From time to time, we seem to experience a power "glitch", once a
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
From time to time, we seem to experience a power "glitch", once a
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
I assume this is some sort of switching transient that affects the
entire city (?) -- or, at least large portions of it.
Just get a 'scope monitoring the line power supply. Point a video camera (preferably with continuous time display) at the screen and record a few minutes before and after 3am every day. You should be able to record the spike and the exact time it appears. Even a webcam on a laptop might do
the job. The power supply company wouldn't be able to argue with that
sort of evidence.
3am seems a strange time for transients. Some sort of fairly regular maintenance work at the generation station or distribution switching, perhaps?
From time to time, we seem to experience a power "glitch", once a
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
I assume this is some sort of switching transient that affects the
entire city (?) -- or, at least large portions of it.
(our services are below grade so not likely caused by something
physically interfering with the transmission lines)
I'm turning my attention to the design of the power systems for
my current project and figure it would be prudent to put some
line-monitoring capabilities into it (if only to let it anticipate
such problems and plan ahead).
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
[Of course, I have to anticipate what the power conditions are
likely to be in other parts of the market (US consumer and,
separately, commercial/industrial) and not just rely on my own
observations.]
I'm tempted to buy a line monitor just to see what they've done
(in terms of hardware interface; the signal processing software
won't be a problem). Recommendations? (again, two/three different
markets, as above)
From time to time, we seem to experience a power "glitch", once a
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
I assume this is some sort of switching transient that affects the
entire city (?) -- or, at least large portions of it.
(our services are below grade so not likely caused by something
physically interfering with the transmission lines)
I'm turning my attention to the design of the power systems for
my current project and figure it would be prudent to put some
line-monitoring capabilities into it (if only to let it anticipate
such problems and plan ahead).
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
[Of course, I have to anticipate what the power conditions are
likely to be in other parts of the market (US consumer and,
separately, commercial/industrial) and not just rely on my own
observations.]
I'm tempted to buy a line monitor just to see what they've done
(in terms of hardware interface; the signal processing software
won't be a problem). Recommendations? (again, two/three different
markets, as above)
On 30/03/2022 03:25, Don Y wrote:
From time to time, we seem to experience a power "glitch", once a
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
I assume this is some sort of switching transient that affects the
entire city (?) -- or, at least large portions of it.
(our services are below grade so not likely caused by something
physically interfering with the transmission lines)
I'm turning my attention to the design of the power systems for
my current project and figure it would be prudent to put some
line-monitoring capabilities into it (if only to let it anticipate
such problems and plan ahead).
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
[Of course, I have to anticipate what the power conditions are
likely to be in other parts of the market (US consumer and,
separately, commercial/industrial) and not just rely on my own
observations.]
I'm tempted to buy a line monitor just to see what they've done
(in terms of hardware interface; the signal processing software
won't be a problem). Recommendations? (again, two/three different
markets, as above)
Just get a 'scope monitoring the line power supply. Point a video camera (preferably with continuous time display) at the screen and record a few minutes before and after 3am every day. You should be able to record the spike
and the exact time it appears. Even a webcam on a laptop might do the job. The
power supply company wouldn't be able to argue with that sort of evidence.
3am seems a strange time for transients. Some sort of fairly regular maintenance work at the generation station or distribution switching, perhaps?
On 2022-03-30 09:18, Jeff Layman wrote:
Just get a 'scope monitoring the line power supply. Point a video camera
(preferably with continuous time display) at the screen and record a few
minutes before and after 3am every day. You should be able to record the
spike and the exact time it appears. Even a webcam on a laptop might do
the job. The power supply company wouldn't be able to argue with that
sort of evidence.
3am seems a strange time for transients. Some sort of fairly regular
maintenance work at the generation station or distribution switching,
perhaps?
Or better: use a low voltage transformer and a resistive attenuator,
then capture the 1Vpp waveform on the LINE IN audio channel of a laptop. Capture and analyze using e.g. the free Audacity, it shows the waveform nicely. Much easier than trying to find a transient on a video (even
when the scope did capture it - some scopes have a low acquisition frame
rate and may miss a spike completely).
