• Water, water everywhere

    From Tricky Dicky@21:1/5 to All on Sun Feb 25 00:45:48 2024
    Today I had a flood in the bathroom. A compression joint connecting the
    copper pipe work to a short length of plastic pipe to the digital shower
    mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I went copper up to the push fit connectors Mira have specified it would have resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so there maybe the nut had not been fully tightened, but that usually results
    in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and compression fittings as necessary and have never felt 100% confident in
    plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about plastic pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management
    was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From RJH@21:1/5 to Dicky on Sun Feb 25 01:12:14 2024
    On 25 Feb 2024 at 00:45:48 GMT, Tricky Dicky wrote:


    Today I had a flood in the bathroom. A compression joint connecting the copper pipe work to a short length of plastic pipe to the digital shower mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I went copper up to the push fit connectors Mira have specified it would have resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so there maybe the nut had not been fully tightened, but that usually results
    in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and compression fittings as necessary and have never felt 100% confident in plastic and push fit joins other than for low pressure waste pipe applications. Today’s experience has not improved my feelings about plastic pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.

    Not sure of the cause - overtightened compression fitting maybe? I'd try a pushfit plastic connector - I've done a fair few plastic-copper connections using them.
    --
    Cheers, Rob, Sheffield UK

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Tricky Dicky on Sun Feb 25 02:45:55 2024
    On 25/02/2024 00:45, Tricky Dicky wrote:

    Today I had a flood in the bathroom. A compression joint connecting the copper pipe work to a short length of plastic pipe to the digital shower mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I went copper up to the push fit connectors Mira have specified it would have resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so there maybe the nut had not been fully tightened, but that usually results
    in a weeping join.

    Not tight enough would be my guess... The rubber seals on the insert
    will keep it watertight with relatively little compression force, but inadequate tightening allows scope for the pipe to slowly be pushed out
    of the joint by water hammer and other pressure fluctuations.

    I am a bit old school in that I prefer copper and soldered joins and compression fittings as necessary and have never felt 100% confident in plastic and push fit joins other than for low pressure waste pipe applications. Today’s experience has not improved my feelings about plastic pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    To be fair I have never had a problem with plastic, although for plastic
    to copper joints I would normally use a pushfit fitting. (probably
    because I keep a sizeable stock of end feed, a handful of pushfit, and
    fairly few compression fittings.

    Anyway, I cannot say I feel confident in the repair and domestic management was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.

    Torque up the compression a bit more... or use copper and put a small
    offset "set" in the pipe with a pipe bender.


    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tim+@21:1/5 to Dicky on Sun Feb 25 08:09:41 2024
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    Today I had a flood in the bathroom. A compression joint connecting the copper pipe work to a short length of plastic pipe to the digital shower mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I went copper up to the push fit connectors Mira have specified it would have resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so there maybe the nut had not been fully tightened, but that usually results
    in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and compression fittings as necessary and have never felt 100% confident in plastic and push fit joins other than for low pressure waste pipe applications. Today’s experience has not improved my feelings about plastic pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.



    You mention a “digital” shower mixer. Does it use a solenoid to shut the water off? Just wondering if the abrupt nature of the shut off could be a factor?

    Tim

    --
    Please don't feed the trolls

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Sid.@21:1/5 to All on Sun Feb 25 08:03:40 2024
    Perhaps the main water is higher, mine varies quite a bit.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SH@21:1/5 to RJH on Sun Feb 25 08:57:06 2024
    On 25/02/2024 01:12, RJH wrote:
    On 25 Feb 2024 at 00:45:48 GMT, Tricky Dicky wrote:


    Today I had a flood in the bathroom. A compression joint connecting the
    copper pipe work to a short length of plastic pipe to the digital shower
    mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I >> went copper up to the push fit connectors Mira have specified it would have >> resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so >> there maybe the nut had not been fully tightened, but that usually results >> in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and
    compression fittings as necessary and have never felt 100% confident in
    plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about plastic
    pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management >> was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.

