    From Don Y@21:1/5 to All on Tue Mar 29 19:25:13 2022
    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    (our services are below grade so not likely caused by something
    physically interfering with the transmission lines)

    I'm turning my attention to the design of the power systems for
    my current project and figure it would be prudent to put some
    line-monitoring capabilities into it (if only to let it anticipate
    such problems and plan ahead).

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    [Of course, I have to anticipate what the power conditions are
    likely to be in other parts of the market (US consumer and,
    separately, commercial/industrial) and not just rely on my own
    observations.]

    I'm tempted to buy a line monitor just to see what they've done
    (in terms of hardware interface; the signal processing software
    won't be a problem). Recommendations? (again, two/three different
    markets, as above)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Anthony William Sloman@21:1/5 to Don Y on Tue Mar 29 19:39:18 2022
    On Wednesday, March 30, 2022 at 1:25:36 PM UTC+11, Don Y wrote:
    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    That sounds like somebody switching a generating set on or off. It is a process that can generate transients.

    The famous Telsa grid scale battery in South Australia is reputed to be fast enough to cancel that sort of transient really fast (and half it's capacity is devoted to doing just that, which made it a really profitable investment.

    The other source of that kind of transient is lightning strikes in the wrong place. They are less predictable.

    <snip>

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Clifford Heath@21:1/5 to Don Y on Wed Mar 30 15:11:43 2022
    On 30/3/22 1:25 pm, Don Y wrote:
    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM.  (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    We had repeated trips of the whole-house RCD every few days for months.
    Always at 7:58AM. ALWAYS. I turned off everything in the house that
    could know the time of day, and they still happened. Eventually I became certain that it was something to do with the power supply, and started harassing our provider.

    They kept fobbing me off, saying I should replace the RCD - which at the
    time was brand-new, after a renovation where we got a new powerboard,
    and I told them that and insisted.

    Eventually they admitted that 7:58AM is when they switch in some large
    PFC capacitors in preparation for inductive industrial loads coming
    alive. I told them that it was therefore their problem, and they
    arranged to send a couple of electricians around to fit a more tolerant
    RCD, at no cost to me.

    When the sparkies came, they said they had been doing *hundreds* like
    this. And that's just for the households who figured it out, and
    complained long and hard enough to wear down the power company.

    This was in 2000, before we started fitting RCD breakers on every circuit.

    Clifford Heath.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Arie de Muijnck@21:1/5 to Jeff Layman on Wed Mar 30 10:11:02 2022
    On 2022-03-30 09:18, Jeff Layman wrote:

    Just get a 'scope monitoring the line power supply. Point a video camera (preferably with continuous time display) at the screen and record a few minutes before and after 3am every day. You should be able to record the spike and the exact time it appears. Even a webcam on a laptop might do
    the job. The power supply company wouldn't be able to argue with that
    sort of evidence.

    3am seems a strange time for transients. Some sort of fairly regular maintenance work at the generation station or distribution switching, perhaps?


    Or better: use a low voltage transformer and a resistive attenuator,
    then capture the 1Vpp waveform on the LINE IN audio channel of a laptop. Capture and analyze using e.g. the free Audacity, it shows the waveform
    nicely. Much easier than trying to find a transient on a video (even
    when the scope did capture it - some scopes have a low acquisition frame
    rate and may miss a spike completely).

    Arie

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jan Panteltje@21:1/5 to blockedofcourse@foo.invalid on Wed Mar 30 07:22:43 2022
    On a sunny day (Tue, 29 Mar 2022 19:25:13 -0700) it happened Don Y <blockedofcourse@foo.invalid> wrote in <t20f2p$ob9$1@dont-email.me>:

    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    (our services are below grade so not likely caused by something
    physically interfering with the transmission lines)

    I'm turning my attention to the design of the power systems for
    my current project and figure it would be prudent to put some
    line-monitoring capabilities into it (if only to let it anticipate
    such problems and plan ahead).

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    [Of course, I have to anticipate what the power conditions are
    likely to be in other parts of the market (US consumer and,
    separately, commercial/industrial) and not just rely on my own
    observations.]

    I'm tempted to buy a line monitor just to see what they've done
    (in terms of hardware interface; the signal processing software
    won't be a problem). Recommendations? (again, two/three different
    markets, as above)

    The power network over here switches, sometimes 2 times a day, between networks it seems.
    This causes a short (usually less than a second) power dip.
    UPS takes care of that as far as computers go.
    Laptop has its on battery and will run much longer,
    For longer power failures (will keep watching satellite, radio, ham radio, etc) I have now a 250 AH 12 V lifepo4 battery and a 2 kW 12V to 230V pure sinewave converter.
    So if the UPS starts screaming when power goes for a longer time,
    then it takes a few minutes to switch the big stuff to that setup manually. Sure, the clock in the microwave will reset,,,,
    Happened a few weeks back, 2 hours no power, neighbor came to ask 'Have you no power too?'
    Well, yes and no, I was just switching to the big battery.
    Talk about clocks, last Sunday we went to summer time, had to adjust 13 clocks here
    Sure hope they get rid of that shit twice a year

    The lifepo4 can easily power a microwave or cooking plate, or the TV for a whole evening..

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeff Layman@21:1/5 to Don Y on Wed Mar 30 08:18:12 2022
    On 30/03/2022 03:25, Don Y wrote:
    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    (our services are below grade so not likely caused by something
    physically interfering with the transmission lines)

    I'm turning my attention to the design of the power systems for
    my current project and figure it would be prudent to put some
    line-monitoring capabilities into it (if only to let it anticipate
    such problems and plan ahead).

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    [Of course, I have to anticipate what the power conditions are
    likely to be in other parts of the market (US consumer and,
    separately, commercial/industrial) and not just rely on my own
    observations.]

