• Re: What's a better UPS?

    From Alan Browne@21:1/5 to J Burns on Thu Jun 9 14:02:20 2022
    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected. Leaving a battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I have
    yet to change the batteries. This includes UPS' with 1 battery (desk
    stations) and 2 batteries ("backoffice" backup power).

    Recently had a power failure that lasted 3 hours. The "backoffice"
    system went the distance. The desktop ones lasted nearly 1.5 hours (the stations that have laptops had no issues, of course).

    I have a "new" UPS here (home) that I bought ca. 2017. No issues at
    all. It often trips in whenever the printer starts.

    The alarm system battery (not APC but similar lead-acid battery) was
    changed after about 5 years based on a message from the alarm system.
    That cost about CAD$22.

    --
    "Mr Speaker, I withdraw my statement that half the cabinet are asses -
    half the cabinet are not asses."
    -Benjamin Disraeli

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From J Burns@21:1/5 to All on Thu Jun 9 13:31:38 2022
    The battery in my APC failed after three years, as expected. Leaving a
    battery on a DC charge is a pretty quick way to ruin it. About 1955, a
    man invented a pulse charger for things like fork lifts and emergency
    lights because, he'd found, it could be left on continuously without
    harm to a battery. Sears marketed a car battery charger like that. I
    think it had one transistor. As the battery voltage rose, the pulses
    narrowed to a trickle charge, and a pulsed trickle charge is harmless.

    It took decades for pulse chargers to become common. Nowadays, a lot of
    smart chargers shut their pulses off and don't charge again until the
    battery voltage falls.

    I bought the APC because I didn't know of a UPS that didn't leave a DC
    trickle charge on the battery. Now I find that they made their battery compartment 1/2" narrower than the standard battery. I might have
    thought that for a premium price, I could buy their replacement, but
    they don't sell them. They sold me the UPS to offer me an upgrade, and
    if I buy a more expensive model, they'll remove the hazardous waste that
    my UPS has become.

    It would be far more pleasing to buy a better model of another brand.
    What's a good model?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From nospam@21:1/5 to All on Thu Jun 9 13:51:52 2022
    In article <t7tapr$27h$1@dont-email.me>, J Burns <burns@nospam.com>
    wrote:

    I bought the APC because I didn't know of a UPS that didn't leave a DC trickle charge on the battery. Now I find that they made their battery compartment 1/2" narrower than the standard battery.

    no they didn't.

    apc upses use standard lead-acid batteries which are available anywhere.

    you might need to reuse connectors in some models, but that's about it.

    which apc ups do you have?

    I might have
    thought that for a premium price, I could buy their replacement, but
    they don't sell them.

    yes they do, although those are more costly than aftermarket batteries.

    They sold me the UPS to offer me an upgrade, and
    if I buy a more expensive model, they'll remove the hazardous waste that
    my UPS has become.

    they do offer upgrades, but that's generally not cost-effective unless
    you're upgrading to a bigger and better model.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From J Burns@21:1/5 to Alan Browne on Thu Jun 9 16:25:16 2022
    On 6/9/22 2:02 PM, Alan Browne wrote:
    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected. Leaving a
    battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I have
    yet to change the batteries.  This includes UPS' with 1 battery (desk stations) and 2 batteries ("backoffice" backup power).

    Recently had a power failure that lasted 3 hours.  The "backoffice"
    system went the distance.  The desktop ones lasted nearly 1.5 hours (the stations that have laptops had no issues, of course).

    I have a "new" UPS here (home) that I bought ca. 2017.  No issues at
    all.  It often trips in whenever the printer starts.

    The alarm system battery (not APC but similar lead-acid battery) was
    changed after about 5 years based on a message from the alarm system.
    That cost about CAD$22.

    After I got the alarm and red flashing light the second time, I removed
    the battery hooked it to a 1-amp bulb for 15 minutes. The voltage under
    that load looked normal. As soon as I switched to a 4-amp bulb, the
    current dropped to milliamps. The acid must have eaten through a
    conductor. I haven't even seen that listed as a cause of UPS battery
    failure.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Wade Garrett@21:1/5 to Alan Browne on Fri Jun 10 08:39:25 2022
    On 6/9/22 2:02 PM, Alan Browne wrote:
    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected. Leaving a
    battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I have
    yet to change the batteries.  This includes UPS' with 1 battery (desk stations) and 2 batteries ("backoffice" backup power).

    Recently had a power failure that lasted 3 hours.  The "backoffice"
    system went the distance.  The desktop ones lasted nearly 1.5 hours (the stations that have laptops had no issues, of course).

    I have a "new" UPS here (home) that I bought ca. 2017.  No issues at
    all.  It often trips in whenever the printer starts.

    Why plug your printer into a UPS? Sucks current, function not critical,
    etc. I never do and suspect that most folks don't either...