    Not sure of the cause - overtightened compression fitting maybe? I'd try a pushfit plastic connector - I've done a fair few plastic-copper connections using them.


    did you put a pipe stiffener at *each* end of the plastic pipe?

    And another cause can be incorrect pipe insertion depth into the
    fitting, some plastic pipe have a repeating black line on the outside of
    the pipe, the idea being you cut at one of the black lines, and then put
    pipe stiffener on, then insert into fitting until you reach the 2nd
    black line on the pipe......

    And as others have said, not screwing up the plastic pipe fitting up
    tight enough. if the pipe is loose, then water hammer will flex the pipe
    and those knife blades will cut grooves and work its wat to the end of
    the pipe with each successive water hammer session.


    Also clipping down the water pipe will reduce the effect of pipe
    movement due to water hammer.

    S.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From nothanks@aolbin.com@21:1/5 to Tricky Dicky on Sun Feb 25 09:57:33 2024
    On 25/02/2024 00:45, Tricky Dicky wrote:

    Today I had a flood in the bathroom. A compression joint connecting the copper pipe work to a short length of plastic pipe to the digital shower mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I went copper up to the push fit connectors Mira have specified it would have resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so there maybe the nut had not been fully tightened, but that usually results
    in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and compression fittings as necessary and have never felt 100% confident in plastic and push fit joins other than for low pressure waste pipe applications. Today’s experience has not improved my feelings about plastic pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.

    A long time ago (18 years?) I had a near disaster when a 22mm plastic
    pipe came out of a compression elbow, fortunately the SWMBO at the time happened to come home very soon after it happened and turned the water
    off before there was much damage. I decided it was probably caused by
    thermal expansion on a long pipe run trying to move the elbow and the
    short run on the other side of the elbow preventing it from moving ... resulting in the pipe walking out of the fitting. I replaced the
    compression elbow with pushfit, restrained the pipe, and allowed the
    short run to move.
    I realise that your problem was on a cold pipe, but perhaps repeated
    hydraulic shock, from the solenoid shutting-off or from general water
    hammer, pushed the pipe out. I always use pushfit for plastic-copper transition.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to All on Sun Feb 25 14:07:12 2024
    On 25/02/2024 08:57, SH wrote:
    On 25/02/2024 01:12, RJH wrote:
    On 25 Feb 2024 at 00:45:48 GMT, Tricky  Dicky wrote:


    Today I had a flood in the bathroom. A compression joint connecting the
    copper pipe work to a short length of plastic pipe to the digital shower >>> mixer failed and being at mains pressure produced a spectacular
    fountain.

    This joint was made mid December and has been fine ever since. The
    reason
    for the short plastic pipe was due to the pipe clips I was using
    meant if I
    went copper up to the push fit connectors Mira have specified it
    would have
    resulted in an awkward little off-set so the plastic pipe solved that. I >>> have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did >>> note the olive did not seem to have bitten into the plastic as
    expected so
    there maybe the nut had not been fully tightened, but that usually
    results
    in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and
    compression fittings as necessary and have never felt 100% confident in
    plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about
    plastic
    pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it >>> just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic
    management
    was not best pleased with the soaked towels and bedding, especially with >>> the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.

    Not sure of the cause - overtightened compression fitting maybe? I'd
    try a
    pushfit plastic connector - I've done a fair few plastic-copper
    connections
    using them.


    did you put a pipe stiffener at *each* end of the plastic pipe?

    And another cause can be incorrect pipe insertion depth into the
    fitting, some plastic pipe have a repeating black line on the outside of
    the pipe, the idea being you cut at one of the black lines, and then put
    pipe stiffener on, then insert into fitting until you reach the 2nd
    black line on the pipe......

    I get the impression you might be assuming the fitting was push fit? The
    OP said it was a compression fitting that failed on the plastic pipe.

