored.

    --
    Remove the '+' and replace with 'plus' to reply by email

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Lee@21:1/5 to Scott on Wed Jan 3 20:44:33 2024
    On 03/01/2024 19:38, Scott wrote:
    On Wed, 3 Jan 2024 18:41:36 +0000, Alan Lee <alan@darkroom.plus.com>
    wrote:

    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.
    Or, buy a Greenwood fan, they dont require a 3 amp fuse.

    What happens next time work is done at the same premises? I thought
    there was a 'last man out' rule making each successive electrician responsible for the entire system - or is responsibility restricted to
    the work done by each individual electrician? I have never been sure.

    Nobody will GAF. There is a good argument that the 3amp fuse is
    spurious, so is ignored, as, really, it does nothing, other than allow a
    way of local isolation (which is not a requirement of the wiring regs.)

    If you go to a house to do work, you are only responsible for the work
    you have done, thats why all of the electrical certificates have an
    'extent of installation covered by this certificate' box, which you fill
    in to show what you have done, e.g. "added fused spur from existing
    circuit 2 to supply single socket in hallway".
    Fill that in, then you cannot be blamed for the socket falling off with
    exposed wires in the bedroom.


    --
    Remove the '+' and replace with 'plus' to reply by email

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeff Layman@21:1/5 to Alan Lee on Wed Jan 3 22:14:46 2024
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be protected >> by a 3A fuse and the issue is that there are at least 3 ceiling fans in the >> rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    --

    Jeff

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to All on Wed Jan 3 22:29:48 2024
    On Wed, 3 Jan 2024 20:44:33 +0000, Alan Lee <alan@darkroom.plus.com>
    wrote:

    On 03/01/2024 19:38, Scott wrote:
    On Wed, 3 Jan 2024 18:41:36 +0000, Alan Lee <alan@darkroom.plus.com>
    wrote:

    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.
    Or, buy a Greenwood fan, they dont require a 3 amp fuse.

    What happens next time work is done at the same premises? I thought
    there was a 'last man out' rule making each successive electrician
    responsible for the entire system - or is responsibility restricted to
    the work done by each individual electrician? I have never been sure.

    Nobody will GAF. There is a good argument that the 3amp fuse is
    spurious, so is ignored, as, really, it does nothing, other than allow a
    way of local isolation (which is not a requirement of the wiring regs.)

    If you go to a house to do work, you are only responsible for the work
    you have done, thats why all of the electrical certificates have an
    'extent of installation covered by this certificate' box, which you fill
    in to show what you have done, e.g. "added fused spur from existing
    circuit 2 to supply single socket in hallway".
    Fill that in, then you cannot be blamed for the socket falling off with >exposed wires in the bedroom.

    Thanks for clarifying that. I genuinely did not know. My guy was
    installing a new consumer unit, so I suppose that creates a wider set
    of responsibilities. He said he had to check the condition of the
    existing wiring.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SteveW@21:1/5 to Jeff Layman on Thu Jan 4 00:00:43 2024
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    A short would trip the 6A breaker anyway. An overload would be
    different, but a ventilation fan, even if stalled, would not overload a
    3A fuse.

    Sensibly, with such fans being connected to the lighting circuit to be
    able to operate with the lights, the requirements should specify that
    the fans should be suitable to be on a 6A circuit without additional protection.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to All on Thu Jan 4 09:15:04 2024
    On Thu, 4 Jan 2024 08:30:56 +0000, Jeff Layman <Jeff@invalid.invalid>
    wrote:

    On 04/01/2024 00:00, SteveW wrote:
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the >>>>> bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans >>>>> in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your
    insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    A short would trip the 6A breaker anyway. An overload would be
    different, but a ventilation fan, even if stalled, would not overload a
    3A fuse.

    I'm not talking about stalling, I'm talking about a short somewhere -
    whether it's in the motor winding or any control circuitry (timer, PIR, >humidity sensor, etc) doesn't matter.

    Sensibly, with such fans being connected to the lighting circuit to be
    able to operate with the lights, the requirements should specify that
    the fans should be suitable to be on a 6A circuit without additional
    protection.

    You're missing the point. Insurance companies will use /any/ excuse, no >matter how unlikely, to avoid paying out. I agree the 6A breaker should
    trip, but if it doesn't and you haven't got the 3A fuse as a backup,
    that's what the insurance company will focus on.

    Do you think a technical non-compliance is enough? Don't you think the
    insurers would need to show (on the balance of probabilities) that the
    method of installation materially contributed to the insured event?

    When I had a ceiling fan and light installed in a new conservatory, the >instructions stated that a 3A fused switched spur was required. The >electrician who installed the fan said I didn't need it. I told him to
    put it in, and it actually proved quite useful when I had to disconnect
    the power to the fan to install a new remote control receiver in it.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeff Layman@21:1/5 to SteveW on Thu Jan 4 08:30:56 2024
    On 04/01/2024 00:00, SteveW wrote:
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your
    insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    A short would trip the 6A breaker anyway. An overload would be
    different, but a ventilation fan, even if stalled, would not overload a
    3A fuse.

    I'm not talking about stalling, I'm talking about a short somewhere -
    whether it's in the motor winding or any control circuitry (timer, PIR, humidity sensor, etc) doesn't matter.

    Sensibly, with such fans being connected to the lighting circuit to be
    able to operate with the lights, the requirements should specify that
    the fans should be suitable to be on a 6A circuit without additional protection.

    You're missing the point. Insurance companies will use /any/ excuse, no
    matter how unlikely, to avoid paying out. I agree the 6A breaker should
    trip, but if it doesn't and you haven't got the 3A fuse as a backup,
    that's what the insurance company will focus on.

    When I had a ceiling fan and light installed in a new conservatory, the instructions stated that a 3A fused switched spur was required. The
    electrician who installed the fan said I didn't need it. I told him to
    put it in, and it actually proved quite useful when I had to disconnect
    the power to the fan to install a new remote control receiver in it.

    --

    Jeff

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Green@21:1/5 to Jeff Layman on Thu Jan 4 09:28:07 2024
    Jeff Layman <Jeff@invalid.invalid> wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    On what grounds wouldn't they pay out? They'd surely have to prove
    you *intended* the house to burn down as a result of not fitting the
    fuse. Otherwise all accidental damage policies would be pointless.

    --
    Chris Green
    ·

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Green@21:1/5 to Scott on Thu Jan 4 09:33:08 2024
    Scott <newsgroups@gefion.myzen.co.uk> wrote:

    You're missing the point. Insurance companies will use /any/ excuse, no >matter how unlikely, to avoid paying out. I agree the 6A breaker should >trip, but if it doesn't and you haven't got the 3A fuse as a backup,
    that's what the insurance company will focus on.

    Do you think a technical non-compliance is enough? Don't you think the insurers would need to show (on the balance of probabilities) that the
    method of installation materially contributed to the insured event?

    Even if they did prove this I don't see how it invalidates the
    insurance. One's insurance is against one's house burning down, not
    against a 'random event' causing one's house to burn down. If I drop
    a cigarette on the floor (not that I have ever smoked) and as a result
    the house burns down then (following the same sort of logic as about
    the fuse) then it's "my fault" for dropping the cigarette and for
    having an inflammable carpet and for not having sprinklers installed,
    etc. etc.

    --
    Chris Green
    ·

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to Chris Green on Thu Jan 4 10:04:50 2024
    On Thu, 4 Jan 2024 09:28:07 +0000, Chris Green <cl@isbd.net> wrote:

    Jeff Layman <Jeff@invalid.invalid> wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your
    insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    On what grounds wouldn't they pay out? They'd surely have to prove
    you *intended* the house to burn down as a result of not fitting the
    fuse. Otherwise all accidental damage policies would be pointless.

    I think gross negligence would suffice. If you leave the keys in your
    car, you could hardly argue that you did not intend someone to steal
    it.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Jeff Layman on Thu Jan 4 10:30:21 2024
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    The question is the marginal case that would blow a 3A fuse and not trip
    a 6A MCB and how realistic it is.

    Even a failing lightbulb used to trip my 6A MCBs in a way that never
    happened with old style fuse wire.

    In reality you wont get a fire from a short on a 6A spur. It will trip
    the whole shebang. The 3A fuse is likely to be there to protect wiring
    on a 32A ring main. You would automagically put in a 3A switched spur in
    that case.