    I'm tempted to buy a line monitor just to see what they've done
    (in terms of hardware interface; the signal processing software
    won't be a problem). Recommendations? (again, two/three different
    markets, as above)

    Just get a 'scope monitoring the line power supply. Point a video camera (preferably with continuous time display) at the screen and record a few minutes before and after 3am every day. You should be able to record the
    spike and the exact time it appears. Even a webcam on a laptop might do
    the job. The power supply company wouldn't be able to argue with that
    sort of evidence.

    3am seems a strange time for transients. Some sort of fairly regular maintenance work at the generation station or distribution switching,
    perhaps?

    --

    Jeff

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Jeff Layman on Wed Mar 30 01:36:59 2022
    On 3/30/2022 12:18 AM, Jeff Layman wrote:
    On 30/03/2022 03:25, Don Y wrote:
    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    (our services are below grade so not likely caused by something
    physically interfering with the transmission lines)

    I'm turning my attention to the design of the power systems for
    my current project and figure it would be prudent to put some
    line-monitoring capabilities into it (if only to let it anticipate
    such problems and plan ahead).

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    [Of course, I have to anticipate what the power conditions are
    likely to be in other parts of the market (US consumer and,
    separately, commercial/industrial) and not just rely on my own
    observations.]

    I'm tempted to buy a line monitor just to see what they've done
    (in terms of hardware interface; the signal processing software
    won't be a problem). Recommendations? (again, two/three different
    markets, as above)

    Just get a 'scope monitoring the line power supply. Point a video camera (preferably with continuous time display) at the screen and record a few minutes before and after 3am every day. You should be able to record the spike
    and the exact time it appears. Even a webcam on a laptop might do the job. The
    power supply company wouldn't be able to argue with that sort of evidence.

    I'm not particularly concerned with *my* experience:

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    Rather, I'm concerned with adding that monitoring capability to my
    product so *it* can learn/know what the "local" power conditions happen
    to be (it runs 24/7/365). This would help it decide how to adjust the
    load and schedule processes in anticipation of (or after detection of)
    outages.

    For example, *real* outages, here, have been very infrequent. And, have
    have always been the result of equipment outages: cable segment failures, blown fuses in the neighborhood distribution station, etc. As these are relatively small events, from the perspective of the utility company, (unlike
    a storm knocking out power to a large portion of a town) they can be
    addressed with a small crew dispatched in short order. In each case, our outage has typically been less than ~6 hours (before they've rerouted power from "the other end" of the feed).

    By contrast, when I lived in the midwest, we had outages pretty regularly
    (6 or more each year) and they persisted for longer periods.

    So, siting my device *here* it could opt to maintain power for a larger
    portion of its componentry (it can selectively shed load) for a longer
    period of time and still hope to have spare backup capacity. In the
    midwest, it would have had to learn to impose deeper cuts as it expected
    longer outages.

    It also lets the size of the (battery) backup be an independent parameter
    at the discretion of the owner instead of an implicit requirement of the design. A deployment with a bigger load looks like a nominal deployment
    with a smaller backup, etc.

    [e.g., I have a ~2200W load that I can keep fully operational for ~2hrs. Someone else might not want to make that investment -- or might have
    a BIGGER load -- so the system needs to know how to make tradeoffs in scheduling its load]

    Finally, being able to guesstimate the likelihood of an outage, based on
    past observations. For example, if power fails, returns and then fails,
    again, you'd be slow to reinstall load hoping instead, to let the power
    supply divert power to RE-charging instead of the load (which you expect
    to likely need to *shed*, again, RSN... when the followup outage strikes)

    [This has been the pattern, here, with power coming back on-line. The
    crews will initially diagnose the problem, restore power -- and have
    the problem manifest, again, in short order ("Hey, Bill, the short is
    still there...")]

    I'm hoping that by being able to *look* at the mains as they are powering
    the system, that it might be able to make some deductions about the
    possible cause (and duration) of the outage. Instead of being "surprised"
    by each new event!

    3am seems a strange time for transients. Some sort of fairly regular maintenance work at the generation station or distribution switching, perhaps?

    Dunno. As I can't tell how widespread the problem is (it just this neighborhood? this side of town? etc.) or the system elements that
    lie between me and the "problem", I can't guess as to its cause.
    Is it something related to some other "nearby" power consumer and
    not the supplier? <shrug>

    The UPSs all claim it to be "excessive rate of change" (or something to
    that effect... not "dropped cycle" or "low line" or...).

    In parts of town with overhead distribution (which likely includes the
    high tension feeding us... somewhere), I can see large "switches"
    (but no idea as to how -- or why -- they are actuated/opened)

    Again, the cause is likely out of my control (unless a local fault).
    I just want to be able to observe it in more detail than "gee, the
    lights flickered" or "ooops! power is out!"

    Hence the question as to what the appropriate capabilities of that
    data acquisition (sub)system...

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Mike Monett@21:1/5 to Arie de Muijnck on Wed Mar 30 11:09:08 2022
    Arie de Muijnck <eternal.september@ademu.com> wrote:

    On 2022-03-30 09:18, Jeff Layman wrote:

    Just get a 'scope monitoring the line power supply. Point a video camera
    (preferably with continuous time display) at the screen and record a few
    minutes before and after 3am every day. You should be able to record the
    spike and the exact time it appears. Even a webcam on a laptop might do
    the job. The power supply company wouldn't be able to argue with that
    sort of evidence.

    3am seems a strange time for transients. Some sort of fairly regular
    maintenance work at the generation station or distribution switching,
    perhaps?


    Or better: use a low voltage transformer and a resistive attenuator,
    then capture the 1Vpp waveform on the LINE IN audio channel of a laptop. Capture and analyze using e.g. the free Audacity, it shows the waveform nicely. Much easier than trying to find a transient on a video (even
    when the scope did capture it - some scopes have a low acquisition frame
    rate and may miss a spike completely).