    The insertion depth marks may not be correct for a compression fitting -
    or even consistent between brands.


    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to Dicky on Sun Feb 25 14:35:36 2024
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    Today I had a flood in the bathroom. A compression joint connecting the copper pipe work to a short length of plastic pipe to the digital shower mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I went copper up to the push fit connectors Mira have specified it would have resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so there maybe the nut had not been fully tightened, but that usually results
    in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and compression fittings as necessary and have never felt 100% confident in plastic and push fit joins other than for low pressure waste pipe applications. Today’s experience has not improved my feelings about plastic pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.



    As a few have said it must have been an under tightened nut as the olive
    just slid off whereas previous compression joints to plastic have resulted
    in secure olives that could not be removed. It just puzzled me that there
    had been no weeping which is a common indication of an under tightened nut
    or that it did not come apart on first pressurisation as we have quite considerable pressure on the mains.

    Anyway SWAMBO has calmed down and the heat pump tumble dryer has been
    working overtime and stuff is going back in the airing cupboard. We are now worrying if it will happen again, I might put a pencil mark on the pipe and regularly observe it to see if any movement occurs.

    Thanks for all the replies.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Tricky Dicky on Sun Feb 25 16:26:20 2024
    On 25/02/2024 14:35, Tricky Dicky wrote:
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    Today I had a flood in the bathroom. A compression joint connecting the
    copper pipe work to a short length of plastic pipe to the digital shower
    mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I >> went copper up to the push fit connectors Mira have specified it would have >> resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so >> there maybe the nut had not been fully tightened, but that usually results >> in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and
    compression fittings as necessary and have never felt 100% confident in
    plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about plastic
    pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management >> was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.



    As a few have said it must have been an under tightened nut as the olive
    just slid off whereas previous compression joints to plastic have resulted
    in secure olives that could not be removed. It just puzzled me that there
    had been no weeping which is a common indication of an under tightened nut
    or that it did not come apart on first pressurisation as we have quite considerable pressure on the mains.

    What inserts were you using? The speedfit ones I normally use[1] have
    several O rings on them to seal in the bore of the pipe and also in the
    bore of the fitting. The olive is not really required to make the joint
    water tight in this case - it just needs to grip the pipe well enough to
    stop it being pulled out.

    [1] https://wiki.diyfaq.org.uk/index.php/File:InsertForPlasticPipe.jpg

    (and two more rings on the stem of the insert that seal on the inside of
    the pipe bore)


    Anyway SWAMBO has calmed down and the heat pump tumble dryer has been
    working overtime and stuff is going back in the airing cupboard. We are now worrying if it will happen again, I might put a pencil mark on the pipe and regularly observe it to see if any movement occurs.
    Probably not a bad idea for peace of mind...

    Failing that make up a compression to plastic fitting on the bench, then
    take it apart and work out how much tightening you need to properly
    deform the olive enough to bit into the pipe.


    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From nothanks@aolbin.com@21:1/5 to Tricky Dicky on Sun Feb 25 18:14:14 2024
    On 25/02/2024 14:35, Tricky Dicky wrote:
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    Today I had a flood in the bathroom. A compression joint connecting the
    copper pipe work to a short length of plastic pipe to the digital shower
    mixer failed and being at mains pressure produced a spectacular fountain.

    This joint was made mid December and has been fine ever since. The reason
    for the short plastic pipe was due to the pipe clips I was using meant if I >> went copper up to the push fit connectors Mira have specified it would have >> resulted in an awkward little off-set so the plastic pipe solved that. I
    have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did
    note the olive did not seem to have bitten into the plastic as expected so >> there maybe the nut had not been fully tightened, but that usually results >> in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and
    compression fittings as necessary and have never felt 100% confident in
    plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about plastic
    pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it
    just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management >> was not best pleased with the soaked towels and bedding, especially with
    the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.