    --
    “Some people like to travel by train because it combines the slowness of
    a car with the cramped public exposure of 
an airplane.”

    Dennis Miller

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to SteveW on Thu Jan 4 10:30:42 2024
    On 04/01/2024 00:00, SteveW wrote:
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your
    insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    A short would trip the 6A breaker anyway. An overload would be
    different, but a ventilation fan, even if stalled, would not overload a
    3A fuse.

    Sensibly, with such fans being connected to the lighting circuit to be
    able to operate with the lights, the requirements should specify that
    the fans should be suitable to be on a 6A circuit without additional protection.

    +1

    --
    A lie can travel halfway around the world while the truth is putting on
    its shoes.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Jeff Layman on Thu Jan 4 10:31:37 2024
    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse, no matter how unlikely, to avoid paying out. I agree the 6A breaker should
    trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the
    manufacturer.

    --
    A lie can travel halfway around the world while the truth is putting on
    its shoes.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to tnp@invalid.invalid on Thu Jan 4 10:42:55 2024
    On Thu, 4 Jan 2024 10:31:37 +0000, The Natural Philosopher <tnp@invalid.invalid> wrote:

    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse, no
    matter how unlikely, to avoid paying out. I agree the 6A breaker should
    trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the >manufacturer.

    Subrogated rights. They would have to prove the case though, which
    could be difficult if the evidence has been destroyed in a fire.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to Fredxx on Thu Jan 4 11:53:25 2024
    On Thu, 4 Jan 2024 11:19:47 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 10:31, The Natural Philosopher wrote:
    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse,
    no matter how unlikely, to avoid paying out. I agree the 6A breaker
    should trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the
    manufacturer.

    Replace 'would' with 'could'. I have never known an insurance company
    sue a manufacturer. Also any contract is with the final supplier of the >goods.

    Does Donoghue v Stevenson not apply in English law?

    Either way, feel free to provide an example of where an "insurance
    company would sue the manufacturer". I know you won't be able to as per >typical of your silly claims.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to The Natural Philosopher on Thu Jan 4 11:19:47 2024
    On 04/01/2024 10:31, The Natural Philosopher wrote:
    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse,
    no matter how unlikely, to avoid paying out. I agree the 6A breaker
    should trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the manufacturer.


    Replace 'would' with 'could'. I have never known an insurance company
    sue a manufacturer. Also any contract is with the final supplier of the
    goods.

    Either way, feel free to provide an example of where an "insurance
    company would sue the manufacturer". I know you won't be able to as per
    typical of your silly claims.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeff Layman@21:1/5 to Chris Green on Thu Jan 4 13:44:19 2024
    On 04/01/2024 09:33, Chris Green wrote:
    Scott <newsgroups@gefion.myzen.co.uk> wrote:

    You're missing the point. Insurance companies will use /any/ excuse, no
    matter how unlikely, to avoid paying out. I agree the 6A breaker should
    trip, but if it doesn't and you haven't got the 3A fuse as a backup,
    that's what the insurance company will focus on.

    Do you think a technical non-compliance is enough? Don't you think the
    insurers would need to show (on the balance of probabilities) that the
    method of installation materially contributed to the insured event?

    Even if they did prove this I don't see how it invalidates the
    insurance. One's insurance is against one's house burning down, not
    against a 'random event' causing one's house to burn down. If I drop
    a cigarette on the floor (not that I have ever smoked) and as a result
    the house burns down then (following the same sort of logic as about
    the fuse) then it's "my fault" for dropping the cigarette and for
    having an inflammable carpet and for not having sprinklers installed,
    etc. etc.

    No, the issue is that you have deliberately ignored an instruction
    regarding installation of the fan. You, and others, might not consider
    it necessary, but the fan supplier does. All the insurance company have
    to do is show that something regarding the policy has not been complied
    with. If you don't believe this, have a look at this decision. This did
    involve a fire, but the reason for the reduced payout by the insurance
    company (Accelerant) was upheld by the ombudsman: <https://www.financial-ombudsman.org.uk/decision/DRN-4044799.pdf>

    It was a commercial policy, which may be different from a household one.
    Note this part of the decision:
    "Accelerant accepts that the qualifying breach wasn’t deliberate or
    reckless. In these circumstances, the Act says that the insurer may
    reduce proportionately the amount to be paid on a claim."

    How much reduced would a payout be where the breach was deliberate or
    reckless, in other words ignoring an instruction by the fan supplier to
    include a fuse?

    --

    Jeff

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to Scott on Thu Jan 4 13:55:25 2024
    On 04/01/2024 11:53, Scott wrote:
    On Thu, 4 Jan 2024 11:19:47 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 10:31, The Natural Philosopher wrote:
    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse,
    no matter how unlikely, to avoid paying out. I agree the 6A breaker
    should trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the
    manufacturer.

    Replace 'would' with 'could'. I have never known an insurance company
    sue a manufacturer. Also any contract is with the final supplier of the
    goods.

    Does Donoghue v Stevenson not apply in English law?

    Certainly a landmark case.

    However, a one-off manufacturing fault with a QA inspection procedure
    will not satisfy a claim using a lack of "duty of care" argument.

    Either way, feel free to provide an example of where an "insurance
    company would sue the manufacturer". I know you won't be able to as per
    typical of your silly claims.

    So, provide an example for an MCB or similar device.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to Fredxx on Thu Jan 4 14:18:07 2024
    On Thu, 4 Jan 2024 13:55:25 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 11:53, Scott wrote:
    On Thu, 4 Jan 2024 11:19:47 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 10:31, The Natural Philosopher wrote:
    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse, >>>>> no matter how unlikely, to avoid paying out. I agree the 6A breaker
    should trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the
    manufacturer.

    Replace 'would' with 'could'. I have never known an insurance company
    sue a manufacturer. Also any contract is with the final supplier of the
    goods.

    Does Donoghue v Stevenson not apply in English law?

    Certainly a landmark case.

    However, a one-off manufacturing fault with a QA inspection procedure
    will not satisfy a claim using a lack of "duty of care" argument.

    Would this not be one of the facta probanda?

    Either way, feel free to provide an example of where an "insurance
    company would sue the manufacturer". I know you won't be able to as per
    typical of your silly claims.

    So, provide an example for an MCB or similar device.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From nothanks@aolbin.com@21:1/5 to nothanks@aolbin.com on Thu Jan 4 14:21:27 2024
    On 03/01/2024 16:48, nothanks@aolbin.com wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in
    conjunction with the bathroom light so that the fan comes on when the
    light
    is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and >> switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as
    planned and using two FCU’s
    One for live and the other for switched live before running the rest
    of the
    cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My
    daughters
    new build has one bathroom, 2 en-suites and a cloakroom/WC all windowless
    and all with ventilators activated by the light switch and I know all the
    lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for the
    MF100T
    has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    Not an answer, but a suggestion: consider having two pull switches, one
    for the fan and one for the light, rather than having the fan always
    come on with the light. This means you don't have the fan noise at night
    time and you can leave the fan on for a while in the morning after a
    vindaloo supper the night before.

    A further thought: you could put a 3A fuse inside the fan enclosure if
    you wanted a fuse but not an FCU.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to nothanks@aolbin.com on Thu Jan 4 14:32:19 2024
    On 03/01/2024 16:48, nothanks@aolbin.com wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in
    conjunction with the bathroom light so that the fan comes on when the
    light
    is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and >> switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as
    planned and using two FCU’s
    One for live and the other for switched live before running the rest
    of the
    cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My
    daughters
    new build has one bathroom, 2 en-suites and a cloakroom/WC all windowless
    and all with ventilators activated by the light switch and I know all the
    lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for the
    MF100T
    has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    Not an answer, but a suggestion: consider having two pull switches, one
    for the fan and one for the light, rather than having the fan always
    come on with the light. This means you don't have the fan noise at night
    time and you can leave the fan on for a while in the morning after a
    vindaloo supper the night before.

    I've used an isolating fan pull-switch for this purpose. It also
    switches all 3 conductors to the fan.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to Scott on Thu Jan 4 14:40:29 2024
    On 04/01/2024 14:18, Scott wrote:
    On Thu, 4 Jan 2024 13:55:25 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 11:53, Scott wrote:
    On Thu, 4 Jan 2024 11:19:47 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 10:31, The Natural Philosopher wrote:
    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse, >>>>>> no matter how unlikely, to avoid paying out. I agree the 6A breaker >>>>>> should trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the
    manufacturer.