    Arie

    A transformer will have poor high frequency response and will filter out
    sharp spikes. Better to use a 100:1 capacitive/resistive divider across the
    AC line voltage. Verify the LINE IN audio channel is 600 ohms, then add a
    600k across the top capacitor.

    The neutral doesn't have to connect to the chassis of the computer. If you
    do, it will likely blow any GFI breaker that is on the ac line. Use GND for
    the return.


    --
    MRM

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Walliker@21:1/5 to Mike Monett on Wed Mar 30 04:41:32 2022
    On Wednesday, 30 March 2022 at 12:09:14 UTC+1, Mike Monett wrote:
    Arie de Muijnck <eternal....@ademu.com> wrote:

    On 2022-03-30 09:18, Jeff Layman wrote:

    Just get a 'scope monitoring the line power supply. Point a video camera >> (preferably with continuous time display) at the screen and record a few >> minutes before and after 3am every day. You should be able to record the >> spike and the exact time it appears. Even a webcam on a laptop might do
    the job. The power supply company wouldn't be able to argue with that
    sort of evidence.

    3am seems a strange time for transients. Some sort of fairly regular
    maintenance work at the generation station or distribution switching,
    perhaps?


    Or better: use a low voltage transformer and a resistive attenuator,
    then capture the 1Vpp waveform on the LINE IN audio channel of a laptop. Capture and analyze using e.g. the free Audacity, it shows the waveform nicely. Much easier than trying to find a transient on a video (even
    when the scope did capture it - some scopes have a low acquisition frame rate and may miss a spike completely).

    Arie
    A transformer will have poor high frequency response and will filter out sharp spikes. Better to use a 100:1 capacitive/resistive divider across the AC line voltage. Verify the LINE IN audio channel is 600 ohms, then add a 600k across the top capacitor.

    The neutral doesn't have to connect to the chassis of the computer. If you do, it will likely blow any GFI breaker that is on the ac line. Use GND for the return.

    But are sharp spikes likely to be a problem? Any product which has been through regulatory testing will have demonstrated a good immunity to
    large short spikes, so it is much more likely that dropouts will cause problems.
    A small transformer will respond to frequencies of many kHz, so that should
    be enough. What will prevent it from measuring large spikes is core
    saturation but there are several ways of minimising the effects of this
    that have been discussed here in the past.
    Most products, especially those with switched mode power supplies,
    should survive dropouts of 10ms or less without any problems
    due to energy storage in their input capacitors.

    John

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to John Walliker on Wed Mar 30 05:12:24 2022
    On 3/30/2022 4:41 AM, John Walliker wrote:
    On Wednesday, 30 March 2022 at 12:09:14 UTC+1, Mike Monett wrote:
    Arie de Muijnck <eternal....@ademu.com> wrote:

    On 2022-03-30 09:18, Jeff Layman wrote:

    Just get a 'scope monitoring the line power supply. Point a video camera >>>> (preferably with continuous time display) at the screen and record a few >>>> minutes before and after 3am every day. You should be able to record the >>>> spike and the exact time it appears. Even a webcam on a laptop might do >>>> the job. The power supply company wouldn't be able to argue with that
    sort of evidence.

    3am seems a strange time for transients. Some sort of fairly regular
    maintenance work at the generation station or distribution switching,
    perhaps?


    Or better: use a low voltage transformer and a resistive attenuator,
    then capture the 1Vpp waveform on the LINE IN audio channel of a laptop. >>> Capture and analyze using e.g. the free Audacity, it shows the waveform
    nicely. Much easier than trying to find a transient on a video (even
    when the scope did capture it - some scopes have a low acquisition frame >>> rate and may miss a spike completely).

    Arie
    A transformer will have poor high frequency response and will filter out
    sharp spikes. Better to use a 100:1 capacitive/resistive divider across the >> AC line voltage. Verify the LINE IN audio channel is 600 ohms, then add a
    600k across the top capacitor.

    The neutral doesn't have to connect to the chassis of the computer. If you >> do, it will likely blow any GFI breaker that is on the ac line. Use GND for >> the return.

    But are sharp spikes likely to be a problem? Any product which has been through regulatory testing will have demonstrated a good immunity to
    large short spikes, so it is much more likely that dropouts will cause problems.

    You've missed the point of (my!) post. The goal isn't to "protect" the
    device -- OBSERVING the line won't do anything to make the device more resilient!

    Rather, the goal is to try to understand the nature of the disturbance
    in light of other, "previously recorded (quantified)" disturbances and
    use that to predict what is likely to happen with the mains, "soon".

    E.g., when our cable segments fail (each transformer is daisy-chained
    to the next transformer down the line -- unlike "taps" on an overhead distribution line), the center/current carrying conductor (it's a coax)
    shorts to the "shield" (neutral/ground). As such, you would expect to
    "see" this arcing event instead of a "clean" open.

    You can imagine that power won't be coming back anytime soon in the
    event of such an observation.

    A drunk slamming into a pole (overhead supply) would likely exhibit
    a different sort of "failure event".

    A brownout, still different.

    Etc. Unless you can claim that those "details" carry no information,
    then one would want to preserve as much data as possible.

    [I can detect an outage just by counting 60Hz cycles and "timing out"
    in ~20ms; doesn't tell me anything other than "power is out!"]

    I'm not limited to just observations of the mains but can also factor in *other* observations (e.g., it is summer and ACbrrr loading, on the network,
    is high; or, it is winter and an ice-coated branch may have taken out
    an overhead line)

    A small transformer will respond to frequencies of many kHz, so that should be enough. What will prevent it from measuring large spikes is core saturation but there are several ways of minimising the effects of this
    that have been discussed here in the past.
    Most products, especially those with switched mode power supplies,
    should survive dropouts of 10ms or less without any problems
    due to energy storage in their input capacitors.