    As a few have said it must have been an under tightened nut as the olive
    just slid off whereas previous compression joints to plastic have resulted
    in secure olives that could not be removed. It just puzzled me that there
    had been no weeping which is a common indication of an under tightened nut
    or that it did not come apart on first pressurisation as we have quite considerable pressure on the mains.

    Anyway SWAMBO has calmed down and the heat pump tumble dryer has been
    working overtime and stuff is going back in the airing cupboard. We are now worrying if it will happen again, I might put a pencil mark on the pipe and regularly observe it to see if any movement occurs.

    Thanks for all the replies.

    Re my earlier - can you replace the compression fitting with push fit?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to nothanks@aolbin.com on Mon Feb 26 09:55:36 2024
    <nothanks@aolbin.com> wrote:
    On 25/02/2024 14:35, Tricky Dicky wrote:
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    Today I had a flood in the bathroom. A compression joint connecting the
    copper pipe work to a short length of plastic pipe to the digital shower >>> mixer failed and being at mains pressure produced a spectacular fountain. >>>
    This joint was made mid December and has been fine ever since. The reason >>> for the short plastic pipe was due to the pipe clips I was using meant if I >>> went copper up to the push fit connectors Mira have specified it would have >>> resulted in an awkward little off-set so the plastic pipe solved that. I >>> have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did >>> note the olive did not seem to have bitten into the plastic as expected so >>> there maybe the nut had not been fully tightened, but that usually results >>> in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and
    compression fittings as necessary and have never felt 100% confident in
    plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about plastic
    pipe in mains pressure applications. It has left me wondering if it was
    more an external issue namely a temporary spike in water pressure and it >>> just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management >>> was not best pleased with the soaked towels and bedding, especially with >>> the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated.



    As a few have said it must have been an under tightened nut as the olive
    just slid off whereas previous compression joints to plastic have resulted >> in secure olives that could not be removed. It just puzzled me that there
    had been no weeping which is a common indication of an under tightened nut >> or that it did not come apart on first pressurisation as we have quite
    considerable pressure on the mains.

    Anyway SWAMBO has calmed down and the heat pump tumble dryer has been
    working overtime and stuff is going back in the airing cupboard. We are now >> worrying if it will happen again, I might put a pencil mark on the pipe and >> regularly observe it to see if any movement occurs.

    Thanks for all the replies.

    Re my earlier - can you replace the compression fitting with push fit?


    John Unfortunetly I used the plain inserts which have always worked in the past.

    As for push fit fittings I already had the compression fittings spare so
    simply used them as such joins always worked in the past. If it looks like
    the problem is likely to repeat using push fit will be an option.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From RJH@21:1/5 to Dicky on Mon Feb 26 10:20:17 2024
    On 26 Feb 2024 at 09:55:36 GMT, Tricky Dicky wrote:

    <nothanks@aolbin.com> wrote:
    On 25/02/2024 14:35, Tricky Dicky wrote:
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    Today I had a flood in the bathroom. A compression joint connecting the >>>> copper pipe work to a short length of plastic pipe to the digital shower >>>> mixer failed and being at mains pressure produced a spectacular fountain. >>>>
    This joint was made mid December and has been fine ever since. The reason >>>> for the short plastic pipe was due to the pipe clips I was using meant if I
    went copper up to the push fit connectors Mira have specified it would have
    resulted in an awkward little off-set so the plastic pipe solved that. I >>>> have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did >>>> note the olive did not seem to have bitten into the plastic as expected so >>>> there maybe the nut had not been fully tightened, but that usually results >>>> in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and
    compression fittings as necessary and have never felt 100% confident in >>>> plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about plastic
    pipe in mains pressure applications. It has left me wondering if it was >>>> more an external issue namely a temporary spike in water pressure and it >>>> just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management
    was not best pleased with the soaked towels and bedding, especially with >>>> the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated. >>>>


    As a few have said it must have been an under tightened nut as the olive >>> just slid off whereas previous compression joints to plastic have resulted >>> in secure olives that could not be removed. It just puzzled me that there >>> had been no weeping which is a common indication of an under tightened nut >>> or that it did not come apart on first pressurisation as we have quite
    considerable pressure on the mains.