    Replace 'would' with 'could'. I have never known an insurance company
    sue a manufacturer. Also any contract is with the final supplier of the >>>> goods.

    Does Donoghue v Stevenson not apply in English law?

    Certainly a landmark case.

    However, a one-off manufacturing fault with a QA inspection procedure
    will not satisfy a claim using a lack of "duty of care" argument.

    Would this not be one of the facta probanda?

    In so far evidence of QA procedure would dismiss such a case.

    Either way, feel free to provide an example of where an "insurance
    company would sue the manufacturer". I know you won't be able to as per >>>> typical of your silly claims.

    So, provide an example for an MCB or similar device.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Jeff Layman on Thu Jan 4 14:45:59 2024
    On 04/01/2024 13:44, Jeff Layman wrote:
    On 04/01/2024 09:33, Chris Green wrote:
    Scott <newsgroups@gefion.myzen.co.uk> wrote:

    You're missing the point. Insurance companies will use /any/ excuse, no >>>> matter how unlikely, to avoid paying out. I agree the 6A breaker should >>>> trip, but if it doesn't and you haven't got the 3A fuse as a backup,
    that's what the insurance company will focus on.

    Do you think a technical non-compliance is enough? Don't you think the
    insurers would need to show (on the balance of probabilities) that the
    method of installation materially contributed to the insured event?

    Even if they did prove this I don't see how it invalidates the
    insurance.  One's insurance is against one's house burning down, not
    against a 'random event' causing one's house to burn down.  If I drop
    a cigarette on the floor (not that I have ever smoked) and as a result
    the house burns down then (following the same sort of logic as about
    the fuse) then it's "my fault" for dropping the cigarette and for
    having an inflammable carpet and for not having sprinklers installed,
    etc. etc.

    No, the issue is that you have deliberately ignored an instruction
    regarding installation of the fan. You, and others, might not consider
    it necessary, but the fan supplier does. All the insurance company have
    to do is show that something regarding the policy has not been complied
    with. If you don't believe this, have a look at this decision. This did involve a fire, but the reason for the reduced payout by the insurance company (Accelerant) was upheld by the ombudsman: <https://www.financial-ombudsman.org.uk/decision/DRN-4044799.pdf>

    It was a commercial policy, which may be different from a household one.
    Note this part of the decision:
    "Accelerant accepts that the qualifying breach wasn’t deliberate or reckless. In these circumstances, the Act says that the insurer may
    reduce proportionately the amount to be paid on a claim."

    How much reduced would a payout be where the breach was deliberate or reckless, in other words ignoring an instruction by the fan supplier to include a fuse?

    Do you work in the public sector?
    Rules for fools is definitely your area of expertise.]

    --
    You can get much farther with a kind word and a gun than you can with a
    kind word alone.

    Al Capone

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to Fredxx on Thu Jan 4 14:50:41 2024
    On Thu, 4 Jan 2024 14:40:29 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 14:18, Scott wrote:
    On Thu, 4 Jan 2024 13:55:25 +0000, Fredxx <fredxx@spam.invalid> wrote:

    On 04/01/2024 11:53, Scott wrote:
    On Thu, 4 Jan 2024 11:19:47 +0000, Fredxx <fredxx@spam.invalid> wrote: >>>>
    On 04/01/2024 10:31, The Natural Philosopher wrote:
    On 04/01/2024 08:30, Jeff Layman wrote:
    You're missing the point. Insurance companies will use /any/ excuse, >>>>>>> no matter how unlikely, to avoid paying out. I agree the 6A breaker >>>>>>> should trip, bu
    Bullshit.

    If a 6A trip failed to trip, the insurance company would sue the
    manufacturer.

    Replace 'would' with 'could'. I have never known an insurance company >>>>> sue a manufacturer. Also any contract is with the final supplier of the >>>>> goods.

    Does Donoghue v Stevenson not apply in English law?

    Certainly a landmark case.

    However, a one-off manufacturing fault with a QA inspection procedure
    will not satisfy a claim using a lack of "duty of care" argument.

    Would this not be one of the facta probanda?

    In so far evidence of QA procedure would dismiss such a case.

    Agreed, if such evidence is accepted of course.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Lee@21:1/5 to Jeff Layman on Thu Jan 4 15:07:17 2024
    On 04/01/2024 13:44, Jeff Layman wrote:

    No, the issue is that you have deliberately ignored an instruction
    regarding installation of the fan.


    What about when Manufacturers Instructions say 'must be installed by a
    NICEIC registered electrician'
    I've seen that a number of times.
    Thats why the electrical regs had a wording change a few years back, so
    such stupid Manufacturers Instructions can be ignored.


    --
    Remove the '+' and replace with 'plus' to reply by email

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to All on Thu Jan 4 15:15:10 2024
    On Thu, 4 Jan 2024 15:07:17 +0000, Alan Lee <alan@darkroom.plus.com>
    wrote:

    On 04/01/2024 13:44, Jeff Layman wrote:

    No, the issue is that you have deliberately ignored an instruction
    regarding installation of the fan.

    What about when Manufacturers Instructions say 'must be installed by a
    NICEIC registered electrician'
    I've seen that a number of times.
    Thats why the electrical regs had a wording change a few years back, so
    such stupid Manufacturers Instructions can be ignored.

    As an aside, an instruction now seems to be appearing to the effect
    that children from 8 years and above can use, clean and perform user maintenance on this appliance in accordance with the User Instructions
    provided they are supervised by a person responsible for their safety
    and have been given instruction concerning the use of the appliance
    and are aware of the hazards.

    I wonder where the age of eight came from. I don't think this is a
    recognised stage of legal capacity.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Green@21:1/5 to Jeff Layman on Thu Jan 4 15:27:55 2024
    Jeff Layman <Jeff@invalid.invalid> wrote:
    On 04/01/2024 09:33, Chris Green wrote:
    Scott <newsgroups@gefion.myzen.co.uk> wrote:

    You're missing the point. Insurance companies will use /any/ excuse, no >>> matter how unlikely, to avoid paying out. I agree the 6A breaker should >>> trip, but if it doesn't and you haven't got the 3A fuse as a backup,
    that's what the insurance company will focus on.

    Do you think a technical non-compliance is enough? Don't you think the
    insurers would need to show (on the balance of probabilities) that the
    method of installation materially contributed to the insured event?

    Even if they did prove this I don't see how it invalidates the
    insurance. One's insurance is against one's house burning down, not against a 'random event' causing one's house to burn down. If I drop
    a cigarette on the floor (not that I have ever smoked) and as a result
    the house burns down then (following the same sort of logic as about
    the fuse) then it's "my fault" for dropping the cigarette and for
    having an inflammable carpet and for not having sprinklers installed,
    etc. etc.

    No, the issue is that you have deliberately ignored an instruction
    regarding installation of the fan.

    I might similarly have ignored an instruction about smoking in bed.

    --
    Chris Green
    ·

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeff Layman@21:1/5 to Alan Lee on Thu Jan 4 15:29:57 2024
    On 04/01/2024 15:07, Alan Lee wrote:
    On 04/01/2024 13:44, Jeff Layman wrote:

    No, the issue is that you have deliberately ignored an instruction
    regarding installation of the fan.


    What about when Manufacturers Instructions say 'must be installed by a
    NICEIC registered electrician'
    I've seen that a number of times.
    Thats why the electrical regs had a wording change a few years back, so
    such stupid Manufacturers Instructions can be ignored.

    Quite so. But it takes time and many examples before it is shown to be unnecessary. The question remains that if the insurance company refuses
    to pay out, and you complain to the ombudsman before the regs have
    changed, will he find in your favour or not?

    --

    Jeff

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Green@21:1/5 to Scott on Thu Jan 4 15:31:38 2024
    Scott <newsgroups@gefion.myzen.co.uk> wrote:
    On Thu, 4 Jan 2024 09:28:07 +0000, Chris Green <cl@isbd.net> wrote:

    Jeff Layman <Jeff@invalid.invalid> wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the >> >> bathroom but that means all lights beyond that point would now be protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your
    insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    On what grounds wouldn't they pay out? They'd surely have to prove
    you *intended* the house to burn down as a result of not fitting the
    fuse. Otherwise all accidental damage policies would be pointless.