Arie
Arie de Muijnck <eternal....@ademu.com> wrote:
On 2022-03-30 09:18, Jeff Layman wrote:
Just get a 'scope monitoring the line power supply. Point a video camera >> (preferably with continuous time display) at the screen and record a few >> minutes before and after 3am every day. You should be able to record the >> spike and the exact time it appears. Even a webcam on a laptop might do
the job. The power supply company wouldn't be able to argue with that
sort of evidence.
3am seems a strange time for transients. Some sort of fairly regular
maintenance work at the generation station or distribution switching,
perhaps?
Or better: use a low voltage transformer and a resistive attenuator,
then capture the 1Vpp waveform on the LINE IN audio channel of a laptop. Capture and analyze using e.g. the free Audacity, it shows the waveform nicely. Much easier than trying to find a transient on a video (even
when the scope did capture it - some scopes have a low acquisition frame rate and may miss a spike completely).
ArieA transformer will have poor high frequency response and will filter out sharp spikes. Better to use a 100:1 capacitive/resistive divider across the AC line voltage. Verify the LINE IN audio channel is 600 ohms, then add a 600k across the top capacitor.
The neutral doesn't have to connect to the chassis of the computer. If you do, it will likely blow any GFI breaker that is on the ac line. Use GND for the return.
On Wednesday, 30 March 2022 at 12:09:14 UTC+1, Mike Monett wrote:
Arie de Muijnck <eternal....@ademu.com> wrote:
On 2022-03-30 09:18, Jeff Layman wrote:A transformer will have poor high frequency response and will filter out
Just get a 'scope monitoring the line power supply. Point a video camera >>>> (preferably with continuous time display) at the screen and record a few >>>> minutes before and after 3am every day. You should be able to record the >>>> spike and the exact time it appears. Even a webcam on a laptop might do >>>> the job. The power supply company wouldn't be able to argue with that
sort of evidence.
3am seems a strange time for transients. Some sort of fairly regular
maintenance work at the generation station or distribution switching,
perhaps?
Or better: use a low voltage transformer and a resistive attenuator,
then capture the 1Vpp waveform on the LINE IN audio channel of a laptop. >>> Capture and analyze using e.g. the free Audacity, it shows the waveform
nicely. Much easier than trying to find a transient on a video (even
when the scope did capture it - some scopes have a low acquisition frame >>> rate and may miss a spike completely).
Arie
sharp spikes. Better to use a 100:1 capacitive/resistive divider across the >> AC line voltage. Verify the LINE IN audio channel is 600 ohms, then add a
600k across the top capacitor.
The neutral doesn't have to connect to the chassis of the computer. If you >> do, it will likely blow any GFI breaker that is on the ac line. Use GND for >> the return.
But are sharp spikes likely to be a problem? Any product which has been through regulatory testing will have demonstrated a good immunity to
large short spikes, so it is much more likely that dropouts will cause problems.
A small transformer will respond to frequencies of many kHz, so that should be enough. What will prevent it from measuring large spikes is core saturation but there are several ways of minimising the effects of this
that have been discussed here in the past.
Most products, especially those with switched mode power supplies,
should survive dropouts of 10ms or less without any problems
due to energy storage in their input capacitors.
John
You've missed the point of (my!) post. The goal isn't to "protect" the
device -- OBSERVING the line won't do anything to make the device more resilient!
From time to time, we seem to experience a power "glitch", once a
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
We had repeated trips of the whole-house RCD every few days for months.
...
On Wednesday, 30 March 2022 at 13:12:48 UTC+1, Don Y wrote:
You've missed the point of (my!) post. The goal isn't to "protect" theOK. I can see why measuring disturbances that won't affect your
device -- OBSERVING the line won't do anything to make the device more
resilient!
devices could be useful. The question then becomes one of how
much measurement bandwidth and resolution is necessary to get
this unknown information and how best to acquire it and process it.
As you don't know what you are looking for about the only
bandwidth constraint is going to be the bandwidth of the power
transmission system subject to avoiding frequencies high enough
to have long-wave broadcast transmissions. That suggests an
upper frequency limit of maybe tens of kHz.
Of course, arcing in
nearby wiring could have much higher frequency components.
Maybe its worth looking at how arc fault interrupters detect arcing?
The power network over here switches, sometimes 2 times a day, between networks it seems.
This causes a short (usually less than a second) power dip.