    --
    Why is it that the politicians who want more government control over
    your life are the same ones who want you to be disarmed?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Browne@21:1/5 to Wade Garrett on Fri Jun 10 11:30:09 2022
    On 2022-06-10 08:39, Wade Garrett wrote:
    On 6/9/22 2:02 PM, Alan Browne wrote:
    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected. Leaving
    a battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I
    have yet to change the batteries.  This includes UPS' with 1 battery
    (desk stations) and 2 batteries ("backoffice" backup power).

    Recently had a power failure that lasted 3 hours.  The "backoffice"
    system went the distance.  The desktop ones lasted nearly 1.5 hours
    (the stations that have laptops had no issues, of course).

    I have a "new" UPS here (home) that I bought ca. 2017.  No issues at
    all.  It often trips in whenever the printer starts.

    Why plug your printer into a UPS? Sucks current, function not critical,
    etc. I never do and suspect that most folks don't either...

    Never said it was. But the printer is on the same circuit as the
    computers in my home office. When it starts it draws a lot of current
    so the voltage sags causing the UPS to kick in for a second or 2.

    If there were another circuit available for the printer, I'd plug it in
    there. But there isn't. This end of the house is far from the breaker
    panel as well, which doesn't help with the voltage sag.

    Don't print all that much, so it's not much of an issue.

    --
    "Mr Speaker, I withdraw my statement that half the cabinet are asses -
    half the cabinet are not asses."
    -Benjamin Disraeli

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Wade Garrett@21:1/5 to Alan Browne on Fri Jun 10 18:39:09 2022
    On 6/10/22 11:30 AM, Alan Browne wrote:
    On 2022-06-10 08:39, Wade Garrett wrote:
    On 6/9/22 2:02 PM, Alan Browne wrote:
    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected. Leaving
    a battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I
    have yet to change the batteries.  This includes UPS' with 1 battery
    (desk stations) and 2 batteries ("backoffice" backup power).

    Recently had a power failure that lasted 3 hours.  The "backoffice"
    system went the distance.  The desktop ones lasted nearly 1.5 hours
    (the stations that have laptops had no issues, of course).

    I have a "new" UPS here (home) that I bought ca. 2017.  No issues at
    all.  It often trips in whenever the printer starts.

    Why plug your printer into a UPS? Sucks current, function not
    critical, etc. I never do and suspect that most folks don't either...

    Never said it was.  But the printer is on the same circuit as the
    computers in my home office.  When it starts it draws a lot of current
    so the voltage sags causing the UPS to kick in for a second or 2.

    If there were another circuit available for the printer, I'd plug it in there.  But there isn't.  This end of the house is far from the breaker panel as well, which doesn't help with the voltage sag.

    Don't print all that much, so it's not much of an issue.

    Ah so, a good example of the tyranny of assumption on my part!

    --
    Why is it that the politicians who want more government control over
    your life are the same ones who want you to be disarmed?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Your Name@21:1/5 to J Burns on Sat Jun 11 10:19:53 2022
    On 2022-06-09 17:31:38 +0000, J Burns said:

    What's a better UPS?

    FedEx? DHL? ;-)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Browne@21:1/5 to Wade Garrett on Fri Jun 10 20:00:52 2022
    On 2022-06-10 18:39, Wade Garrett wrote:
    On 6/10/22 11:30 AM, Alan Browne wrote:
    On 2022-06-10 08:39, Wade Garrett wrote:
    On 6/9/22 2:02 PM, Alan Browne wrote:
    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected.
    Leaving a battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I
    have yet to change the batteries.  This includes UPS' with 1 battery
    (desk stations) and 2 batteries ("backoffice" backup power).

    Recently had a power failure that lasted 3 hours.  The "backoffice"
    system went the distance.  The desktop ones lasted nearly 1.5 hours
    (the stations that have laptops had no issues, of course).

    I have a "new" UPS here (home) that I bought ca. 2017.  No issues at
    all.  It often trips in whenever the printer starts.

    Why plug your printer into a UPS? Sucks current, function not
    critical, etc. I never do and suspect that most folks don't either...

    Never said it was.  But the printer is on the same circuit as the
    computers in my home office.  When it starts it draws a lot of current
    so the voltage sags causing the UPS to kick in for a second or 2.

    If there were another circuit available for the printer, I'd plug it
    in there.  But there isn't.  This end of the house is far from the
    breaker panel as well, which doesn't help with the voltage sag.

    Don't print all that much, so it's not much of an issue.

    Ah so, a good example of the tyranny of assumption on my part!

    Not like I put up a diagram, so let's call it a draw and enjoy the weekend!

    --
    "Mr Speaker, I withdraw my statement that half the cabinet are asses -
    half the cabinet are not asses."
    -Benjamin Disraeli

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Browne@21:1/5 to Your Name on Fri Jun 10 20:03:52 2022
    On 2022-06-10 18:19, Your Name wrote:
    On 2022-06-09 17:31:38 +0000, J Burns said:

    What's a better UPS?

    FedEx? DHL?   ;-)

    FedEx? Perhaps, even: sure.

    DHL? The word "sucks" lacks sufficient vacuum.