    I think gross negligence would suffice. If you leave the keys in your
    car, you could hardly argue that you did not intend someone to steal
    it.

    I know of such a case (many years ago), keys left in car, insurance
    company tried to wriggle out of paying up but in they end they paid.
    I think it was down to the intentions behind leaving the keys in the
    car, the claimant said he left them there by mistake and that was
    enough to make the claim good.

    --
    Chris Green
    ·

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to Chris Green on Thu Jan 4 17:11:54 2024
    On 04/01/2024 15:31, Chris Green wrote:
    Scott <newsgroups@gefion.myzen.co.uk> wrote:
    On Thu, 4 Jan 2024 09:28:07 +0000, Chris Green <cl@isbd.net> wrote:

    Jeff Layman <Jeff@invalid.invalid> wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the >>>>>> bathroom but that means all lights beyond that point would now be protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur. >>>>> There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your >>>> insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    On what grounds wouldn't they pay out? They'd surely have to prove
    you *intended* the house to burn down as a result of not fitting the
    fuse. Otherwise all accidental damage policies would be pointless.

    I think gross negligence would suffice. If you leave the keys in your
    car, you could hardly argue that you did not intend someone to steal
    it.

    I know of such a case (many years ago), keys left in car, insurance
    company tried to wriggle out of paying up but in they end they paid.
    I think it was down to the intentions behind leaving the keys in the
    car, the claimant said he left them there by mistake and that was
    enough to make the claim good.

    https://www.casemine.com/judgement/uk/5a8ff71860d03e7f57ea77a1

    Makes interesting reading.

    Most policies now have a wording to remove this sort of claim.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SH@21:1/5 to SteveW on Fri Jan 5 10:28:41 2024
    On 04/01/2024 00:00, SteveW wrote:
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince your
    insurance company that the absent fuse would have made no difference
    when they refuse to pay out. Good luck with that.

    A short would trip the 6A breaker anyway. An overload would be
    different, but a ventilation fan, even if stalled, would not overload a
    3A fuse.

    Sensibly, with such fans being connected to the lighting circuit to be
    able to operate with the lights, the requirements should specify that
    the fans should be suitable to be on a 6A circuit without additional protection.



    random question....

    If the entire lighing circuit is on LED bulbs only and there are no
    halogen or tungsten filaments or fluorescents, the load would be much
    lower so could one downrate the existing 6A MCB/RCBO down to 3A or do 3A RCBOs/MCBs not exist?

    S.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SteveW@21:1/5 to All on Fri Jan 5 10:34:07 2024
    On 05/01/2024 10:28, SH wrote:
    On 04/01/2024 00:00, SteveW wrote:
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the >>>>> bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling
    fans in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince
    your insurance company that the absent fuse would have made no
    difference when they refuse to pay out. Good luck with that.

    A short would trip the 6A breaker anyway. An overload would be
    different, but a ventilation fan, even if stalled, would not overload
    a 3A fuse.

    Sensibly, with such fans being connected to the lighting circuit to be
    able to operate with the lights, the requirements should specify that
    the fans should be suitable to be on a 6A circuit without additional
    protection.



    random question....

    If the entire lighing circuit is on LED bulbs only and there are no
    halogen or tungsten filaments or fluorescents, the load would be much
    lower so could one downrate the existing 6A MCB/RCBO down to 3A or do 3A RCBOs/MCBs not exist?

    6A seems to be the lowest rated RCBO for my consumer unit.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Andy Burns@21:1/5 to SteveW on Fri Jan 5 10:51:42 2024
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I can
    see is 2A

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SH@21:1/5 to Andy Burns on Fri Jan 5 11:32:13 2024
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I can
    see is 2A


    I have a 5 bedroom house and I have literally just counted the number of
    bulbs on all of my lighting circuits (I have 4 lighting circuits.)

    The one with the most lamps is the ground floor with 55 lamps, all are
    LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives 330
    Watts. There is an extractor fan on the d/stairs toilet fed by this circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4 watts
    to 20 watts. Lets take the 20 watts figure as worst case and multiply by
    18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of 660
    Watts at a supply voltage of 220 watts which is almost double the the
    wattage assuming *all* lamps were all on at the same time. In practie
    very few of us actually have *all* the lamps on at the same time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit is
    that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SH@21:1/5 to All on Fri Jan 5 11:41:41 2024
    On 05/01/2024 11:32, SH wrote:
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I
    can see is 2A


    I have a 5 bedroom house and I have literally just counted the number of bulbs on all of my lighting circuits (I have 4 lighting circuits.)

    The one with the most lamps is the ground floor with 55 lamps, all are
    LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives 330 Watts. There is an extractor fan on the d/stairs toilet fed by this
    circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4 watts
    to 20 watts. Lets take the 20 watts figure as worst case and multiply by
    18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of 660
    Watts at a supply voltage of 220 watts which is almost double the the
    wattage assuming *all* lamps were all on at the same time. In practie
    very few of us actually have *all* the lamps on at the same time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit is
    that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.




    Coming back to the original OP's query,

    It strikces me that there is a possible solution but with a Caveat (*)

    Put in a dry lining box next to the light fitting.

    Transfer the Power Loop in and Power loop Out cables from the existing
    light fitting to the new drylining box.

    Then wire in some twin and earth cable from the new drylining box and
    then fit a FCU to this drylining box so that the bathroom light is now
    on its own 3A supply.

    It is assumed that the wall switch also runs to the existing rose and
    that the 3 core & E is also taken from the existing rose to the isolator
    switch and thence onwards to the fan.

    (*) you will need to pay attention to the special zones of bathrooms
    such that (a) the FCU is at a sifficient distance and hieght away from
    the bath or shower and (b) with it being a humid atmosphere, humidity
    may get inside teh FCU so it might be prudent to use a IP66 rated FCU
    enclosure OR extend the power loop in, power loop out and the bridging
    cable so that teh FCU can be mounted somewhere outside the bathroom.

    As a side point, putting a 3A fuse into the Live in for the fan does not
    offer any protection to the switched live wire. Although you could put a
    2nd fuse into teh Switched live, you then could have an unsafe situation
    where if a fuse opens, unless one is diligent about opening the fan
    isolator switch, one could be working on a fan thinking its completely
    dead when in fact either teh permanent Live or switched Live is still Live!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Andy Burns@21:1/5 to All on Fri Jan 5 11:57:26 2024
    SH wrote:

    Swapping to a 3A MCB or RCBO would support a continuous current of 660
    Watts at a supply voltage of 220 watts which is almost double the the
    wattage assuming all lamps were all on at the same time.

    But if you suffered a power cut while they were all on, what sort of
    spike would all the PSUs in those LEDs generate?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to All on Fri Jan 5 12:18:39 2024
    On 05/01/2024 11:41, SH wrote:
    On 05/01/2024 11:32, SH wrote:
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I
    can see is 2A


    I have a 5 bedroom house and I have literally just counted the number
    of bulbs on all of my lighting circuits (I have 4 lighting circuits.)

    The one with the most lamps is the ground floor with 55 lamps, all are
    LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives
    330 Watts. There is an extractor fan on the d/stairs toilet fed by
    this circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4 watts
    to 20 watts. Lets take the 20 watts figure as worst case and multiply
    by 18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a
    supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of 660
    Watts at a supply voltage of 220 watts which is almost double the the
    wattage assuming *all* lamps were all on at the same time. In practie
    very few of us actually have *all* the lamps on at the same time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit is
    that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.




    Coming back to the original OP's query,

    It strikces me that there is a possible solution but with a Caveat (*)

    Put in a dry lining box next to the light fitting.

    Transfer the Power Loop in and Power loop Out cables from the existing
    light fitting to the new drylining box.

    Then wire in some twin and earth cable from the new drylining box and
    then fit a FCU to this drylining box so that the bathroom light is now
    on its own 3A supply.

    It is assumed that the wall switch also runs to the existing rose and
    that the 3 core & E is also taken from the existing rose to the isolator switch and thence onwards to the fan.

    (*) you will need to pay attention to the special zones of bathrooms
    such that (a) the FCU is at a sifficient distance and hieght away from
    the bath or shower and (b) with it being a humid atmosphere, humidity
    may get inside teh FCU so it might be prudent to use a IP66 rated FCU enclosure OR extend the power loop in, power loop out and the bridging
    cable so that teh FCU can be mounted somewhere outside the bathroom.