UPS takes care of that as far as computers go.
Laptop has its on battery and will run much longer,
I'm turning my attention to the design of the power systems for
my current project and figure it would be prudent to put some
line-monitoring capabilities into it (if only to let it anticipate
such problems and plan ahead).
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
I'd like to use a laptop for a control application in an unattended
location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like laptops can't do that for some reason. I'd love to find one that does.
On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:
I'd like to use a laptop for a control application in an unattended
location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like
laptops can't do that for some reason. I'd love to find one that does.
MacOS laptops can be scheduled for turn-on and/or off once a day, with
the 'energy saver' settings. UPS connection sometimes adds options, too.
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
It's relatively important to have an average-AC-voltage measure,
because some wiring issues can be diagnosed that way; you'd want to
sample rectified/filtered V at tenth second or so, but only log 'events', not keep all the data. There's a few percent variance allowable, of course.
Load changes and loose connections or lightning strikes, or
diurnal overvoltage because of xformer tap decisions could show up.
Sites vary, but expect 2kV for miliseconds, in case of lightning.
More important surges or loads will cause zero-cross timing shifts which
tie into odd clunks from motors, so I'd think to log also any deviation from 'normal' 120 (or 100) zero crossings per second. Maybe store a few dozen cycles before and after an 'event', gives you an idea of the transient. Motor
starts without zero-voltage-switching have dimmed my lights and
several times rebooted a Linux box exactly when I hear the buzzsaw.
On 30/3/22 1:25 pm, Don Y wrote:
From time to time, we seem to experience a power "glitch", once a
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
I assume this is some sort of switching transient that affects the
entire city (?) -- or, at least large portions of it.
We had repeated trips of the whole-house RCD every few days for months. Always at 7:58AM. ALWAYS. I turned off everything in the house that
could know the time of day, and they still happened. Eventually I became certain that it was something to do with the power supply, and started harassing our provider.
They kept fobbing me off, saying I should replace the RCD - which at the
time was brand-new, after a renovation where we got a new powerboard,
and I told them that and insisted.
Eventually they admitted that 7:58AM is when they switch in some large
PFC capacitors in preparation for inductive industrial loads coming
alive. I told them that it was therefore their problem, and they
arranged to send a couple of electricians around to fit a more tolerant
RCD, at no cost to me.
When the sparkies came, they said they had been doing *hundreds* like
this. And that's just for the households who figured it out, and
complained long and hard enough to wear down the power company.
This was in 2000, before we started fitting RCD breakers on every circuit.
Clifford Heath.
Maybe its worth looking at how arc fault interrupters detect arcing?
On 3/30/2022 2:58 PM, whit3rd wrote:
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
... I'd think to log also any deviation fromHmmm... I hadn't thought of keeping much "context".
'normal' 120 (or 100) zero crossings per second. Maybe store a few dozen cycles before and after an 'event', gives you an idea of the transient. Motor
starts without zero-voltage-switching have dimmed my lights and
several times rebooted a Linux box exactly when I hear the buzzsaw.
The FNET folks sample at ~1.5KHz (I don't recall the precision) and try to detect anomalies in the grid by coordinating observations from geographically dispersed measurement stations. I assume some of their algorithms could be applied to local "single observation" points.
On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whi...@gmail.com>
wrote:
On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:
I'd like to use a laptop for a control application in an unattended
location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like
laptops can't do that for some reason. I'd love to find one that does.
MacOS laptops can be scheduled for turn-on and/or off once a day, with
the 'energy saver' settings. UPS connection sometimes adds options, too.
I need a Windows machine. If power fails for a full day maybe, a
laptop will run out of battery power and shut down, but can't be set
up to restart when power comes back. At least none that I can find.
On Wed, 30 Mar 2022 07:22:43 GMT, Jan Panteltje
<pNaonStpealmtje@yahoo.com> wrote:
The power network over here switches, sometimes 2 times a day, between networks it seems.
This causes a short (usually less than a second) power dip.
UPS takes care of that as far as computers go.
Laptop has its on battery and will run much longer,
I'd like to use a laptop for a control application in an unattended
location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like >laptops can't do that for some reason. I'd love to find one that does.