    John


    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Walliker@21:1/5 to Don Y on Wed Mar 30 06:34:04 2022
    On Wednesday, 30 March 2022 at 13:12:48 UTC+1, Don Y wrote:

    You've missed the point of (my!) post. The goal isn't to "protect" the
    device -- OBSERVING the line won't do anything to make the device more resilient!

    OK. I can see why measuring disturbances that won't affect your
    devices could be useful. The question then becomes one of how
    much measurement bandwidth and resolution is necessary to get
    this unknown information and how best to acquire it and process it.
    As you don't know what you are looking for about the only
    bandwidth constraint is going to be the bandwidth of the power
    transmission system subject to avoiding frequencies high enough
    to have long-wave broadcast transmissions. That suggests an
    upper frequency limit of maybe tens of kHz. Of course, arcing in
    nearby wiring could have much higher frequency components.
    Maybe its worth looking at how arc fault interrupters detect arcing?

    John

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Doe@21:1/5 to Don Y on Wed Mar 30 13:34:55 2022
    Don Y wrote:

    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    For 10+ years, I have been using a Tripp Lite LC 1200 voltage regulator
    instead of a UPS, that's overkill for my PC and peripherals but it probably increases the protection against occasional dropouts. Seems to work great. Other stuff blinks, but not my PC. And if it ever does turn off, not in at least a year, it stays off instead of blinking back on.

    It has proved to be better than messing with a battery.
    If it clicks, I backup stuff. Never know!

    It also helps monitor room/household voltage since it includes over/under voltage LEDs.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bob Engelhardt@21:1/5 to Clifford Heath on Wed Mar 30 11:33:35 2022
    On 3/30/2022 12:11 AM, Clifford Heath wrote:
    We had repeated trips of the whole-house RCD every few days for months.
    ...

    RCD - residual-current device or ground fault circuit interrupter (GFCI)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to John Walliker on Wed Mar 30 11:16:04 2022
    On 3/30/2022 6:34 AM, John Walliker wrote:
    On Wednesday, 30 March 2022 at 13:12:48 UTC+1, Don Y wrote:

    You've missed the point of (my!) post. The goal isn't to "protect" the
    device -- OBSERVING the line won't do anything to make the device more
    resilient!

    OK. I can see why measuring disturbances that won't affect your
    devices could be useful. The question then becomes one of how
    much measurement bandwidth and resolution is necessary to get
    this unknown information and how best to acquire it and process it.

    There are a fair number of publications (research) that describe faults
    in the transmission network (because the utilities have an interest
    in minimizing these). How those are reflected *into* a "point of
    observation" that *I* would easily monitor is an issue. (telling
    me what's happening on the high-tension side of my local feed isn't
    the same thing as telling me what I will see "locally")

    As you don't know what you are looking for about the only
    bandwidth constraint is going to be the bandwidth of the power
    transmission system subject to avoiding frequencies high enough
    to have long-wave broadcast transmissions. That suggests an
    upper frequency limit of maybe tens of kHz.

    But, that ignores:

    Of course, arcing in
    nearby wiring could have much higher frequency components.

    ...as well as other failures, noise sources, etc. E.g., a fault
    in a large load that eventually takes out the local branch circuit
    can be just as "bad" for your source of power as a system-wide
    power failure.

    Tens of Hz is enough to (quickly) detect *outages*. Will tens of
    KHz be sufficient to differentiate between different line faults
    and transients? How much wire do you assume separates the
    observation from the fault?? <shrug>

    [And, we've not addressed the magnitude of the transients... 10X?
    log scale?]

    Maybe its worth looking at how arc fault interrupters detect arcing?

    That's a good idea. But, again, they are only looking for arcing and
    not the general case of "disturbances"/line quality. E.g., in an
    industrial setting, I'd expect the mains to be a lot dirtier than
    in a domestic setting. So, you'd have to "learn" when that "dirt"
    is significant and when it just has to be tolerated.

    And, they are obviously targeting "cheap" detection methods; I'm
    not so constrained.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Larkin@21:1/5 to pNaonStpealmtje@yahoo.com on Wed Mar 30 12:27:32 2022
    On Wed, 30 Mar 2022 07:22:43 GMT, Jan Panteltje
    <pNaonStpealmtje@yahoo.com> wrote:


    The power network over here switches, sometimes 2 times a day, between networks it seems.
    This causes a short (usually less than a second) power dip.
    UPS takes care of that as far as computers go.
    Laptop has its on battery and will run much longer,

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like
    laptops can't do that for some reason. I'd love to find one that does.

    --

    If a man will begin with certainties, he shall end with doubts,
    but if he will be content to begin with doubts he shall end in certainties. Francis Bacon

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From whit3rd@21:1/5 to Don Y on Wed Mar 30 14:58:12 2022
    On Tuesday, March 29, 2022 at 7:25:36 PM UTC-7, Don Y wrote:

    I'm turning my attention to the design of the power systems for
    my current project and figure it would be prudent to put some
    line-monitoring capabilities into it (if only to let it anticipate
    such problems and plan ahead).

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    It's relatively important to have an average-AC-voltage measure,
    because some wiring issues can be diagnosed that way; you'd want to
    sample rectified/filtered V at tenth second or so, but only log 'events', not keep all the data. There's a few percent variance allowable, of course.

    Load changes and loose connections or lightning strikes, or
    diurnal overvoltage because of xformer tap decisions could show up.
    Sites vary, but expect 2kV for miliseconds, in case of lightning.