    As a side point, putting a 3A fuse into the Live in for the fan does not offer any protection to the switched live wire.

    The switched live might be a sensor input rather than supplying power. I
    note the wiring diagram:
    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    allows for a fuse in just the live feed.

    Nevertheless I still feel that is an issue and would prefer the light
    and fan on it's own fuse.

    Although you could put a
    2nd fuse into teh Switched live, you then could have an unsafe situation where if a fuse opens, unless one is diligent about opening the fan
    isolator switch, one could be working on a fan thinking its completely
    dead when in fact either teh permanent Live or switched Live is still Live!

    As long as the wires are correctly sleeved, anyone gaining access to the terminals ought to be checking to see if a wire is live and remove power wherever possible.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to All on Fri Jan 5 12:19:55 2024
    On 05/01/2024 10:28, SH wrote:
    On 04/01/2024 00:00, SteveW wrote:
    On 03/01/2024 22:14, Jeff Layman wrote:
    On 03/01/2024 18:41, Alan Lee wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:
    One option is to fit a fused spur unit into the incoming feed for the >>>>> bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling
    fans in the
    rooms beyond that point.


    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.

    When your house burns down because of a short in the fan leading to a
    fire, which would have blown a 3A fuse, you will have to convince
    your insurance company that the absent fuse would have made no
    difference when they refuse to pay out. Good luck with that.

    A short would trip the 6A breaker anyway. An overload would be
    different, but a ventilation fan, even if stalled, would not overload
    a 3A fuse.

    Sensibly, with such fans being connected to the lighting circuit to be
    able to operate with the lights, the requirements should specify that
    the fans should be suitable to be on a 6A circuit without additional
    protection.



    random question....

    If the entire lighing circuit is on LED bulbs only and there are no
    halogen or tungsten filaments or fluorescents, the load would be much
    lower so could one downrate the existing 6A MCB/RCBO down to 3A or do 3A RCBOs/MCBs not exist?

    That was my thought too. Some 3A MCBs do exist but relatively rare.

    I would have thought the fan would have it's own internal fuse, even a non-replaceable one.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SH@21:1/5 to Andy Burns on Fri Jan 5 12:21:13 2024
    On 05/01/2024 11:57, Andy Burns wrote:
    SH wrote:

    Swapping to a 3A MCB or RCBO would support a continuous current of 660
    Watts at a supply voltage of 220 watts which is almost double the the
    wattage assuming all lamps were all on at the same time.

    But if you suffered a power cut while they were all on, what sort of
    spike would all the PSUs in those LEDs generate?


    That all depends on the PSU design.... I have a chart somewhere that
    details something like 15 different PSU designs

    Some PSU designs here:

    https://www.researchgate.net/figure/Different-basic-converters-layout-a-Boost-b-Buckboost-c-Zeta-d-Cuk-Converter-and_fig5_365037354

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Tricky Dicky on Fri Jan 5 12:46:42 2024
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will
    have a 3 pole isolator outside the bathroom and the plan is to run it in conjunction with the bathroom light so that the fan comes on when the light is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the bathroom but that means all lights beyond that point would now be protected by a 3A fuse and the issue is that there are at least 3 ceiling fans in the rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as planned and using two FCU’s
    One for live and the other for switched live before running the rest of the cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My daughters new build has one bathroom, 2 en-suites and a cloakroom/WC all windowless
    and all with ventilators activated by the light switch and I know all the lighting circuits are 6A.

    So what to do?

    Here are a number of options:

    https://wiki.diyfaq.org.uk/index.php/Extractor_fan_wiring#Fused_Fan_supplies





    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Theo on Fri Jan 5 12:56:20 2024
    On 03/01/2024 20:11, Theo wrote:
    Scott <newsgroups@gefion.myzen.co.uk> wrote:
    What happens next time work is done at the same premises? I thought
    there was a 'last man out' rule making each successive electrician
    responsible for the entire system - or is responsibility restricted to
    the work done by each individual electrician? I have never been sure.

    You have to ensure your own work is to regs, but you don't have to update
    the work done by anyone else in the past.

    So far, that is true.

    eg it's fine to add an extra
    socket on a circuit with rewireable fuses, even though the latter is not up to current regs.

    but that is where it argument collapses. If you add a socket without RCD protection, then you are not working to the current rules.

    If you were adding a new way in the consumer unit you
    couldn't install that with a rewireable fuse,

    Actually you could if you really wanted to - there is no ban on having a circuit with a rewireable fuse.

    However if it were a socket circuit then it would need RCD protection,
    as would any circuit with an unprotected cable run. So there are very
    limited cases were you could install a new circuit with a re-wireable
    fuse and no RCD.

    (use of a rewireable also imposes a de-rating factor on the circuit
    cables since that type of fuse is slower in operation in some cases)

    but you could put it behind an
    RCBO if that would fit in the old CU - if not you'd need to change the
    board.

    A RCBO includes over current protection as well as a RCD. So there would
    be no need for a fuse as well.

    Practically speaking you couldn't do it any other way, since J. Random Electrician has no idea what could be lurking in the parts they can't
    access. Otherwise you'd have to tear the house apart every time you changed a light fitting.




    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Alan Lee on Fri Jan 5 13:00:24 2024
    On 03/01/2024 20:44, Alan Lee wrote:
    On 03/01/2024 19:38, Scott wrote:
    On Wed, 3 Jan 2024 18:41:36 +0000, Alan Lee <alan@darkroom.plus.com>
    wrote:

    Just do what 95% of sparkies do, and dont bother with the fused spur.
    There really is no need for it.
    Or, buy a Greenwood fan, they dont require a 3 amp fuse.

    What happens next time work is done at the same premises?  I thought
    there was a 'last man out' rule making each successive electrician
    responsible for the entire system - or is responsibility restricted to
    the work done by each individual electrician?  I have never been sure.

    Nobody will GAF. There is a good argument that the 3amp fuse is
    spurious, so is ignored, as, really, it does nothing, other than allow a
    way of local isolation (which is not a requirement of the wiring regs.)

    If you go to a house to do work, you are only responsible for the work
    you have done, thats why all of the electrical certificates have an
    'extent of installation covered by this certificate' box, which you fill
    in to show what you have done, e.g. "added fused spur from existing
    circuit 2 to supply single socket in hallway".
    Fill that in, then you cannot be blamed for the socket falling off with exposed wires in the bedroom.

    There is a little more nuance there though. There are some cases where
    you can't ignore what is there. Say you notice that the main
    equipotential bonding is missing. You can't sign off your work with it
    left in that state. So you would have to insist that the bonding fault
    is fixed, or decline the new work.

    Likewise, if asked to add a new light to a circuit that is wired with
    twin cable and no earth. Then you would not be able to extend that, and
    work to the required standards.

    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to nothanks@aolbin.com on Fri Jan 5 13:15:36 2024
    On 04/01/2024 14:21, nothanks@aolbin.com wrote:
    On 03/01/2024 16:48, nothanks@aolbin.com wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This will >>> have a 3 pole isolator outside the bathroom and the plan is to run it in >>> conjunction with the bathroom light so that the fan comes on when the
    light
    is operated typical of many windowless bathrooms and en-suites in many
    modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live and >>> switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as
    planned and using two FCU’s
    One for live and the other for switched live before running the rest
    of the
    cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My
    daughters
    new build has one bathroom, 2 en-suites and a cloakroom/WC all
    windowless
    and all with ventilators activated by the light switch and I know all
    the
    lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for the
    MF100T
    has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    Not an answer, but a suggestion: consider having two pull switches,
    one for the fan and one for the light, rather than having the fan
    always come on with the light. This means you don't have the fan noise
    at night time and you can leave the fan on for a while in the morning
    after a vindaloo supper the night before.

    A further thought: you could put a 3A fuse inside the fan enclosure if
    you wanted a fuse but not an FCU.

    That can work, but will be limited to fans with only one live connection.

    If it has run on, then you would need a fuse protecting its permanent
    live and another one on the switched live. Now you have two fuses in
    parallel protecting the same device which is not good in a number of ways.