On Wednesday, March 30, 2022 at 7:11:29 PM UTC-7, Don Y wrote:
On 3/30/2022 2:58 PM, whit3rd wrote:
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
... I'd think to log also any deviation fromHmmm... I hadn't thought of keeping much "context".
'normal' 120 (or 100) zero crossings per second. Maybe store a few dozen >>> cycles before and after an 'event', gives you an idea of the transient. Motor
starts without zero-voltage-switching have dimmed my lights and
several times rebooted a Linux box exactly when I hear the buzzsaw.
The FNET folks sample at ~1.5KHz (I don't recall the precision) and try to >> detect anomalies in the grid by coordinating observations from geographically
dispersed measurement stations. I assume some of their algorithms could be >> applied to local "single observation" points.
Finding someone else's algorithms would be a good idea;
I belatedly realize that a bit
of powerline signalling is done near zero crossings, and maybe timing peaks then
resetting the peak detector at zero crossings is a better way to go. A powerline
45 MHz Ethernet link wouldn't look benign.
On a sunny day (Wed, 30 Mar 2022 12:27:32 -0700) it happened John Larkin ><jlarkin@highland_atwork_technology.com> wrote in ><4eb94hd6nturau50ev7muckgefj21h6nh0@4ax.com>:
On Wed, 30 Mar 2022 07:22:43 GMT, Jan Panteltje
<pNaonStpealmtje@yahoo.com> wrote:
The power network over here switches, sometimes 2 times a day, between networks it seems.
This causes a short (usually less than a second) power dip.
UPS takes care of that as far as computers go.
Laptop has its on battery and will run much longer,
I'd like to use a laptop for a control application in an unattended >>location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like >>laptops can't do that for some reason. I'd love to find one that does.
Is that not mainly a BIOS config?
On Thu, 31 Mar 2022 05:40:56 GMT, Jan Panteltje
<pNaonStpealmtje@yahoo.com> wrote:
On a sunny day (Wed, 30 Mar 2022 12:27:32 -0700) it happened John Larkin >><jlarkin@highland_atwork_technology.com> wrote in >><4eb94hd6nturau50ev7muckgefj21h6nh0@4ax.com>:
On Wed, 30 Mar 2022 07:22:43 GMT, Jan Panteltje >>><pNaonStpealmtje@yahoo.com> wrote:
The power network over here switches, sometimes 2 times a day, between networks it seems.
This causes a short (usually less than a second) power dip.
UPS takes care of that as far as computers go.
Laptop has its on battery and will run much longer,
I'd like to use a laptop for a control application in an unattended >>>location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like >>>laptops can't do that for some reason. I'd love to find one that does.
Is that not mainly a BIOS config?
Yes. Some big PCs have the powerup boot option in their BIOS, some
don't. I've not found a laptop that does.
On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whit3rd@gmail.com>
wrote:
On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:
I'd like to use a laptop for a control application in an unattended
location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like
laptops can't do that for some reason. I'd love to find one that does.
MacOS laptops can be scheduled for turn-on and/or off once a day, with
the 'energy saver' settings. UPS connection sometimes adds options, too.
I need a Windows machine. If power fails for a full day maybe, a
laptop will run out of battery power and shut down, but can't be set
up to restart when power comes back. At least none that I can find.
Strange.
Maybe some laptops can be set up to deep-sleep when batteries get low,
but wake up when power comes back. If one could ride out a few days
that way on remaining battery power, it would be OK.
John Larkin wrote:
On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whi...@gmail.com>
wrote:
On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:
I'd like to use a laptop for a control application in an unattended
location, instead of a big PC and a UPS. But a PC bios can usually be
set up to restart the PC after a hard power failure, and it seems like >>> laptops can't do that for some reason. I'd love to find one that does.
MacOS laptops can be scheduled for turn-on and/or off once a day, with
the 'energy saver' settings. UPS connection sometimes adds options, too.
I need a Windows machine. If power fails for a full day maybe, a
laptop will run out of battery power and shut down, but can't be set
up to restart when power comes back. At least none that I can find.
Strange.
Maybe some laptops can be set up to deep-sleep when batteries get low,
but wake up when power comes back. If one could ride out a few days
that way on remaining battery power, it would be OK.
IIRC a lot of them have wake-on-LAN in the BIOS, so you might be able to apply some router hackery to the problem. (I'm a devoted user of legacy
BIOS, so I don't know a lot about UEFI things.)