    --
    "Mr Speaker, I withdraw my statement that half the cabinet are asses -
    half the cabinet are not asses."
    -Benjamin Disraeli

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Neill Massello@21:1/5 to J Burns on Sat Jun 11 02:44:02 2022
    On 2022-06-09 at 11:31:38 MDT, "J Burns" <burns@nospam.com> wrote:

    It would be far more pleasing to buy a better model of another brand.
    What's a good model?

    I've been pleased with CyberPower's PFC Sinewave models. Can't say that
    they're tremendously better than APC's, but they do tend to be a little cheaper. (I've never used TrippLite, the other big name.)

    <https://www.cyberpowersystems.com/products/ups/>

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bud Frede@21:1/5 to Alan Browne on Sun Jun 19 15:21:39 2022
    Alan Browne <bitbucket@blackhole.com> writes:

    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected. Leaving
    a battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I
    have yet to change the batteries. This includes UPS' with 1 battery
    (desk stations) and 2 batteries ("backoffice" backup power).

    The standard best practice for a UPS in a datacenter is to replace
    lead-acid batteries every 5 years, and some places do it every 4.

    I really wouldn't recommend using batteries for 8 years. :-)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Browne@21:1/5 to Bud Frede on Sun Jun 19 17:04:19 2022
    On 2022-06-19 15:21, Bud Frede wrote:
    Alan Browne <bitbucket@blackhole.com> writes:

    On 2022-06-09 13:31, J Burns wrote:
    The battery in my APC failed after three years, as expected. Leaving
    a battery on a DC charge is a pretty quick way to ruin it.

    I have APC UPSs at work that have been in service since 2014 and I
    have yet to change the batteries. This includes UPS' with 1 battery
    (desk stations) and 2 batteries ("backoffice" backup power).

    The standard best practice for a UPS in a datacenter is to replace
    lead-acid batteries every 5 years, and some places do it every 4.

    I really wouldn't recommend using batteries for 8 years. :-)


    Lead acid batteries seeing little cycling in a benign environment don't
    worry me much. Real enemy is lots of deep cycles in a very hot, or
    very, very cold environment.

    The other day we had storms in the area and intermittent "blinks", all
    of the UPS' kicked in (work and at home), no power lost at all.

    --
    “Donald Trump and his allies and supporters are a clear and present
    danger to American democracy.”
    - J Michael Luttig - 2022-06-16
    - Former US appellate court judge (R) testifying to the January 6
    committee

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From J Burns@21:1/5 to Neill Massello on Tue Jun 28 17:19:48 2022
    On 6/10/22 10:44 PM, Neill Massello wrote:
    On 2022-06-09 at 11:31:38 MDT, "J Burns" <burns@nospam.com> wrote:

    It would be far more pleasing to buy a better model of another brand.
    What's a good model?

    I've been pleased with CyberPower's PFC Sinewave models. Can't say that they're tremendously better than APC's, but they do tend to be a little cheaper. (I've never used TrippLite, the other big name.)

    <https://www.cyberpowersystems.com/products/ups/>

    I see it uses standard battery dimensions. I see they have two batteries recommended for it: 8 and 9 amp hours. The price difference is small,
    and the warranty is the same. I wonder why they sell the one with less capacity.

    I saw a model --- I think it was Cyberpower --- with two batteries. That
    makes them hot swappable in the event of a long outage.

    It would also make testing easy. Without shutting down, you could remove
    a battery, hook it up to a certain load, and see how long it stayed
    above a certain voltage. According to the SAE, that's the best way of
    telling if a car battery should be replaced. For a 12 volt car battery,
    I believe the cuttoff voltage is 10.5 and the load is 25 amps. IIRC, if
    it lasts 40% of the published reserve minutes, its okay. (Maybe I'm
    wrong about the percent.)

    I've found that this can rejuvenate a car battery. APC recommends it to
    help a battery's service life. I think twice a year you unplug the UPS
    and draw current until it cuts off. They didn't mention that with my UPS.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From nospam@21:1/5 to All on Tue Jun 28 18:02:22 2022
    In article <t9fr9l$16knn$1@dont-email.me>, J Burns <burns@nospam.com>
    wrote:

    I saw a model --- I think it was Cyberpower --- with two batteries. That makes them hot swappable in the event of a long outage.

    nope. hot swap depends on the design of the ups itself, not the number
    of batteries.

    It would also make testing easy. Without shutting down, you could remove
    a battery, hook it up to a certain load, and see how long it stayed
    above a certain voltage. According to the SAE, that's the best way of
    telling if a car battery should be replaced.

    the ups does that by itself.

    For a 12 volt car battery,
    I believe the cuttoff voltage is 10.5 and the load is 25 amps. IIRC, if
    it lasts 40% of the published reserve minutes, its okay. (Maybe I'm
    wrong about the percent.)

    you're wrong about all of that.

    I've found that this can rejuvenate a car battery. APC recommends it to
    help a battery's service life. I think twice a year you unplug the UPS
    and draw current until it cuts off. They didn't mention that with my UPS.

    that's for calibration, not to extend its life.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)