    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to John Rumm on Fri Jan 5 13:21:01 2024
    On 05/01/2024 13:15, John Rumm wrote:
    On 04/01/2024 14:21, nothanks@aolbin.com wrote:
    On 03/01/2024 16:48, nothanks@aolbin.com wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This
    will
    have a 3 pole isolator outside the bathroom and the plan is to run
    it in
    conjunction with the bathroom light so that the fan comes on when
    the light
    is operated typical of many windowless bathrooms and en-suites in many >>>> modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live >>>> and
    switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as >>>> planned and using two FCU’s
    One for live and the other for switched live before running the rest
    of the
    cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My
    daughters
    new build has one bathroom, 2 en-suites and a cloakroom/WC all
    windowless
    and all with ventilators activated by the light switch and I know
    all the
    lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for the
    MF100T
    has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    Not an answer, but a suggestion: consider having two pull switches,
    one for the fan and one for the light, rather than having the fan
    always come on with the light. This means you don't have the fan
    noise at night time and you can leave the fan on for a while in the
    morning after a vindaloo supper the night before.

    A further thought: you could put a 3A fuse inside the fan enclosure if
    you wanted a fuse but not an FCU.

    That can work, but will be limited to fans with only one live connection.

    If it has run on, then you would need a fuse protecting its permanent
    live and another one on the switched live. Now you have two fuses in
    parallel protecting the same device which is not good in a number of ways.

    The Manrose install sheet only requires a fuse on the permanent live.
    Why the need for two fuses? The switched live can be treated a signal
    wire and I presume doesn't supply any current to the fan.

    If that is the case there is perhaps no need for the triple isolation
    switch?

    If the fuse is fan side of the 3-pole isolation switch then it can be
    changed, or altered, whilst being fully isolated without switching the
    lighting MCB.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to Fredxx on Fri Jan 5 15:22:37 2024
    Fredxx <fredxx@spam.invalid> wrote:
    On 05/01/2024 11:41, SH wrote:
    On 05/01/2024 11:32, SH wrote:
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I
    can see is 2A


    I have a 5 bedroom house and I have literally just counted the number
    of bulbs on all of my lighting circuits (I have 4 lighting circuits.)

    The one with the most lamps is the ground floor with 55 lamps, all are
    LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives
    330 Watts. There is an extractor fan on the d/stairs toilet fed by
    this circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4 watts
    to 20 watts. Lets take the 20 watts figure as worst case and multiply
    by 18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a
    supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of 660
    Watts at a supply voltage of 220 watts which is almost double the the
    wattage assuming *all* lamps were all on at the same time. In practie
    very few of us actually have *all* the lamps on at the same time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit is
    that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.




    Coming back to the original OP's query,

    It strikces me that there is a possible solution but with a Caveat (*)

    Put in a dry lining box next to the light fitting.

    Transfer the Power Loop in and Power loop Out cables from the existing
    light fitting to the new drylining box.

    Then wire in some twin and earth cable from the new drylining box and
    then fit a FCU to this drylining box so that the bathroom light is now
    on its own 3A supply.

    It is assumed that the wall switch also runs to the existing rose and
    that the 3 core & E is also taken from the existing rose to the isolator
    switch and thence onwards to the fan.

    (*) you will need to pay attention to the special zones of bathrooms
    such that (a) the FCU is at a sifficient distance and hieght away from
    the bath or shower and (b) with it being a humid atmosphere, humidity
    may get inside teh FCU so it might be prudent to use a IP66 rated FCU
    enclosure OR extend the power loop in, power loop out and the bridging
    cable so that teh FCU can be mounted somewhere outside the bathroom.

    As a side point, putting a 3A fuse into the Live in for the fan does not
    offer any protection to the switched live wire.

    The switched live might be a sensor input rather than supplying power. I
    note the wiring diagram:
    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    allows for a fuse in just the live feed.

    Nevertheless I still feel that is an issue and would prefer the light
    and fan on it's own fuse.

    Although you could put a
    2nd fuse into teh Switched live, you then could have an unsafe situation
    where if a fuse opens, unless one is diligent about opening the fan
    isolator switch, one could be working on a fan thinking its completely
    dead when in fact either teh permanent Live or switched Live is still Live!

    As long as the wires are correctly sleeved, anyone gaining access to the terminals ought to be checking to see if a wire is live and remove power wherever possible.


    Look again the diagram for the timer version shows the switched live tapped
    off the live connection after the 3A fuse

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SH@21:1/5 to Tricky Dicky on Fri Jan 5 15:33:59 2024
    On 05/01/2024 15:22, Tricky Dicky wrote:
    Fredxx <fredxx@spam.invalid> wrote:
    On 05/01/2024 11:41, SH wrote:
    On 05/01/2024 11:32, SH wrote:
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I
    can see is 2A


    I have a 5 bedroom house and I have literally just counted the number
    of bulbs on all of my lighting circuits (I have 4 lighting circuits.)

    The one with the most lamps is the ground floor with 55 lamps, all are >>>> LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives
    330 Watts. There is an extractor fan on the d/stairs toilet fed by
    this circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4 watts >>>> to 20 watts. Lets take the 20 watts figure as worst case and multiply
    by 18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a
    supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of 660 >>>> Watts at a supply voltage of 220 watts which is almost double the the
    wattage assuming *all* lamps were all on at the same time. In practie
    very few of us actually have *all* the lamps on at the same time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit is >>>> that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.




    Coming back to the original OP's query,

    It strikces me that there is a possible solution but with a Caveat (*)

    Put in a dry lining box next to the light fitting.

    Transfer the Power Loop in and Power loop Out cables from the existing
    light fitting to the new drylining box.

    Then wire in some twin and earth cable from the new drylining box and
    then fit a FCU to this drylining box so that the bathroom light is now
    on its own 3A supply.

    It is assumed that the wall switch also runs to the existing rose and
    that the 3 core & E is also taken from the existing rose to the isolator >>> switch and thence onwards to the fan.

    (*) you will need to pay attention to the special zones of bathrooms
    such that (a) the FCU is at a sifficient distance and hieght away from
    the bath or shower and (b) with it being a humid atmosphere, humidity
    may get inside teh FCU so it might be prudent to use a IP66 rated FCU
    enclosure OR extend the power loop in, power loop out and the bridging
    cable so that teh FCU can be mounted somewhere outside the bathroom.

    As a side point, putting a 3A fuse into the Live in for the fan does not >>> offer any protection to the switched live wire.

    The switched live might be a sensor input rather than supplying power. I
    note the wiring diagram:
    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    allows for a fuse in just the live feed.

    Nevertheless I still feel that is an issue and would prefer the light
    and fan on it's own fuse.

    Although you could put a
    2nd fuse into teh Switched live, you then could have an unsafe situation >>> where if a fuse opens, unless one is diligent about opening the fan
    isolator switch, one could be working on a fan thinking its completely
    dead when in fact either teh permanent Live or switched Live is still Live! >>
    As long as the wires are correctly sleeved, anyone gaining access to the
    terminals ought to be checking to see if a wire is live and remove power
    wherever possible.


    Look again the diagram for the timer version shows the switched live tapped off the live connection after the 3A fuse



    Fig 3 assumes you dont have power loop in and power loop out at the
    lighting rose....

    The circuit digram would be more complex once the power loop in and
    power loop out is added....

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Fredxx on Fri Jan 5 18:03:06 2024
    On 05/01/2024 13:21, Fredxx wrote:
    On 05/01/2024 13:15, John Rumm wrote:
    On 04/01/2024 14:21, nothanks@aolbin.com wrote:
    On 03/01/2024 16:48, nothanks@aolbin.com wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This
    will
    have a 3 pole isolator outside the bathroom and the plan is to run
    it in
    conjunction with the bathroom light so that the fan comes on when
    the light
    is operated typical of many windowless bathrooms and en-suites in many >>>>> modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for
    live and
    switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the >>>>> bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling
    fans in the
    rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom
    light as
    planned and using two FCU’s
    One for live and the other for switched live before running the
    rest of the
    cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My
    daughters
    new build has one bathroom, 2 en-suites and a cloakroom/WC all
    windowless
    and all with ventilators activated by the light switch and I know
    all the
    lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for
    the MF100T
    has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    Not an answer, but a suggestion: consider having two pull switches,
    one for the fan and one for the light, rather than having the fan
    always come on with the light. This means you don't have the fan
    noise at night time and you can leave the fan on for a while in the
    morning after a vindaloo supper the night before.

    A further thought: you could put a 3A fuse inside the fan enclosure
    if you wanted a fuse but not an FCU.

    That can work, but will be limited to fans with only one live connection.

