• Testing circuit breakers with a welder

    From bob prohaska@21:1/5 to All on Mon Jun 5 01:50:50 2023
    I've been given a collection of residential service panel breakers
    and would like to check them to see if they trip correctly. They
    were in use before I got them, so they certainly close correctly,
    but it's unknown if they trip correctly.

    As it happens, I have an AC arc welder which can be set between
    about 20 and 200 amps, with an open circuit voltage of about 80 V.

    Anybody ever tried this? Does it seem an unrealistically harsh
    test?

    Thanks for reading,

    bob prohaska

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Phil Allison@21:1/5 to bob prohaska on Sun Jun 4 23:01:59 2023
    bob prohaska wrote:
    --------------------------------
    I've been given a collection of residential service panel breakers
    and would like to check them to see if they trip correctly. They
    were in use before I got them, so they certainly close correctly,
    but it's unknown if they trip correctly.

    As it happens, I have an AC arc welder which can be set between
    about 20 and 200 amps, with an open circuit voltage of about 80 V.

    Anybody ever tried this? Does it seem an unrealistically harsh
    test?


    ** Nope - such breakers are rated to open instantly with fault currents in the thousands of amps.
    At rated current they will take a while, maybe 20 minutes, since the trip mechanism is thermal rather than magnetic.
    FYI:
    A neat, low cost test is to connect an electro cap of about 100uF / 400V with a 6 amp series diode across the output.
    The peak surge should trip the breaker pronto.


    ...... Phil

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Jones@21:1/5 to bob prohaska on Mon Jun 5 21:17:29 2023
    On 5/06/2023 11:50 am, bob prohaska wrote:
    I've been given a collection of residential service panel breakers
    and would like to check them to see if they trip correctly. They
    were in use before I got them, so they certainly close correctly,
    but it's unknown if they trip correctly.

    As it happens, I have an AC arc welder which can be set between
    about 20 and 200 amps, with an open circuit voltage of about 80 V.

    Anybody ever tried this? Does it seem an unrealistically harsh
    test?

    Thanks for reading,

    bob prohaska




    At least traditional welders (line frequency not switched mode) look
    very inductive, and are designed to sustain an arc. Whilst I would hope
    that the circuit breakers are able to break the arc, it is a much
    harsher test than with a resistive load. If the welder is able to
    sustain an arc after the circuit breaker opens, then this will destroy
    the breaker.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From bob prohaska@21:1/5 to Chris Jones on Mon Jun 5 21:31:38 2023
    Chris Jones <lugnut808@spam.yahoo.com> wrote:

    At least traditional welders (line frequency not switched mode) look
    very inductive, and are designed to sustain an arc. Whilst I would hope
    that the circuit breakers are able to break the arc, it is a much
    harsher test than with a resistive load. If the welder is able to
    sustain an arc after the circuit breaker opens, then this will destroy
    the breaker.


    I agree it's a harsh test, but the breakers were free. I'd rather not
    use them without some evidence they work.

    After posting my question I again searched the web and found one set
    of YouTube videos demonstrating overcurrent testing of breakers and
    connectors. One suggests that at least some circuit breakers can stop
    an arc welder without self-destruction. It's at https://www.youtube.com/watch?v=fhXtXVBvSfg

    Thanks for writing!

    bob prohaska

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From legg@21:1/5 to bp@www.zefox.net on Tue Jun 6 10:31:26 2023
    On Mon, 5 Jun 2023 21:31:38 -0000 (UTC), bob prohaska
    <bp@www.zefox.net> wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:

    At least traditional welders (line frequency not switched mode) look
    very inductive, and are designed to sustain an arc. Whilst I would hope
    that the circuit breakers are able to break the arc, it is a much
    harsher test than with a resistive load. If the welder is able to
    sustain an arc after the circuit breaker opens, then this will destroy
    the breaker.


    I agree it's a harsh test, but the breakers were free. I'd rather not
    use them without some evidence they work.

    After posting my question I again searched the web and found one set
    of YouTube videos demonstrating overcurrent testing of breakers and >connectors. One suggests that at least some circuit breakers can stop
    an arc welder without self-destruction. It's at >https://www.youtube.com/watch?v=fhXtXVBvSfg

    Thanks for writing!

    bob prohaska

    DC ratings of standard breakers seldom exceed 40V, due to arcing.
    AC arcs are interrupted by line voltage reversal, preventing
    damage. But even these have a limited guaranteed operation count.

    RL

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Phil Allison@21:1/5 to legg on Tue Jun 6 20:12:24 2023
    legg wrote:
    -----------------

    DC ratings of standard breakers seldom exceed 40V, due to arcing.


    ** However most *mains rated* breakers employ magnetic or physical barrier arc quenching whenever contacts open.

    AC arcs are interrupted by line voltage reversal,

    ** Strange how AC arc welders work so well then.

    FYI:

    Relays and most switches suffer from limited DC switching capacity, usually limited to 24 or 30 volts at rated currents.
    Any more results in a permanent arc bridging the contacts, followed by complete self destruction.
    Relays used as "speaker protection" generally do not.


