pbs-nas Communications with UPS SmartUPS-750 restoredNei apcupsd.events trovo:
APC : 001,041,0937
DATE : 2023-11-21 08:11:19 +0100
HOSTNAME : pbs-nas
VERSION : 3.14.14 (31 May 2016) debian
UPSNAME : SmartUPS-750
CABLE : USB Cable
DRIVER : USB UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2023-11-21 08:11:06 +0100
MODEL : Smart-UPS 750
STATUS : COMMLOST
LINEV : 223.2 Volts
LOADPCT : 56.5 Percent
BCHARGE : 0.0 Percent
TIMELEFT : 0.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
OUTPUTV : 223.2 Volts
SENSE : High
DWAKE : -1 Seconds
DSHUTD : 180 Seconds
LOTRANS : 0.0 Volts
HITRANS : 0.0 Volts
RETPCT : 90.0 Percent
ITEMP : 36.0 C
ALARMDEL : 30 Seconds
BATTV : 27.3 Volts
LINEFREQ : 50.0 Hz
NUMXFERS : 0
TONBATT : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI : 7 days
STATFLAG : 0x01000100
MANDATE : 2006-05-27
SERIALNO : AS0622342047
BATTDATE : 2022-11-13
NOMOUTV : 0 Volts
NOMBATTV : 24.0 Volts
END APC : 2023-11-21 08:11:19 +0100
# grep "2023-11-21 08:11" /var/log/apcupsd.eventsUn Battery disconnected e poi a raffica i restored. Negli apcupsd.events relativamente a Battery trovo:
2023-11-21 08:11:06 +0100Â apcupsd 3.14.14 (31 May 2016) debian
startup succeeded
2023-11-21 08:11:10 +0100Â Battery disconnected.
2023-11-21 08:11:19 +0100Â Communications with UPS restored.
2023-11-21 08:11:27 +0100Â Communications with UPS restored.
2023-11-21 08:11:36 +0100Â Communications with UPS restored.
2023-11-21 08:11:50 +0100Â Communications with UPS restored.
# grep -A1 -B3 -i battery /var/log/apcupsd.eventsCome vedete alle 08:11 ho riacceso il server con il mio ups e ha
2023-11-17 15:25:55 +0100Â apcupsd exiting, signal 15
2023-11-17 15:25:55 +0100Â apcupsd shutdown succeeded
2023-11-17 15:27:23 +0100Â apcupsd 3.14.14 (31 May 2016) debian
startup succeeded
2023-11-20 06:56:50 +0100Â UPS Self Test switch to battery.
2023-11-20 06:56:55 +0100Â UPS battery must be replaced.
2023-11-20 06:56:55 +0100Â UPS Self Test completed: No test results available
2023-11-20 15:57:55 +0100Â UPS battery must be replaced.
2023-11-20 18:31:24 +0100Â apcupsd exiting, signal 15
--
2023-11-20 22:27:13 +0100Â apcupsd exiting, signal 15
2023-11-20 22:27:13 +0100Â apcupsd shutdown succeeded
2023-11-21 08:11:06 +0100Â apcupsd 3.14.14 (31 May 2016) debian
startup succeeded
2023-11-21 08:11:10 +0100Â Battery disconnected.
2023-11-21 08:11:19 +0100Â Communications with UPS restored.
--
2023-11-21 08:12:00 +0100Â Communications with UPS restored.
2023-11-21 08:12:08 +0100Â Communications with UPS restored.
2023-11-21 08:12:21 +0100Â Communications with UPS restored.
2023-11-21 08:12:22 +0100Â Battery reattached.
2023-11-21 08:12:31 +0100Â Communications with UPS restored.
Probabilmente perché il tuo PC consuma meno del server.
L'allarme c'è quando l'autonomia calcolata (in base al carico) è
inferiore a quella impostata come soglia. Nel mio APC di casa
continuava a lamentarsi anche con batterie nuove. Con 2 pacchi in
parallelo ha smesso :)
Ma dal prossimo voglio batterie al litio (in particolare LiFePO4)!
Diego
Il 21/11/2023 14:24, Piviul ha scritto:
Ciao a tutti, vorrei sottoporvi una stranezza su un UPS APC...
Questa mattina arrivo in ufficio ed un APC smartups 750 si lamenta
che la batteria è da cambiare con i soliti bip-bip ossessivi. Mi
dico: no problem, sul mio PC ho un altro smartups 750, lo sostituisco
con quello prima dell'arrivo dell'orda degli utenti. Spengo il mio
pc, spengo il server e sostituisco l'UPS del server con quello del
mio pc; appena accendo l'ups del server incomincia a rifare bip-bip
dicendo che la batteria è da cambiare. Sono un po' perplesso ma vorrÃ
dire che entrambi gli ups hanno le batterie esauste, morte
contemporaneamente... improbabile ma possibile. Prendo l'ups del
server, lo metto sul mio pc e... va tutto bene. L'ups non si lamenta
con il solito bip-bip ossessivo. Avvio il mio pc con l'ups che prima
era sul server faccio un self-test e passa il test. Allora eseguo una
calibrazione della batteria. Anche quella va a buon fine.
Certamente domani mattina ci riprovo, scambio nuovamente i 2 UPS
ma... come è possibile?