    If it has run on, then you would need a fuse protecting its permanent
    live and another one on the switched live. Now you have two fuses in
    parallel protecting the same device which is not good in a number of
    ways.

    The Manrose install sheet only requires a fuse on the permanent live.
    Why the need for two fuses? The switched live can be treated a signal
    wire and I presume doesn't supply any current to the fan.

    You can't really extrapolate from one fan to all. If you need a 3A fused supply, then it is better IMHO to run all inputs to the fan from the
    same supply.

    If that is the case there is perhaps no need for the triple isolation
    switch?

    You need the triple isolator to make sure mains can't reach the fan
    while maintaining it. Some fans will run with neutral and a live feed to
    the switched live terminal. (they will only need the perm live connected
    to "run on")

    If the fuse is fan side of the 3-pole isolation switch then it can be changed, or altered, whilst being fully isolated without switching the lighting MCB.

    Most faceplate installed fuses can be safely changed live anyway - the
    fuse carrier inserts and removes it, and the terminals are not (easily) touchable.

    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SteveW@21:1/5 to All on Fri Jan 5 20:46:30 2024
    On 05/01/2024 11:32, SH wrote:

    <snip>

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit is
    that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    And in my case *HAVE* to be, as it is a Crabtree Starbreaker, with their
    own design of busbar and devices that plug directly into it and have no incoming Live terminal.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From nothanks@aolbin.com@21:1/5 to John Rumm on Fri Jan 5 20:57:28 2024
    On 05/01/2024 13:15, John Rumm wrote:
    On 04/01/2024 14:21, nothanks@aolbin.com wrote:
    On 03/01/2024 16:48, nothanks@aolbin.com wrote:
    On 03/01/2024 16:07, Tricky Dicky wrote:

    I am fitting a Manrose MF100T ventilation fan in our bathroom. This
    will
    have a 3 pole isolator outside the bathroom and the plan is to run
    it in
    conjunction with the bathroom light so that the fan comes on when
    the light
    is operated typical of many windowless bathrooms and en-suites in many >>>> modern houses.

    The issue is that the manufacturer specify’s a 3A max. fuse for live >>>> and
    switched live and of course the lighting circuit is 6A.

    One option is to fit a fused spur unit into the incoming feed for the
    bathroom but that means all lights beyond that point would now be
    protected
    by a 3A fuse and the issue is that there are at least 3 ceiling fans
    in the
    rooms beyond that point.

    An alternative is to take 3-core and E cable from the bathroom light as >>>> planned and using two FCU’s
    One for live and the other for switched live before running the rest
    of the
    cable to the 3-pole isolator.

    The trouble is that I have not seen this arrangement anywhere. My
    daughters
    new build has one bathroom, 2 en-suites and a cloakroom/WC all
    windowless
    and all with ventilators activated by the light switch and I know
    all the
    lighting circuits are 6A.

    So what to do?

    I have a link to a similar fan which unlike the instructions for the
    MF100T
    has a wiring diagram

    https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    Not an answer, but a suggestion: consider having two pull switches,
    one for the fan and one for the light, rather than having the fan
    always come on with the light. This means you don't have the fan
    noise at night time and you can leave the fan on for a while in the
    morning after a vindaloo supper the night before.

    A further thought: you could put a 3A fuse inside the fan enclosure if
    you wanted a fuse but not an FCU.

    That can work, but will be limited to fans with only one live connection.

    If it has run on, then you would need a fuse protecting its permanent
    live and another one on the switched live. Now you have two fuses in
    parallel protecting the same device which is not good in a number of ways.


    Agreed. Having multiple, independently isolated, supplies to one device
    is a recipe for an unpleasant surprise for someone. My main point is
    that being able to directly control the fan has value, especially near a bedroom.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Fredxx on Sat Jan 6 16:37:52 2024
    On 05/01/2024 12:18, Fredxx wrote:
    On 05/01/2024 11:41, SH wrote:
    On 05/01/2024 11:32, SH wrote:
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I
    can see is 2A


    I have a 5 bedroom house and I have literally just counted the number
    of bulbs on all of my lighting circuits (I have 4 lighting circuits.)

    The one with the most lamps is the ground floor with 55 lamps, all
    are LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives
    330 Watts. There is an extractor fan on the d/stairs toilet fed by
    this circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4
    watts to 20 watts. Lets take the 20 watts figure as worst case and
    multiply by 18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a
    supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of
    660 Watts at a supply voltage of 220 watts which is almost double the
    the wattage assuming *all* lamps were all on at the same time. In
    practie very few of us actually have *all* the lamps on at the same
    time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit
    is that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.




    Coming back to the original OP's query,

    It strikces me that there is a possible solution but with a Caveat (*)

    Put in a dry lining box next to the light fitting.

    Transfer the Power Loop in and Power loop Out cables from the existing
    light fitting to the new drylining box.

    Then wire in some twin and earth cable from the new drylining box and
    then fit a FCU to this drylining box so that the bathroom light is now
    on its own 3A supply.

    It is assumed that the wall switch also runs to the existing rose and
    that the 3 core & E is also taken from the existing rose to the
    isolator switch and thence onwards to the fan.

    (*) you will need to pay attention to the special zones of bathrooms
    such that (a) the FCU is at a sifficient distance and hieght away from
    the bath or shower and (b) with it being a humid atmosphere, humidity
    may get inside teh FCU so it might be prudent to use a IP66 rated FCU
    enclosure OR extend the power loop in, power loop out and the bridging
    cable so that teh FCU can be mounted somewhere outside the bathroom.

    As a side point, putting a 3A fuse into the Live in for the fan does
    not offer any protection to the switched live wire.

    The switched live might be a sensor input rather than supplying power. I
    note the wiring diagram:
      https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    allows for a fuse in just the live feed.

    Take another look - in particular fig 3. The first two examples are only
    for single live feeds.

    If you look at fig 3 - the first example with two live connections, you
    will note that *both* are derived from the fused supply.

    Nevertheless I still feel that is an issue and would prefer the light
    and fan on it's own fuse.

    If the switched live is feeding both the fan and the light, the they
    *must* both be fed from the fused supply.

    Although you could put a 2nd fuse into teh Switched live, you then
    could have an unsafe situation where if a fuse opens, unless one is
    diligent about opening the fan isolator switch, one could be working
    on a fan thinking its completely dead when in fact either teh
    permanent Live or switched Live is still Live!

    As long as the wires are correctly sleeved, anyone gaining access to the terminals ought to be checking to see if a wire is live and remove power wherever possible.


    While true, that is no excuse for dangerous shoddy work.

    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to All on Sat Jan 6 16:41:10 2024
    On 05/01/2024 15:33, SH wrote:
    On 05/01/2024 15:22, Tricky Dicky wrote:
    Fredxx <fredxx@spam.invalid> wrote:
    On 05/01/2024 11:41, SH wrote:
    On 05/01/2024 11:32, SH wrote:
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I >>>>>> can see is 2A


    I have a 5 bedroom house and I have literally just counted the number >>>>> of bulbs on all of my lighting circuits (I have 4 lighting circuits.) >>>>>
    The one with the most lamps is the ground floor with 55 lamps, all are >>>>> LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives >>>>> 330 Watts. There is an extractor fan on the d/stairs toilet fed by
    this circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4 watts >>>>> to 20 watts. Lets take the 20 watts figure as worst case and multiply >>>>> by 18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a
    supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of 660 >>>>> Watts at a supply voltage of 220 watts which is almost double the the >>>>> wattage assuming *all* lamps were all on at the same time. In practie >>>>> very few of us actually have *all* the lamps on at the same time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer unit is >>>>> that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.




    Coming back to the original OP's query,

    It strikces me that there is a possible solution but with a Caveat (*) >>>>
    Put in a dry lining box next to the light fitting.

    Transfer the Power Loop in and Power loop Out cables from the existing >>>> light fitting to the new drylining box.

    Then wire in some twin and earth cable from the new drylining box and
    then fit a FCU to this drylining box so that the bathroom light is now >>>> on its own 3A supply.

    It is assumed that the wall switch also runs to the existing rose and
    that the 3 core & E is also taken from the existing rose to the
    isolator
    switch and thence onwards to the fan.