    ...... Phil

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Phil Allison@21:1/5 to legg on Wed Jun 7 06:07:59 2023
    legg wrote:

    ------------------

    legg wrote:
    -----------------

    DC ratings of standard breakers seldom exceed 40V, due to arcing.


    ** However most *mains rated* breakers employ magnetic or physical barrier arc quenching whenever contacts open.

    Not so much quenching, as sacrificial absorption....


    ** Hello to the smug troll calling itself " legg" .

    The term "quenching" here clearly refers to physically breaking an arc by extending it.
    Rest of your pedantic, tedious, self aggrandizing, spew inducing BULLSHIT snipped.
    Have a really rotten day.

    .... Phil

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From legg@21:1/5 to pallison49@gmail.com on Wed Jun 7 08:40:58 2023
    On Tue, 6 Jun 2023 20:12:24 -0700 (PDT), Phil Allison
    <pallison49@gmail.com> wrote:

    legg wrote:
    -----------------

    DC ratings of standard breakers seldom exceed 40V, due to arcing.


    ** However most *mains rated* breakers employ magnetic or physical barrier arc quenching whenever contacts open.

    Not so much quenching, as sacrificial absorption, in locations that
    are not relied on for physical working contact area. Life-limited,
    bulky and $$$.


    AC arcs are interrupted by line voltage reversal,

    ** Strange how AC arc welders work so well then.

    Wadabaudit? Nobody's saying that AC won't arc.

    They don't work so well, because an arc has to be re-established
    on every cyclic reversal. Breaking the AC arc is 'easy'. Maintaining
    one is hard. AC arc welding produces spatter. Industry preference
    is for smooth.

    What AC welding is, is cheap.

    Sometimes, for some types of metal, or for delicate work, having
    an easily broken arc, or repeatedly forcing a restart has an
    advantage. For highly magnetic material, it avoids 'wandering'.


    FYI:

    Relays and most switches suffer from limited DC switching capacity, usually limited to 24 or 30 volts at rated currents.
    Any more results in a permanent arc bridging the contacts, followed by complete self destruction.
    Relays used as "speaker protection" generally do not.


    ...... Phil

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From ohger1s@gmail.com@21:1/5 to All on Wed Jun 7 06:45:40 2023
    Have a really rotten day.

    .... Phil

    Welcome back Phil!!!

    John

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From legg@21:1/5 to pallison49@gmail.com on Thu Jun 8 09:14:37 2023
    On Wed, 7 Jun 2023 06:07:59 -0700 (PDT), Phil Allison
    <pallison49@gmail.com> wrote:

    legg wrote:

    ------------------

    legg wrote:
    -----------------

    DC ratings of standard breakers seldom exceed 40V, due to arcing.


    ** However most *mains rated* breakers employ magnetic or physical barrier arc quenching whenever contacts open.

    Not so much quenching, as sacrificial absorption....


    ** Hello to the smug troll calling itself " legg" .

    The term "quenching" here clearly refers to physically breaking an arc by extending it.
    Rest of your pedantic, tedious, self aggrandizing, spew inducing BULLSHIT snipped.
    Have a really rotten day.

    .... Phil

    G'daye.

    RL

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From whit3rd@21:1/5 to bob prohaska on Sat Jun 10 05:52:19 2023
    On Sunday, June 4, 2023 at 9:50:55 PM UTC-4, bob prohaska wrote:
    I've been given a collection of residential service panel breakers
    and would like to check them to see if they trip correctly. They
    were in use before I got them, so they certainly close correctly,
    but it's unknown if they trip correctly.


    If they're thermal breakers, the only part that can fail while retaining
    the on/off function is a heater. A welder intended to melt metal
    applied to a heater is... maybe not a test that should be applied.

    The heater, if it fails open, won't let the breaker pass current.
    If it fails closed circuit... there's extra metal inside the breaker?

    Circuit breakers should, and generally do, fail in safe ways.
    Go ahead and use them without applying a stress test beyond normal
    currents and voltages.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bob F@21:1/5 to All on Sat Jun 10 11:17:41 2023
    On 6/10/2023 5:52 AM, whit3rd wrote:
    On Sunday, June 4, 2023 at 9:50:55 PM UTC-4, bob prohaska wrote:
    I've been given a collection of residential service panel breakers
    and would like to check them to see if they trip correctly. They
    were in use before I got them, so they certainly close correctly,
    but it's unknown if they trip correctly.


    If they're thermal breakers, the only part that can fail while retaining
    the on/off function is a heater. A welder intended to melt metal
    applied to a heater is... maybe not a test that should be applied.

    The heater, if it fails open, won't let the breaker pass current.
    If it fails closed circuit... there's extra metal inside the breaker?

    Circuit breakers should, and generally do, fail in safe ways.
    Go ahead and use them without applying a stress test beyond normal
    currents and voltages.

    If the breakers trip using a heater, then the setting of the welder (AC)
    output current will not represent the current that the breaker actually
    would trip at on line voltage, because the welder voltage likely will be
    lower

    --- SoupGate-Win32 v1.05