    More important surges or loads will cause zero-cross timing shifts which
    tie into odd clunks from motors, so I'd think to log also any deviation from 'normal' 120 (or 100) zero crossings per second. Maybe store a few dozen cycles before and after an 'event', gives you an idea of the transient. Motor starts without zero-voltage-switching have dimmed my lights and
    several times rebooted a Linux box exactly when I hear the buzzsaw.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From whit3rd@21:1/5 to John Larkin on Wed Mar 30 16:08:04 2022
    On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like laptops can't do that for some reason. I'd love to find one that does.

    MacOS laptops can be scheduled for turn-on and/or off once a day, with
    the 'energy saver' settings. UPS connection sometimes adds options, too.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Larkin@21:1/5 to All on Wed Mar 30 16:27:00 2022
    On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whit3rd@gmail.com>
    wrote:

    On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like
    laptops can't do that for some reason. I'd love to find one that does.

    MacOS laptops can be scheduled for turn-on and/or off once a day, with
    the 'energy saver' settings. UPS connection sometimes adds options, too.

    I need a Windows machine. If power fails for a full day maybe, a
    laptop will run out of battery power and shut down, but can't be set
    up to restart when power comes back. At least none that I can find.

    Strange.

    Maybe some laptops can be set up to deep-sleep when batteries get low,
    but wake up when power comes back. If one could ride out a few days
    that way on remaining battery power, it would be OK.



    --

    If a man will begin with certainties, he shall end with doubts,
    but if he will be content to begin with doubts he shall end in certainties. Francis Bacon

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Wed Mar 30 19:11:03 2022
    On 3/30/2022 2:58 PM, whit3rd wrote:

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    It's relatively important to have an average-AC-voltage measure,
    because some wiring issues can be diagnosed that way; you'd want to
    sample rectified/filtered V at tenth second or so, but only log 'events', not keep all the data. There's a few percent variance allowable, of course.

    But those would be "perform once" types of calculations; the wiring
    isn't likely to change "dynamically".

    Load changes and loose connections or lightning strikes, or
    diurnal overvoltage because of xformer tap decisions could show up.
    Sites vary, but expect 2kV for miliseconds, in case of lightning.

    OK. I assume we're still speaking of consumer deployments...

    More important surges or loads will cause zero-cross timing shifts which
    tie into odd clunks from motors, so I'd think to log also any deviation from 'normal' 120 (or 100) zero crossings per second. Maybe store a few dozen cycles before and after an 'event', gives you an idea of the transient. Motor
    starts without zero-voltage-switching have dimmed my lights and
    several times rebooted a Linux box exactly when I hear the buzzsaw.

    Hmmm... I hadn't thought of keeping much "context".

    The FNET folks sample at ~1.5KHz (I don't recall the precision) and try to detect anomalies in the grid by coordinating observations from geographically dispersed measurement stations. I assume some of their algorithms could be applied to local "single observation" points.

    As long as the "disturbance/transient" doesn't affect (or predict!) power availability (as seen at the output of MY power supply), I'm likely not too concerned with it. I can carry most of my (distributed) loads over short durations, regardless of the investment a particular site may have made
    in "backup" capability.

    I'd have to be more concerned about sites that power individual nodes
    "locally" from PSUs that aren't as robust. I will know that this is
    happening (*has* happened) and can take some measures to prevent loss
    of functionality. E.g., don't dispatch processes to nodes that may
    not have reliable power at a particular site. Or, force the OS to
    checkpoint every process running on those nodes (which adds overhead).

    Ideally, I'd not want to take any prophylactic measures unless needed
    as they translate into "overhead"/waste.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From bud--@21:1/5 to Clifford Heath on Wed Mar 30 21:24:49 2022
    On 3/29/2022 10:11 PM, Clifford Heath wrote:
    On 30/3/22 1:25 pm, Don Y wrote:
     From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM.  (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    We had repeated trips of the whole-house RCD every few days for months. Always at 7:58AM. ALWAYS. I turned off everything in the house that
    could know the time of day, and they still happened. Eventually I became certain that it was something to do with the power supply, and started harassing our provider.

    They kept fobbing me off, saying I should replace the RCD - which at the
    time was brand-new, after a renovation where we got a new powerboard,
    and I told them that and insisted.

    Eventually they admitted that 7:58AM is when they switch in some large
    PFC capacitors in preparation for inductive industrial loads coming
    alive. I told them that it was therefore their problem, and they
    arranged to send a couple of electricians around to fit a more tolerant
    RCD, at no cost to me.

    When the sparkies came, they said they had been doing *hundreds* like
    this. And that's just for the households who figured it out, and
    complained long and hard enough to wear down the power company.

    This was in 2000, before we started fitting RCD breakers on every circuit.

    Clifford Heath.

    Switching of power factor caps is a known potential cause of significant surges. Would be interesting why that trips a RCD.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From bud--@21:1/5 to John Walliker on Wed Mar 30 21:34:59 2022
    On 3/30/2022 7:34 AM, John Walliker wrote:

    Maybe its worth looking at how arc fault interrupters detect arcing?


    Note that AFCIs only detect arcing downstream. They ignore 'normal' arcs
    like switch open/close.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From whit3rd@21:1/5 to Don Y on Wed Mar 30 20:58:05 2022
    On Wednesday, March 30, 2022 at 7:11:29 PM UTC-7, Don Y wrote:
    On 3/30/2022 2:58 PM, whit3rd wrote:

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    ... I'd think to log also any deviation from
    'normal' 120 (or 100) zero crossings per second. Maybe store a few dozen cycles before and after an 'event', gives you an idea of the transient. Motor
    starts without zero-voltage-switching have dimmed my lights and
    several times rebooted a Linux box exactly when I hear the buzzsaw.
    Hmmm... I hadn't thought of keeping much "context".