On Thursday, 31 March 2022 at 18:18:44 UTC+1, Phil Hobbs wrote:
John Larkin wrote:
On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whi...@gmail.com>IIRC a lot of them have wake-on-LAN in the BIOS, so you might be able to
wrote:
On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:I need a Windows machine. If power fails for a full day maybe, a
I'd like to use a laptop for a control application in an unattendedMacOS laptops can be scheduled for turn-on and/or off once a day, with >>>> the 'energy saver' settings. UPS connection sometimes adds options, too. >>>
location, instead of a big PC and a UPS. But a PC bios can usually be >>>>> set up to restart the PC after a hard power failure, and it seems like >>>>> laptops can't do that for some reason. I'd love to find one that does. >>>>
laptop will run out of battery power and shut down, but can't be set
up to restart when power comes back. At least none that I can find.
Strange.
Maybe some laptops can be set up to deep-sleep when batteries get low,
but wake up when power comes back. If one could ride out a few days
that way on remaining battery power, it would be OK.
apply some router hackery to the problem. (I'm a devoted user of legacy
BIOS, so I don't know a lot about UEFI things.)
If laptops don't do what is needed, there are a lot of mini-itx motherboards around that can be configured to auto restart and which have a single 12V dc input. If the disc drives don't use 12V, (SSDs and 2.5inch spinning drives don't)
then they will usually cope with quite a wide variation in input voltage as the 12V
input goes to a buck converter to generate 5V and then the other lower voltages
needed. Some industrial motherboards are even rated for inputs of up to about
19Vdc. This means that a 12V SLA battery would make a very efficient UPS
for such a motherboard. I have used ASRock IMB-150/151 motherboards in this way.
They are rated for input voltages of 9-19V, but I think the TI buck converter chip
they use is actually good for operation with up to 25V.
John
From time to time, we seem to experience a power "glitch", once aIf I understand correctly what you are trying to do, I'd suggest applying Nyquist criteria for waveform re-construction....
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
I assume this is some sort of switching transient that affects the
entire city (?) -- or, at least large portions of it.
(our services are below grade so not likely caused by something
physically interfering with the transmission lines)
I'm turning my attention to the design of the power systems for
my current project and figure it would be prudent to put some
line-monitoring capabilities into it (if only to let it anticipate
such problems and plan ahead).
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
[Of course, I have to anticipate what the power conditions are
likely to be in other parts of the market (US consumer and,
separately, commercial/industrial) and not just rely on my own
observations.]
I'm tempted to buy a line monitor just to see what they've done
(in terms of hardware interface; the signal processing software
won't be a problem). Recommendations? (again, two/three different
markets, as above)
On Tuesday, March 29, 2022 at 10:25:36 PM UTC-4, Don Y wrote:
From time to time, we seem to experience a power "glitch", once aIf I understand correctly what you are trying to do, I'd suggest applying Nyquist criteria for waveform re-construction....
day, at roughly the same time -- usually ~3AM. (but, not every day...
just "periods" when it manifests followed by periods where it is
completely absent).
It's not a problem, for the most part, as everything is on UPSs, here
(the microwave oven seems to complain the most as it isn't on a UPS
and its damn clock often resets -- I long for the day when appliances
have synchronized clocks or NO clocks!!!)
I assume this is some sort of switching transient that affects the
entire city (?) -- or, at least large portions of it.
(our services are below grade so not likely caused by something
physically interfering with the transmission lines)
I'm turning my attention to the design of the power systems for
my current project and figure it would be prudent to put some
line-monitoring capabilities into it (if only to let it anticipate
such problems and plan ahead).
So, the questions are:
- how often to sample (to be able to catch transient events)
- maximum peak likely to be encountered
[Of course, I have to anticipate what the power conditions are
likely to be in other parts of the market (US consumer and,
separately, commercial/industrial) and not just rely on my own
observations.]
I'm tempted to buy a line monitor just to see what they've done
(in terms of hardware interface; the signal processing software
won't be a problem). Recommendations? (again, two/three different
markets, as above)
https://en.wikipedia.org/wiki/Nyquist%E2%80%93Shannon_sampling_theorem understanding the highest frequency in the sampled signal is the key.