    Anyway SWAMBO has calmed down and the heat pump tumble dryer has been
    working overtime and stuff is going back in the airing cupboard. We are now >>> worrying if it will happen again, I might put a pencil mark on the pipe and >>> regularly observe it to see if any movement occurs.

    Thanks for all the replies.

    Re my earlier - can you replace the compression fitting with push fit?


    John Unfortunetly I used the plain inserts which have always worked in the past.

    As for push fit fittings I already had the compression fittings spare so simply used them as such joins always worked in the past. If it looks like the problem is likely to repeat using push fit will be an option.

    I'd just add - make sure the pipe is clean, round and unscored. I had an issue with an unprotected plastic pipe pushed through a wall, and picked up some light scratched. The pushfit connector didn't seal to the pipe properly.
    --
    Cheers, Rob, Sheffield UK

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Tricky Dicky on Mon Feb 26 16:34:28 2024
    On 26/02/2024 09:55, Tricky Dicky wrote:
    <nothanks@aolbin.com> wrote:
    On 25/02/2024 14:35, Tricky Dicky wrote:
    Tricky Dicky <tricky.dicky@sky.com> wrote:

    Today I had a flood in the bathroom. A compression joint connecting the >>>> copper pipe work to a short length of plastic pipe to the digital shower >>>> mixer failed and being at mains pressure produced a spectacular fountain. >>>>
    This joint was made mid December and has been fine ever since. The reason >>>> for the short plastic pipe was due to the pipe clips I was using meant if I
    went copper up to the push fit connectors Mira have specified it would have
    resulted in an awkward little off-set so the plastic pipe solved that. I >>>> have been scratching my head as to the cause why after 21/2 months?

    At first I thought I may have omitted the insert but it was there, I did >>>> note the olive did not seem to have bitten into the plastic as expected so >>>> there maybe the nut had not been fully tightened, but that usually results >>>> in a weeping join.

    I am a bit old school in that I prefer copper and soldered joins and
    compression fittings as necessary and have never felt 100% confident in >>>> plastic and push fit joins other than for low pressure waste pipe
    applications. Today’s experience has not improved my feelings about plastic
    pipe in mains pressure applications. It has left me wondering if it was >>>> more an external issue namely a temporary spike in water pressure and it >>>> just found the weakest point?

    Anyway, I cannot say I feel confident in the repair and domestic management
    was not best pleased with the soaked towels and bedding, especially with >>>> the stuff she had ironed only a couple of hours before.

    Any opinions on the cause and suggested remedies would be appreciated. >>>>


    As a few have said it must have been an under tightened nut as the olive >>> just slid off whereas previous compression joints to plastic have resulted >>> in secure olives that could not be removed. It just puzzled me that there >>> had been no weeping which is a common indication of an under tightened nut >>> or that it did not come apart on first pressurisation as we have quite
    considerable pressure on the mains.

    Anyway SWAMBO has calmed down and the heat pump tumble dryer has been
    working overtime and stuff is going back in the airing cupboard. We are now >>> worrying if it will happen again, I might put a pencil mark on the pipe and >>> regularly observe it to see if any movement occurs.

    Thanks for all the replies.

    Re my earlier - can you replace the compression fitting with push fit?


    John Unfortunetly I used the plain inserts which have always worked in the past.

    Not actually my post :-)

    However, they will work with plain inserts, but will depend more on
    adequate tightening for the seal as well as just the mechanical restraint.

    As for push fit fittings I already had the compression fittings spare so simply used them as such joins always worked in the past. If it looks like the problem is likely to repeat using push fit will be an option.

    Either should work...


    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)