    The FNET folks sample at ~1.5KHz (I don't recall the precision) and try to detect anomalies in the grid by coordinating observations from geographically dispersed measurement stations. I assume some of their algorithms could be applied to local "single observation" points.

    Finding someone else's algorithms would be a good idea; I belatedly realize that a bit
    of powerline signalling is done near zero crossings, and maybe timing peaks then
    resetting the peak detector at zero crossings is a better way to go. A powerline
    45 MHz Ethernet link wouldn't look benign.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From whit3rd@21:1/5 to John Larkin on Wed Mar 30 20:59:03 2022
    On Wednesday, March 30, 2022 at 4:27:12 PM UTC-7, John Larkin wrote:
    On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whi...@gmail.com>
    wrote:
    On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like
    laptops can't do that for some reason. I'd love to find one that does.

    MacOS laptops can be scheduled for turn-on and/or off once a day, with
    the 'energy saver' settings. UPS connection sometimes adds options, too.

    I need a Windows machine. If power fails for a full day maybe, a
    laptop will run out of battery power and shut down, but can't be set
    up to restart when power comes back. At least none that I can find.

    So, load a Windows virtual machine into a MacBook. The energy manager "schedule" settings will still work; set it to sleep soonish if only battery is available.

    It's not 'when power comes back' that you set, but an internal time-of-day start
    time, and/or shutdown time. If power drops or not, it'll still start
    the next day, at the appointed time, on battery. The battery/line-power status
    would have to be checked by a script if you wanted any power-on event to make it reboot,
    and no script can startup or wake-from-sleep on condition of power inlet status.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jan Panteltje@21:1/5 to jlarkin@highland_atwork_technology. on Thu Mar 31 05:40:56 2022
    On a sunny day (Wed, 30 Mar 2022 12:27:32 -0700) it happened John Larkin <jlarkin@highland_atwork_technology.com> wrote in <4eb94hd6nturau50ev7muckgefj21h6nh0@4ax.com>:

    On Wed, 30 Mar 2022 07:22:43 GMT, Jan Panteltje
    <pNaonStpealmtje@yahoo.com> wrote:


    The power network over here switches, sometimes 2 times a day, between networks it seems.
    This causes a short (usually less than a second) power dip.
    UPS takes care of that as far as computers go.
    Laptop has its on battery and will run much longer,

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like >laptops can't do that for some reason. I'd love to find one that does.

    Is that not mainly a BIOS config?
    My laptop runs Linux, but I have specified a BIOS password, if you do not then it will boot normally AFAIK.
    Same for my other older small laptop, was even running as web server for years.

    Use a Raspberry?
    I now have 5 of those in use.
    Some just via SSH, no monitor no keyboard, like the one used as router,
    Lower power use too.
    There exist battery backup 'shields' for those.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Wed Mar 30 22:45:26 2022
    On 3/30/2022 8:58 PM, whit3rd wrote:
    On Wednesday, March 30, 2022 at 7:11:29 PM UTC-7, Don Y wrote:
    On 3/30/2022 2:58 PM, whit3rd wrote:

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    ... I'd think to log also any deviation from
    'normal' 120 (or 100) zero crossings per second. Maybe store a few dozen >>> cycles before and after an 'event', gives you an idea of the transient. Motor
    starts without zero-voltage-switching have dimmed my lights and
    several times rebooted a Linux box exactly when I hear the buzzsaw.
    Hmmm... I hadn't thought of keeping much "context".

    The FNET folks sample at ~1.5KHz (I don't recall the precision) and try to >> detect anomalies in the grid by coordinating observations from geographically
    dispersed measurement stations. I assume some of their algorithms could be >> applied to local "single observation" points.

    Finding someone else's algorithms would be a good idea;

    There are three problems, there:
    - they are looking for something different than what I seek
    - they are academics (with notoriously crappy implementations)
    - their algorithms may not be completely specified in the literature
    (and CURRENT source code may not be publicly available from which to
    extract those "latest details/discoveries")

    I belatedly realize that a bit
    of powerline signalling is done near zero crossings, and maybe timing peaks then
    resetting the peak detector at zero crossings is a better way to go. A powerline
    45 MHz Ethernet link wouldn't look benign.

    I was thinking do a DFT on the samples and extract the fundamental. From
    that, go back and "pick" whatever points you want on the specific waveforms
    for "actual observations".

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From jlarkin@highlandsniptechnology.com@21:1/5 to pNaonStpealmtje@yahoo.com on Thu Mar 31 07:10:37 2022
    On Thu, 31 Mar 2022 05:40:56 GMT, Jan Panteltje
    <pNaonStpealmtje@yahoo.com> wrote:

    On a sunny day (Wed, 30 Mar 2022 12:27:32 -0700) it happened John Larkin ><jlarkin@highland_atwork_technology.com> wrote in ><4eb94hd6nturau50ev7muckgefj21h6nh0@4ax.com>:

    On Wed, 30 Mar 2022 07:22:43 GMT, Jan Panteltje
    <pNaonStpealmtje@yahoo.com> wrote:


    The power network over here switches, sometimes 2 times a day, between networks it seems.
    This causes a short (usually less than a second) power dip.
    UPS takes care of that as far as computers go.
    Laptop has its on battery and will run much longer,

    I'd like to use a laptop for a control application in an unattended >>location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like >>laptops can't do that for some reason. I'd love to find one that does.

    Is that not mainly a BIOS config?

    Yes. Some big PCs have the powerup boot option in their BIOS, some
    don't. I've not found a laptop that does.