    (*) you will need to pay attention to the special zones of bathrooms
    such that (a) the FCU is at a sifficient distance and hieght away from >>>> the bath or shower and (b) with it being a humid atmosphere, humidity
    may get inside teh FCU so it might be prudent to use a IP66 rated FCU
    enclosure OR extend the power loop in, power loop out and the bridging >>>> cable so that teh FCU can be mounted somewhere outside the bathroom.

    As a side point, putting a 3A fuse into the Live in for the fan does
    not
    offer any protection to the switched live wire.

    The switched live might be a sensor input rather than supplying power. I >>> note the wiring diagram:
       https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf
    allows for a fuse in just the live feed.

    Nevertheless I still feel that is an issue and would prefer the light
    and fan on it's own fuse.

    Although you could put a
    2nd fuse into teh Switched live, you then could have an unsafe
    situation
    where if a fuse opens, unless one is diligent about opening the fan
    isolator switch, one could be working on a fan thinking its completely >>>> dead when in fact either teh permanent Live or switched Live is
    still Live!

    As long as the wires are correctly sleeved, anyone gaining access to the >>> terminals ought to be checking to see if a wire is live and remove power >>> wherever possible.


    Look again the diagram for the timer version shows the switched live
    tapped
    off the live connection after the 3A fuse



    Fig 3 assumes you dont have power loop in and power loop out at the
    lighting rose....

    The circuit digram would be more complex once the power loop in and
    power loop out is added....

    Here is what you need with loop in wiring:

    https://wiki.diyfaq.org.uk/index.php/Extractor_fan_wiring#Simplified_Schematic_Version

    That can all be done from a ceiling rose with one additional terminal
    required:

    https://wiki.diyfaq.org.uk/images/f/f3/CeilingRoseFusedFanConnection.png

    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Graham.@21:1/5 to All on Sat Jan 6 17:49:17 2024
    That was my thought too. Some 3A MCBs do exist but relatively
    rare.I would have thought the fan would have it's own internal
    fuse, even a non-replaceable one.

    All the faulty mains bathroom fans that I have examined have had a
    thermal fuse buried in the winding. I have concluded that it's a
    requirment.


    --

    Graham.
    %Profound_observation%

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Fredxx@21:1/5 to Graham. on Sat Jan 6 19:21:21 2024
    On 06/01/2024 17:49, Graham. wrote:
    That was my thought too. Some 3A MCBs do exist but relatively
    rare.I would have thought the fan would have it's own internal
    fuse, even a non-replaceable one.

    All the faulty mains bathroom fans that I have examined have had a
    thermal fuse buried in the winding. I have concluded that it's a
    requirment.

    I don't know of any British Standard or other requirement but it is
    common for a winding to have some internal thermal protection. It only
    takes a shorted turn or similar failure for the device to overheat and
    melt a housing, yet not draw sufficient current for a fuse to blow.

    I'm therefore sceptical of the enhanced safety using a 3 Amp fuse in the
    OP's example as opposed to a 5 or 6 Amp MCB.

    I am aware of the control circuitry for a fan with an internal timer,
    using discrete ICs and thyristor, but I still don't see the advantage.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Green@21:1/5 to graham-usenet@mail.com on Sat Jan 6 20:29:07 2024
    Graham. <graham-usenet@mail.com> wrote:
    That was my thought too. Some 3A MCBs do exist but relatively
    rare.I would have thought the fan would have it's own internal
    fuse, even a non-replaceable one.

    They're not **that** difficult to find. I have a load of 2 amp ones
    which were a bit of a nuisance to be honest because they were the only
    ones I could find that fitted into the CU on my boat. I kept tripping
    them when I tried to run the vacuum cleaner or an electric heater on
    those circuits. I have since replaced them with more suitable ratings
    (it wasn't totally trivial because they were two pole breakers that
    disconnect both live and neutral).


    --
    Chris Green
    ·

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SH@21:1/5 to John Rumm on Sun Jan 7 12:59:47 2024
    On 06/01/2024 16:41, John Rumm wrote:
    On 05/01/2024 15:33, SH wrote:
    On 05/01/2024 15:22, Tricky Dicky wrote:
    Fredxx <fredxx@spam.invalid> wrote:
    On 05/01/2024 11:41, SH wrote:
    On 05/01/2024 11:32, SH wrote:
    On 05/01/2024 10:51, Andy Burns wrote:
    SteveW wrote:

    6A seems to be the lowest rated RCBO for my consumer unit.

    Plenty of 1A MCBs and even the occasional 0.5A, but smallest RCBO I >>>>>>> can see is 2A


    I have a 5 bedroom house and I have literally just counted the number >>>>>> of bulbs on all of my lighting circuits (I have 4 lighting circuits.) >>>>>>
    The one with the most lamps is the ground floor with 55 lamps, all >>>>>> are
    LED lamps or LED Strips. All are at 4 to 6 watts.

    So lets take the highest wattage bulb and multiply by 55. This gives >>>>>> 330 Watts. There is an extractor fan on the d/stairs toilet fed by >>>>>> this circuit.

    The one with the highest wattage lamps is the outdoor floodlights
    circuit and there are 18 floodlamps with wattages ranging from 4
    watts
    to 20 watts. Lets take the 20 watts figure as worst case and multiply >>>>>> by 18 which gives 350 Watts

    A 6A MCB or RCBO supports a continuous current of 1320 Watta at a
    supply voltage of 220 watts so 6A is cleary more than adequate.

    Swapping to a 3A MCB or RCBO would support a continuous current of >>>>>> 660
    Watts at a supply voltage of 220 watts which is almost double the the >>>>>> wattage assuming *all* lamps were all on at the same time. In practie >>>>>> very few of us actually have *all* the lamps on at the same time.

    The main issue with swapping out NCBs/RCBOs/RCDs in a consumer
    unit is
    that it is mandataed somewhere that the consumer unit and the
    MCBs/RCBOs/RCDs *should* be from the same manufacturer.

    S.




    Coming back to the original OP's query,

    It strikces me that there is a possible solution but with a Caveat (*) >>>>>
    Put in a dry lining box next to the light fitting.

    Transfer the Power Loop in and Power loop Out cables from the existing >>>>> light fitting to the new drylining box.

    Then wire in some twin and earth cable from the new drylining box and >>>>> then fit a FCU to this drylining box so that the bathroom light is now >>>>> on its own 3A supply.

    It is assumed that the wall switch also runs to the existing rose and >>>>> that the 3 core & E is also taken from the existing rose to the
    isolator
    switch and thence onwards to the fan.

    (*) you will need to pay attention to the special zones of bathrooms >>>>> such that (a) the FCU is at a sifficient distance and hieght away from >>>>> the bath or shower and (b) with it being a humid atmosphere, humidity >>>>> may get inside teh FCU so it might be prudent to use a IP66 rated FCU >>>>> enclosure OR extend the power loop in, power loop out and the bridging >>>>> cable so that teh FCU can be mounted somewhere outside the bathroom. >>>>>
    As a side point, putting a 3A fuse into the Live in for the fan
    does not
    offer any protection to the switched live wire.

    The switched live might be a sensor input rather than supplying
    power. I
    note the wiring diagram:
       https://www.manrose.co.uk/wp-content/uploads/doc/FandWs/496934.pdf >>>> allows for a fuse in just the live feed.

    Nevertheless I still feel that is an issue and would prefer the light
    and fan on it's own fuse.

    Although you could put a
    2nd fuse into teh Switched live, you then could have an unsafe
    situation
    where if a fuse opens, unless one is diligent about opening the fan
    isolator switch, one could be working on a fan thinking its completely >>>>> dead when in fact either teh permanent Live or switched Live is
    still Live!

    As long as the wires are correctly sleeved, anyone gaining access to
    the
    terminals ought to be checking to see if a wire is live and remove
    power
    wherever possible.


    Look again the diagram for the timer version shows the switched live
    tapped
    off the live connection after the 3A fuse



    Fig 3 assumes you dont have power loop in and power loop out at the
    lighting rose....

    The circuit digram would be more complex once the power loop in and
    power loop out is added....

    Here is what you need with loop in wiring:

    https://wiki.diyfaq.org.uk/index.php/Extractor_fan_wiring#Simplified_Schematic_Version

    That can all be done from a ceiling rose with one additional terminal required:

    https://wiki.diyfaq.org.uk/images/f/f3/CeilingRoseFusedFanConnection.png



    One coould in fact use a 3 terminal wago connector provided there was
    room in the ceiling rose..


    Or alternatively, use a round dry lining box behind the exisiting rose
    for more room/