Altro indizio strano... sul server se avvio il demone apcupsd
incomincia a raffica (5 messaggi al minuto circa) mandarmi qualcosa
tipo:
pbs-nas Communications with UPS SmartUPS-750 restoredNei apcupsd.events trovo:
APCÂ Â Â Â Â : 001,041,0937
DATEÂ Â Â Â : 2023-11-21 08:11:19 +0100
HOSTNAME : pbs-nas
VERSIONÂ : 3.14.14 (31 May 2016) debian
UPSNAMEÂ : SmartUPS-750
CABLEÂ Â Â : USB Cable
DRIVERÂ Â : USB UPS Driver
UPSMODEÂ : Stand Alone
STARTTIME: 2023-11-21 08:11:06 +0100
MODELÂ Â Â : Smart-UPS 750
STATUSÂ Â : COMMLOST
LINEVÂ Â Â : 223.2 Volts
LOADPCTÂ : 56.5 Percent
BCHARGEÂ : 0.0 Percent
TIMELEFT : 0.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIMEÂ : 0 Seconds
OUTPUTVÂ : 223.2 Volts
SENSEÂ Â Â : High
DWAKEÂ Â Â : -1 Seconds
DSHUTDÂ Â : 180 Seconds
LOTRANSÂ : 0.0 Volts
HITRANSÂ : 0.0 Volts
RETPCTÂ Â : 90.0 Percent
ITEMPÂ Â Â : 36.0 C
ALARMDEL : 30 Seconds
BATTVÂ Â Â : 27.3 Volts
LINEFREQ : 50.0 Hz
NUMXFERS : 0
TONBATTÂ : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
SELFTEST : NO
STESTIÂ Â : 7 days
STATFLAG : 0x01000100
MANDATEÂ : 2006-05-27
SERIALNO : AS0622342047
BATTDATE : 2022-11-13
NOMOUTVÂ : 0 Volts
NOMBATTV : 24.0 Volts
END APCÂ : 2023-11-21 08:11:19 +0100
# grep "2023-11-21 08:11" /var/log/apcupsd.eventsUn Battery disconnected e poi a raffica i restored. Negli
2023-11-21 08:11:06 +0100Â apcupsd 3.14.14 (31 May 2016) debian
startup succeeded
2023-11-21 08:11:10 +0100Â Battery disconnected.
2023-11-21 08:11:19 +0100Â Communications with UPS restored.
2023-11-21 08:11:27 +0100Â Communications with UPS restored.
2023-11-21 08:11:36 +0100Â Communications with UPS restored.
2023-11-21 08:11:50 +0100Â Communications with UPS restored.
apcupsd.events relativamente a Battery trovo:
# grep -A1 -B3 -i battery /var/log/apcupsd.eventsCome vedete alle 08:11 ho riacceso il server con il mio ups e ha
2023-11-17 15:25:55 +0100Â apcupsd exiting, signal 15
2023-11-17 15:25:55 +0100Â apcupsd shutdown succeeded
2023-11-17 15:27:23 +0100Â apcupsd 3.14.14 (31 May 2016) debian
startup succeeded
2023-11-20 06:56:50 +0100Â UPS Self Test switch to battery.
2023-11-20 06:56:55 +0100Â UPS battery must be replaced.
2023-11-20 06:56:55 +0100Â UPS Self Test completed: No test results
available
2023-11-20 15:57:55 +0100Â UPS battery must be replaced.
2023-11-20 18:31:24 +0100Â apcupsd exiting, signal 15
--
2023-11-20 22:27:13 +0100Â apcupsd exiting, signal 15
2023-11-20 22:27:13 +0100Â apcupsd shutdown succeeded
2023-11-21 08:11:06 +0100Â apcupsd 3.14.14 (31 May 2016) debian
startup succeeded
2023-11-21 08:11:10 +0100Â Battery disconnected.
2023-11-21 08:11:19 +0100Â Communications with UPS restored.
--
2023-11-21 08:12:00 +0100Â Communications with UPS restored.
2023-11-21 08:12:08 +0100Â Communications with UPS restored.
2023-11-21 08:12:21 +0100Â Communications with UPS restored.
2023-11-21 08:12:22 +0100Â Battery reattached.
2023-11-21 08:12:31 +0100Â Communications with UPS restored.
incominciato a dare i problemi di battery disconnected. Sembra che
ora ci siano problemi di dialogo fra la batteria e l'UPS ma perché
prima, quando era sul mio pc questi problemi non si verificavano e
come mai invece sul mio pc l'ups del server non ha dato problemi nel
test della batteria che quando la stessa alimentava il server si
lamentava che era da cambiare?
Sono molto confuso, domattina comunque vi aggiorno.
Piviul
2023-11-20 06:56:50 +0100Â UPS Self Test switch to battery.per quello che vedo da qui la batteria deve essere cambiata. adesso non
2023-11-20 06:56:55 +0100Â UPS battery must be replaced.
2023-11-20 06:56:55 +0100Â UPS Self Test completed: No test results availabl
come è possibile?
Altro indizio strano... sul server se avvio il demone apcupsd incomincia
a raffica (5 messaggi al minuto circa) mandarmi qualcosa tipo:
pbs-nas Communications with UPS SmartUPS-750 restored
Sysop: | Keyop |
---|---|
Location: | Huddersfield, West Yorkshire, UK |
Users: | 297 |
Nodes: | 16 (2 / 14) |
Uptime: | 10:25:58 |
Calls: | 6,666 |
Files: | 12,213 |
Messages: | 5,336,335 |