    --

    I yam what I yam - Popeye

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jan Panteltje@21:1/5 to jlarkin@highlandsniptechnology.com on Thu Mar 31 14:37:52 2022
    On a sunny day (Thu, 31 Mar 2022 07:10:37 -0700) it happened jlarkin@highlandsniptechnology.com wrote in <afdb4h5f4bd3dej65ohb7ksrsug0skpifo@4ax.com>:

    On Thu, 31 Mar 2022 05:40:56 GMT, Jan Panteltje
    <pNaonStpealmtje@yahoo.com> wrote:

    On a sunny day (Wed, 30 Mar 2022 12:27:32 -0700) it happened John Larkin >><jlarkin@highland_atwork_technology.com> wrote in >><4eb94hd6nturau50ev7muckgefj21h6nh0@4ax.com>:

    On Wed, 30 Mar 2022 07:22:43 GMT, Jan Panteltje >>><pNaonStpealmtje@yahoo.com> wrote:


    The power network over here switches, sometimes 2 times a day, between networks it seems.
    This causes a short (usually less than a second) power dip.
    UPS takes care of that as far as computers go.
    Laptop has its on battery and will run much longer,

    I'd like to use a laptop for a control application in an unattended >>>location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like >>>laptops can't do that for some reason. I'd love to find one that does.

    Is that not mainly a BIOS config?

    Yes. Some big PCs have the powerup boot option in their BIOS, some
    don't. I've not found a laptop that does.

    OK, I think when the laptop powers off by itself it is because the battery is empty
    it will need charging before it will boot again?
    I wrote some software 'xbat' that runs on my laptop that makes it beep very loud when battery is low
    http://panteltje.com/pub/xbat-0.5.tgz
    Linux C code for X of course.

    <quote from readme>
    xbat uses ACPI and gets its info from /proc/acpi/battery/BAT1/state, try:
    cat /proc/acpi/battery/BAT1/state

    xbat displays battery level and time left on a charge in X.
    The display is updated once per second.
    If 3 minutes or less time is left, a 100 ms 4 kHz warning beep sounds every second.
    The beep function requires siggen-2.3.10 to be installed,
    it also requires access to the audio device.
    <end quote>


    You could make it power the laptop down early too (say with 1 hour spare left)
    ~ # cat /proc/acpi/battery/BAT1/state
    present: yes
    capacity state: ok
    charging state: charged
    present rate: 0 mA
    remaining capacity: 4424 mAh
    present voltage: 16517 mV

    If all else fails then a bridge rectifier and series cap driving a relay could press the power button for a second when mains comes on.
    But modern laptops will run for hours with mains power down, so how long are your mains interruptions?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Phil Hobbs@21:1/5 to John Larkin on Thu Mar 31 13:18:34 2022
    John Larkin wrote:
    On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whit3rd@gmail.com>
    wrote:

    On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like
    laptops can't do that for some reason. I'd love to find one that does.

    MacOS laptops can be scheduled for turn-on and/or off once a day, with
    the 'energy saver' settings. UPS connection sometimes adds options, too.

    I need a Windows machine. If power fails for a full day maybe, a
    laptop will run out of battery power and shut down, but can't be set
    up to restart when power comes back. At least none that I can find.

    Strange.

    Maybe some laptops can be set up to deep-sleep when batteries get low,
    but wake up when power comes back. If one could ride out a few days
    that way on remaining battery power, it would be OK.




    IIRC a lot of them have wake-on-LAN in the BIOS, so you might be able to
    apply some router hackery to the problem. (I'm a devoted user of legacy
    BIOS, so I don't know a lot about UEFI things.)

    Cheers

    Phil Hobbs

    --
    Dr Philip C D Hobbs
    Principal Consultant
    ElectroOptical Innovations LLC / Hobbs ElectroOptics
    Optics, Electro-optics, Photonics, Analog Electronics
    Briarcliff Manor NY 10510

    http://electrooptical.net
    http://hobbs-eo.com

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Walliker@21:1/5 to Phil Hobbs on Thu Mar 31 11:00:07 2022
    On Thursday, 31 March 2022 at 18:18:44 UTC+1, Phil Hobbs wrote:
    John Larkin wrote:
    On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whi...@gmail.com>
    wrote:

    On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be
    set up to restart the PC after a hard power failure, and it seems like >>> laptops can't do that for some reason. I'd love to find one that does.

    MacOS laptops can be scheduled for turn-on and/or off once a day, with
    the 'energy saver' settings. UPS connection sometimes adds options, too.

    I need a Windows machine. If power fails for a full day maybe, a
    laptop will run out of battery power and shut down, but can't be set
    up to restart when power comes back. At least none that I can find.

    Strange.

    Maybe some laptops can be set up to deep-sleep when batteries get low,
    but wake up when power comes back. If one could ride out a few days
    that way on remaining battery power, it would be OK.



    IIRC a lot of them have wake-on-LAN in the BIOS, so you might be able to apply some router hackery to the problem. (I'm a devoted user of legacy
    BIOS, so I don't know a lot about UEFI things.)


    If laptops don't do what is needed, there are a lot of mini-itx motherboards around that can be configured to auto restart and which have a single 12V dc input. If the disc drives don't use 12V, (SSDs and 2.5inch spinning drives don't)
    then they will usually cope with quite a wide variation in input voltage as the 12V
    input goes to a buck converter to generate 5V and then the other lower voltages needed. Some industrial motherboards are even rated for inputs of up to about 19Vdc. This means that a 12V SLA battery would make a very efficient UPS
    for such a motherboard. I have used ASRock IMB-150/151 motherboards in this way.
    They are rated for input voltages of 9-19V, but I think the TI buck converter chip
    they use is actually good for operation with up to 25V.
    John

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Phil Hobbs@21:1/5 to John Walliker on Thu Mar 31 14:41:53 2022
    John Walliker wrote:
    On Thursday, 31 March 2022 at 18:18:44 UTC+1, Phil Hobbs wrote:
    John Larkin wrote:
    On Wed, 30 Mar 2022 16:08:04 -0700 (PDT), whit3rd <whi...@gmail.com>
    wrote:

    On Wednesday, March 30, 2022 at 12:27:44 PM UTC-7, John Larkin wrote:

    I'd like to use a laptop for a control application in an unattended
    location, instead of a big PC and a UPS. But a PC bios can usually be >>>>> set up to restart the PC after a hard power failure, and it seems like >>>>> laptops can't do that for some reason. I'd love to find one that does. >>>>
    MacOS laptops can be scheduled for turn-on and/or off once a day, with >>>> the 'energy saver' settings. UPS connection sometimes adds options, too. >>>
    I need a Windows machine. If power fails for a full day maybe, a
    laptop will run out of battery power and shut down, but can't be set
    up to restart when power comes back. At least none that I can find.

    Strange.

    Maybe some laptops can be set up to deep-sleep when batteries get low,
    but wake up when power comes back. If one could ride out a few days
    that way on remaining battery power, it would be OK.



    IIRC a lot of them have wake-on-LAN in the BIOS, so you might be able to
    apply some router hackery to the problem. (I'm a devoted user of legacy
    BIOS, so I don't know a lot about UEFI things.)


    If laptops don't do what is needed, there are a lot of mini-itx motherboards around that can be configured to auto restart and which have a single 12V dc input. If the disc drives don't use 12V, (SSDs and 2.5inch spinning drives don't)
    then they will usually cope with quite a wide variation in input voltage as the 12V
    input goes to a buck converter to generate 5V and then the other lower voltages
    needed. Some industrial motherboards are even rated for inputs of up to about
    19Vdc. This means that a 12V SLA battery would make a very efficient UPS
    for such a motherboard. I have used ASRock IMB-150/151 motherboards in this way.
    They are rated for input voltages of 9-19V, but I think the TI buck converter chip
    they use is actually good for operation with up to 25V.
    John


    It's pretty attractive to use old laptops for this sort of job--I use
    them as NASes, for instance. You get them from eBay for $100 or so,
    replace the HDD, and you're done. (I run Linux on them, so there are
    no huge issues with reinstalling the OS.)

    Cheers

    Phil Hobbs

    --
    Dr Philip C D Hobbs
    Principal Consultant
    ElectroOptical Innovations LLC / Hobbs ElectroOptics
    Optics, Electro-optics, Photonics, Analog Electronics
    Briarcliff Manor NY 10510

    http://electrooptical.net
    http://hobbs-eo.com

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Three Jeeps@21:1/5 to Don Y on Thu Mar 31 17:10:14 2022
    On Tuesday, March 29, 2022 at 10:25:36 PM UTC-4, Don Y wrote:
    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    (our services are below grade so not likely caused by something
    physically interfering with the transmission lines)

    I'm turning my attention to the design of the power systems for
    my current project and figure it would be prudent to put some
    line-monitoring capabilities into it (if only to let it anticipate
    such problems and plan ahead).

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    [Of course, I have to anticipate what the power conditions are
    likely to be in other parts of the market (US consumer and,
    separately, commercial/industrial) and not just rely on my own
    observations.]

    I'm tempted to buy a line monitor just to see what they've done
    (in terms of hardware interface; the signal processing software
    won't be a problem). Recommendations? (again, two/three different
    markets, as above)
    If I understand correctly what you are trying to do, I'd suggest applying Nyquist criteria for waveform re-construction....
    https://en.wikipedia.org/wiki/Nyquist%E2%80%93Shannon_sampling_theorem understanding the highest frequency in the sampled signal is the key.
    J

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Three Jeeps on Thu Mar 31 17:52:50 2022
    On 3/31/2022 5:10 PM, Three Jeeps wrote:
    On Tuesday, March 29, 2022 at 10:25:36 PM UTC-4, Don Y wrote:
    From time to time, we seem to experience a power "glitch", once a
    day, at roughly the same time -- usually ~3AM. (but, not every day...
    just "periods" when it manifests followed by periods where it is
    completely absent).

    It's not a problem, for the most part, as everything is on UPSs, here
    (the microwave oven seems to complain the most as it isn't on a UPS
    and its damn clock often resets -- I long for the day when appliances
    have synchronized clocks or NO clocks!!!)

    I assume this is some sort of switching transient that affects the
    entire city (?) -- or, at least large portions of it.

    (our services are below grade so not likely caused by something
    physically interfering with the transmission lines)

    I'm turning my attention to the design of the power systems for
    my current project and figure it would be prudent to put some
    line-monitoring capabilities into it (if only to let it anticipate
    such problems and plan ahead).

    So, the questions are:
    - how often to sample (to be able to catch transient events)
    - maximum peak likely to be encountered

    [Of course, I have to anticipate what the power conditions are
    likely to be in other parts of the market (US consumer and,
    separately, commercial/industrial) and not just rely on my own
    observations.]

    I'm tempted to buy a line monitor just to see what they've done
    (in terms of hardware interface; the signal processing software
    won't be a problem). Recommendations? (again, two/three different
    markets, as above)
    If I understand correctly what you are trying to do, I'd suggest applying Nyquist criteria for waveform re-construction....
    https://en.wikipedia.org/wiki/Nyquist%E2%80%93Shannon_sampling_theorem understanding the highest frequency in the sampled signal is the key.

    That's the essence of the question. *Knowing* what the line can look like
    and *which* aspects of the waveform carry information pertinent to making these sorts of decisions. Capturing the "entire" waveform may not be essential if
    it doesn't "add value" to any deductive process (e.g., simply noting the magnitude of the highest peak (captured asynchronously) might reveal more information for less effort than trying to sample it "continuously".

    --- SoupGate-Win32 v1.05